I got a batch reactor (cc 1500 mmWC) which operates under vacuum and 4 kg/cm2 conditions for a chemical.
But the transmitter manufacturers recommond for DP level remote seal transmitters but of 80NB why is it so 40 NB sized flange d DPT should work what's your suggessions?
Regards,
sanjiv Patil.
Re: level measurement
10/20/2008 3:42 AM
On the basis of diaphragm area, an 80ø connection will be more accurate and therefore more easily available than a 40ø one.
10/21/2008 12:42 AM
by how much? 40NB they mention accuracy around 0.07% and for 80NB 0.067% does it really matters?
10/21/2008 5:38 AM
You aren't as interested in the instrument accuracy as you are about the measurement accuracy. 1500 mmWC is around 2 psi and is a small measurement. A larger face will give you a more accurate measurement. Since pressure is a function of area, a larger area will multiply the force and gives the amplifier a better signal to noise ratio.
Do this. Don't do that. Can't you redesign?
10/21/2008 7:41 AM
when we are using DPT without Extended flange then same sensor has less accuracy that what you mean to say?
regards,
sanjiv
10/21/2008 6:22 PM
Yes, exactly. A larger surface area is more sensitive to small differences in pressure.
10/22/2008 12:11 AM
thanks
Regards,
sanjiv