Cable Gland and Low Voltage Control Cable 0.6/1 kV

10/06/2008 10:32 PM

Dear Engineers,

Kindly please help me to know the methods to select the right CABLE GLAND such as PG-7, PG-9, PG-21,... that are fitted suitably with the following types of low voltage control cable 0.6/1kV: Cu/PVC/PVC-S/2x2.5mm2; 2x4; 4x4; 8x4; 12x4; 4x1.5 (4x2.5); 7x1.5(2.5); 10x1.5(2.5); 14x1.5(2.5); 19x1.5(2.5); 24x1.5(2.5)...

Thanks in Advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#1

Re: Cable Gland and Low Voltage Control Cable 0.6/1 kV

10/08/2008 8:14 AM

You will have to know the outside diameter of each cable. The gland manufacturer lists the minimum/maximum diameters each will hold. You first pick one you think you can drill a hole for, if box mounting. (that becomes a real problem in the USA when trying to decide which metric diameter is closest to a bit sized in fractional inches that is in stock in your machine shop) Then check the range of cable diameters the gland will fit. (look at the min listing and the max lsting - is your cable within this range?) If the gland fits use it. If not, go to a bigger or smaller one, whichever is required. No magic here - no rules or regulations - just some common sense.

By the way. As I am told, the PG gland sizes are becoming obsolete and the simple metric sized ones are the ones to choose. We use NPT here in the States, which probably should be obsolete by now, but we just can't change our ways.