power Cable testing

09/16/2008 10:56 PM

what will be the reason for the spark coming out while testing(insulation resistance) the 6KV cable drums enenthough i applied correct testing voltage?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: power Cable testing

09/16/2008 11:09 PM

Hello "Guest"

Which "Cable Drums" are you talking about?

What test voltage and AC or DC were you using.

For how long was the Test voltage applied.

Where did the "spark" come from?

My best guess as to your Question:

If you are talking about a new drum of cable, with one end sealed by the makers, and you were testing from the end you opened up, the capacitance of the cable will enable it to store large amounts of energy if you used a 5kV DC supply to test the cable.

After you disconnect the test supply, the cable is still holding the charge voltage, perhaps for several days.

Ensure after all High Voltage testing, that charged conductors and equipment is correctly discharged, or yourself or others may suffer injury or death.

As you may see from my reply, I am guessing at your problem, and thus my best (so far) answer, because you need to be more specific.

Reply with

Why remain as a Guest. Register at and enjoy helping others.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: power Cable testing

09/17/2008 7:25 AM

Insulation breakdown. It is an expression of the cable failing the test.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: Jul 2007
Location: Toronto
Posts: 14
#3

Re: power Cable testing

09/18/2008 12:19 AM

Residual charges. You have to discharge cable after testing megger.

Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#4
In reply to #3

Re: power Cable testing

09/18/2008 1:13 AM

Nope! Sparkstation got it right the first time. Saw the same problem/phenomenom when I was doing dielectric testing of power cables when I worked for Hydro. Evidently "Guest" isn't using proper test equipment or else not following procedure. Either will get someone killed sooner rather than later.

__________________
Elnav
Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#5

Re: power Cable testing

09/19/2008 6:58 PM

If you are not competently trained in high voltage testing, you are risking severe injury and/or death. It is imperative that you know and follow proper HV testing procedure(s) at all times.

Where is the arcing occurring?

If you are testing cable wrapped on a drum (reel?) and do not have control of both ends of the cable, the distance between the conductors at either end could be insufficient to prevent arcing between the conductors and/or whatever it is attached to.

One-time acceptance testing for new electrical apparatus is: 2E + 1,000 (2 x rated voltage) + 1,000. If the cable in this case is used, do not exceed the manufacturer's nominal voltage rating stamped on the cable. If you are not exceeding the manufacturer's rating, and the arcing is occurring at a specific location (other than at an end), or at intervals along the length of the cable, the insulation has failed and the cable should not be used for any reason.

If you are not absolutely sure of what you are doing, get competent help before continuing.

Good luck and be very careful.

Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#6

Re: power Cable testing

09/20/2008 4:59 AM

Is the cable a continious lenght or are there welds in the calbe that could have broken inside the insulation and a spark burnt thru to the outside ?

__________________
If you never do anything you never have problems.
Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#7
In reply to #6

Re: power Cable testing

09/20/2008 6:56 AM

Hello dadw5boys

In the usual manner of Guest Topic Starters, I venture to state that the Original Topic Starter Guest shall not bother to give a proper response.

Of course "Guest" could reply, but there is currently no way of determining which "Guest" is which.

If the cable is "On the reel" as stated, the "spark" is almost certainly the built-up charge in the cable, after using HV test equipment without making certain the stored charge was properly and safely discharged, refer my best guess here:http://cr4.globalspec.com/comment/282485/Re-power-Cable-testing

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#8
In reply to #7

Re: power Cable testing

09/20/2008 12:03 PM

In cutting fixed lenghts for aircraft wiring bundles our test blew out broken welds in stranded cables up to 4/0 Nickle Plated power cable.

Plus I just like to ask questions .

__________________
If you never do anything you never have problems.
Reply
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dadw5boys (2); elnav (1); hareshptl (1); PWSlack (1); SHOCKISCAN (1); Sparkstation (2)