PLC5 Watchdog Timer Issue

11/12/2008 5:57 PM

I connected to a PLC5 that wasn't working and there was a watchdog timer error. Somehow the timer was set to zero. After changing the timer to 500 the problem went away. Is there any way for the value to change to 0 other than the fact that someone went in before me and changed it? I'm assuming it couldn't have been running at zero before today.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Instrumentation Engineering - New Member Hobbies - Fishing - New Member

Join Date: Jan 2008
Location: Kazakhstan
Posts: 753
Good Answers: 8
#1

Re: PLC5 Watchdog Timer Issue

11/12/2008 6:41 PM

It might be as you said i.e. someone has changed time out for WT. Also it depends on how were stored variables at PLC memory. For instance if it stored at NVRAM it might be caused the battery discharge.

For hazardous industrial conditions sometimes it used to be when data is losing at some of memory registers, especially if program for your particular PLC was completely downloaded to SRAM.

Reply
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#2

Re: PLC5 Watchdog Timer Issue

11/12/2008 11:13 PM

Hi "Guest", please take the time to register if you haven't already.

Typically the PLC5 system is pretty reliable. A few months ago one of my plc5/11 systems gave up its CPU in a similar manner that you are asking about.

It started by giving me some intermittent strangeness, dumping some register values here and there over a couple of days, even changed a timer value once, and then faulted off the watchdog... same thing...register had blown it's value and was 0. I replaced the the CPU and have no other issues.

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Reply
Anonymous Poster
#3

Re: PLC5 Watchdog Timer Issue

11/13/2008 11:10 PM

I am CoronaCameraMan -

My history goes back to the early 1980's with the A-B PLC's, haven't worked with them recently but worked with several in power generation where voltage surges could get thru the standard A-B power supply and shut the program down.

I also found a history where the electric utility at 34.5 kV was switching capacitors in a substation 7 miles away and 7 of 10 plant trips correlated to capacitor switching times. After installing a line filter ahead of the PLC power supply that problem went away.

I did have processor cards fail with line power filters installed.

Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#4

Re: PLC5 Watchdog Timer Issue

11/18/2008 6:28 PM

Is it possible that an unexpected data value with an indexed register or other program "glitch" caused a value of 0 to be written to the watchdog timer's register?

--JMM