Voltage problem

09/20/2008 6:06 PM

Hello friends,

We have connected 720KVAR capacitor bank to improve our plant power factor.It was working well, But now we are facing voltage rise problem in our plant. Instead of 415V, voltage rises upto 450 to 460 volts & single phase voltage rises upto 260 volts. If we switch OFF this 720KVAR bank; voltage becomes normal.

So please help to sort out a problem?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
9
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Voltage problem

09/20/2008 6:33 PM

Sounds as though you are over correcting. That is the risk of bulk correction, the power factor correction method you are using if you have only one set of 720kVAR caps. You have designed the system based upon the worst case of lagging power factor, but now for whatever reason you have less inductance, probably fewer motors on-line. That means you now have too much capacitance and it s raising your voltage.

This is the reason why it is better to correct power factor at the offending loads, the AC motors. By attaching smaller PFC capacitors on the load side of each of the motor contactors, the capacitance is only added to the system when the induction motor is on-line.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 9)
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#4
In reply to #1

Re: Voltage problem

09/21/2008 6:49 AM

Hello JRaef

from me

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11
In reply to #1

Re: Voltage problem

09/22/2008 3:14 AM

I gave you a GA for an excellent and fully correct answer.

The original poster is among the many people that fail to understand that the problem is usually dynamic and only a dynamic fix will really work. For example, as you pointed out, a correction that is built into each offending unit so that only when it is powered up, does the correcting cap come into play......

I have noticed this complete lack of understanding of these types of problems several times on CR4 and if you try and correct their way of thinking, some people get quite upset!!! So I gave up trying to help such stupid people a long time ago!!

I hope your post brings some light into some really dark minds!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
2
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2

Re: Voltage problem

09/21/2008 3:01 AM

Hello "Guest",

Whoever installed a 720kVAR PF correction Capacitor bank without an Automatic Power Factor Correction Unit being fitted?

The alternative to the JRaef response above, is to use an automatic Power Factor Correction Unit, which switches capacitors in or out, to correct what the Unit is set to deliver at the Main switchboard.

The best place to install PF correction is at the Motor terminals, as JRaef says, this lessens Wattless circulating currents, and also only works to correct PF of the motor when the motor is powered.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply Good Answer (Score 2)
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#3

Re: Voltage problem

09/21/2008 4:42 AM

You are over correcting.720KVAR should be split into various segments and depending upon the requirement a bank of capacitors should be switched on

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Active Contributor

Join Date: Sep 2008
Posts: 16
#5

Re: Voltage problem

09/21/2008 8:45 AM

THE SELECTION OF THE CAPACITORS MAY NOT BE ACCURATE .THATS WHY YOUR VOLTAGE IS UNBALANCED DUE TO HARMONICS CREATED BY THE CPACITOR BANKS WHICH WOULD EVEN BE DANGERIOUS FOR YOUR CAPACITORS ALSO.

SELECTION OF HEAVY INDUSTRIAL CAPACITOR BANK IS NEEDED IN ADDITION TO THE APFC PANEL .I.E AUTOMATIC POWER FACTOR CONTROLER WHICH WILL SENSE THE LOAD AND ACCORDINGLY IT WILL DECIDE HOW MANY CAPACITORS ARE REQUIRED TO OPERATE.

Reply
Anonymous Poster
#6

Re: Voltage problem

09/21/2008 4:05 PM

Sorry friends, I forgot to write that this bank is controlled with APFC & also controller is switching ON & OFF the small capacitors automatically as per inductive load.

Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#7
In reply to #6

Re: Voltage problem

09/21/2008 6:10 PM

Hello "Guest",

That is a very important piece of information which you "forgot" to mention earlier.

Are such "memory lapses" often occurring, if so you need to seek urgent help, because you risk damage to equipment, a penalising power account, and possible personal accident to your good self.

Taking this "previously unmentioned fact" into account, there are only two possibilities:

  1. The APFC controller is faulty
  2. The APFC Controller has been incorrectly set

If the APFC Unit and capacitor Bank are new, then your recourse is:

If (1) above, then contact the supplier immediately.

If (2) above, then get an Electrical Technician or Electrical Engineer, who has the Test Equipment available, and knows how to use it, to set the APFC setting correctly.

Let us hope you have had no further "memory lapses", because electricity needs a clear head, proper knowledge, correct Test Equipment, no memory lapses, and other necessary items for your being able to run equipment such as an APFC unit properly, automatically and safely.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#21
In reply to #6

Re: Voltage problem

09/22/2008 2:19 PM

Did you measure the power factor for the 3 phases on which you try to compensate the inductive power ?

Based on the resulting power factor you can determinate if you overcompensate or not and go on from there.

__________________
Scientes et audaces fortuna juvat !
Reply
Associate
India - Member - New Member

Join Date: Mar 2007
Location: India Bangalore
Posts: 40
#8

Re: Voltage problem

09/21/2008 10:50 PM

May be capacitor in one of phases in one or more of units being open or faulty.

__________________
Nothing is impossible, Impossible is nothing
Reply
Associate

Join Date: Jul 2008
Posts: 37
#9

Re: Voltage problem

09/21/2008 11:39 PM

hi

the capacitor bank of 720 kvar is of fixed rating, u can't adjust the kvar supplied by the bank,

the rating is based on some kw load and PF keeping in mind, at the time of kvar calculation,

this bank will raise the system voltage if the load is less then calculated one, so at less or reduced load the capacitor bank's kvar also needs to be adjusted accordingly,

if u don't adjust the kvar of bank, the kvar supplied by the bank will increase the system voltage by10 to 20 % approx.

u need to make variable bank means u can adjust the kvar of the bank when u needed

best regards

divyesh patel

Reply
2
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#10

Re: Voltage problem

09/22/2008 1:32 AM

I've only just covered this at tech so please make it a clean kill if you decide to shoot the messenger, But...

From what I understand, there are either of two things happening: -

1) Your incoming Voltage is High and this is now being seen as your PFC has done it's job correctly.

2) You have a problem with your Earth and or Neutral and you have a floating Voltage on a Star (Wye) transformer.

Harmonics may play apart in this, but I don't believe a PFC can increase voltage, only return its value to the same as supply, otherwise everyone would use it to "Create Free Energy"

Regards,
Sapper.

__________________
It's all about the Boom! - MythBusters
Reply Good Answer (Score 2)
Active Contributor

Join Date: Jul 2008
Posts: 15
#13
In reply to #10

Re: Voltage problem

09/22/2008 5:05 AM

sapper you are correct but i suggest some of the winding are shorted otherwise if the neutral or the earth is missing the voltage may even be higher than the above mentioned voltage

Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2008
Location: TR
Posts: 142
Good Answers: 1
#22
In reply to #10

Re: Voltage problem

09/22/2008 3:50 PM

I don't agree the last part of your post.

"...but I don't believe a PFC can increase voltage, only return its value to the same as supply, otherwise everyone would use it to "Create Free Energy"

Increasing voltage level is not the same as increasing mean energy.

You are thinking of the CAPS of PFC alone. This is not the case, think of them with the inductances on the network.

These caps and inductances resonates and this phenomenon is encountered as increase at voltage level if the load current is below than that of PFC designed. Means these are transient peaks actually and decay factor depends on load current.

Regards

Reply
Member

Join Date: Aug 2008
Posts: 5
#12

Re: Voltage problem

09/22/2008 4:03 AM

Dear Sir,

Pl check actual requirement of capacitor ( 720 seems high) and put it.

My expectation is you have put heigher capacity.

Reply
Anonymous Poster
#14

Re: Voltage problem

09/22/2008 7:34 AM

Dear Sir,

Your problem does not lies with the Capacitor Bank. You donot have any voltage problem. Normally a capcitor bank injects leading (VAr) Power factor. If your turn on the Capacitor then The Voltage rises.

if you really want the capcitor bank to run, then lower the tap of the Power Transformer.

Regards,

N.Suresh

Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#16
In reply to #14

Re: Voltage problem

09/22/2008 8:12 AM

N.Suresh, you are probably correct. While it is possible that the bank is over-compensating, it is not the only possibility. Measure the power factor with the capacitor bank on. If it is below 0.98 lagging, you are OK. Simply reduced the transformers taps. They were originally set high to compensate for the voltage loss in the cables at low power factor.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply
Participant

Join Date: Sep 2008
Posts: 2
#15

Re: Voltage problem

09/22/2008 7:51 AM

Hello friend,

Basically capacitor bank is used to increase the voltage in order to improve power factor.In your case , already you have normal voltage means don't add capacitor.This case you should check the plant running electrical equipment and find out which one is running with 70 or less than 70 % of the load and change that existing electrical motor with less capacity to met 90 and above % your power factor will improve by it.

Reply
Anonymous Poster
#17

Re: Voltage problem

09/22/2008 8:50 AM

so ,its clear my friend u should go for less kvar capactior bank or increase ur load correspondingly

Reply
Anonymous Poster
#18

Re: Voltage problem

09/22/2008 9:21 AM

Hello,

Your capicitor bank is over correcting your power factor beyond 100%

That puts you in a lead position. You need to throttle your bank by adding a controller that automatically corrects by connecting or disconnecting capacitors within your bank to get you close to 90% power factor. Your local power company rep will tell you what level they want you at.

Hope this helps

Reply
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#19

Re: Voltage problem

09/22/2008 12:43 PM

From the replies I've read so far, Sapper seems to be the closest to the actual problem. One of the side effects of PFC is the noticed lack of voltage drop that was previously on the system. The lagging current is now being offset/supplied by the PFC, so the voltage drop it imposed on the system will no longer be present, giving the illusion that the caps are increasing the voltage.

Leave the caps on-line, readjust the taps on your in-coming transformer(s) to the desired voltage, and then pat yourself on the back for all the cash you will not be paying the utility.

Reply Score 1 for Good Answer
Anonymous Poster
#20

Re: Voltage problem

09/22/2008 12:55 PM

We had a similar problem testing so AC power. Our final conclusion was that the power was looping thus incressing.

As a result we are now and have been working with DC power only and later converting it to AC.

In short. Much greater control. Plus larger amounts of DC can be stored for use as needed and with AC thats not the case for much long term use.

Thank You,

Sarah Angelina DeLagostti
www.DeLagostti-Industries.com
Manhattan, New York City
United State Territories

Reply
Anonymous Poster
#23
In reply to #20

Re: Voltage problem

09/23/2008 2:04 AM

Are you joking?

Reply
Commentator
Engineering Fields - Power Engineering - Projects Engineer

Join Date: Aug 2008
Location: Tanzania- East Africa
Posts: 71
#24

Re: Voltage problem

09/24/2008 10:08 AM

Hai,

do you have harmonic generating equipments installed recently e.g Motor drives ,smps units etc.

you may be developing a resonant circuit loop thus developing a higher than normal voltage .

switch off the above mentioned equipments and observe.

Also check the Neutral to ground voltage ,you may be having a floating neutral .

__________________
A wise person will understand more from a Foolish question than what a Fool will understand from a Wise Answer
Reply
Reply to Forum Thread 24 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: