Single phasing of squirrel cage induction motor

10/12/2008 4:17 PM

How squirrel cage induction motor reacts if single phasing occurs during running condition at different loads,no load to full load?

note:please neglect Single phasing protection.

Please be specific about motor load relates to your answer.

__________________
Stay foolish to learn..
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Single phasing of squirrel cage induction motor

10/12/2008 4:25 PM

The motor will continue to run at significantly reduced Hp. It will get hot and be damaged if it is not de-energized.

Register to Reply Score 1 for Good Answer
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#2
In reply to #1

Re: Single phasing of squirrel cage induction motor

10/12/2008 6:24 PM

No load or light load it may run for a while without hurting anything at all---

BUT--with a normal load it won't run, long, if the motor has normal overload protection---

A normal thermal overload relay(Not single phase protection) will will drop the motor out on the high amps of the other legs, typically--Then when you try to restart the motor it won't have a reason to turn.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Commentator

Join Date: Sep 2008
Location: India
Posts: 91
Good Answers: 6
#3

Re: Single phasing of squirrel cage induction motor

10/12/2008 10:25 PM

The amount of load is directly proportional to the time required for winding insulation damage.

Register to Reply
Commentator

Join Date: Sep 2008
Location: India
Posts: 91
Good Answers: 6
#6
In reply to #3

Re: Single phasing of squirrel cage induction motor

10/14/2008 4:35 AM

The amount of load is directly inversly proportional to the time required for winding insulation damage at single phasing if no protection.

Sorry for the mistake.

Register to Reply
Guru

Join Date: May 2007
Location: Budapest, Hungary, HA5YAR
Posts: 617
Good Answers: 14
#4

Re: Single phasing of squirrel cage induction motor

10/12/2008 11:49 PM

The available torque will be less, 1/3-2 of the original value, so will be less the available power. If the load remains below this value the motor will keep running. If the load exceeds that value the motor will stop and - if you have it - the overload protection will trip.

__________________
Aged man is not old man...
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#10
In reply to #4

Re: Single phasing of squirrel cage induction motor

02/16/2026 6:19 AM

1/3-2= 9

You sure that is what you meant?

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#5

Re: Single phasing of squirrel cage induction motor

10/13/2008 4:54 PM

If the motor still runs (light loading), it will be mechanically very loud and as has already been pointed out, it will overheat.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Anonymous Poster
#7

Re: Single phasing of squirrel cage induction motor

10/14/2008 11:44 AM

With one phase, there are any rotation fields and induction motor cannot run.

--------------------------------------

Register to Reply
Power-User

Join Date: Jan 2008
Location: Silvis, IL (Quad Cities)
Posts: 141
Good Answers: 5
#8

Re: Single phasing of squirrel cage induction motor

10/20/2008 6:10 AM

All of the others are correct. Another thing to note is that if the motor is not running and it is single phased, when you try to start the motor it will not turn and will give off a very loud humming sound. Once you have heard it once it is very distinctive and a dead giveaway that a motor is single phased. The most common reason that I have seen personally is one of the contacts in a starter is no longer making contact or a cut wire in the power leads to a motor.

__________________
Perfection is achieved, not when there is nothing left to add, but when there is nothing else to take away
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Single phasing of squirrel cage induction motor

02/11/2026 11:57 AM

If the motor is correctly installed, then (a) protection device(s) will operate, thereby disconnecting and protecting it from damage.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 10 comments