voltage drop

11/18/2008 5:24 AM

I need to connect a pressure switch to a PLC, what is the maximum cable distance that i can use as a rule of thumb? considering a voltage of 110VAC

thanks,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: voltage drop

11/18/2008 11:05 AM

A few km?

If it's a worry, consider putting a local outstation near the pressure switch, and sending the switch position as a data signal down the PLC's remote I/O facilities via a network cable.

If transmission speed becomes a concern remember that if a signal in the real world plant changes faster than once per second, it ain't real.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#2

Re: voltage drop

11/18/2008 3:47 PM

If you're going to detect whether the switch is open or closed, the input impedaance of the PLC should be high enough to run it as far as you need. In other words, there should be little to no voltage drop.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Power-User
Hobbies - Fishing - New Member

Join Date: Feb 2007
Location: Suva Fiji Islands
Posts: 229
Good Answers: 3
#3

Re: voltage drop

11/19/2008 5:39 PM

If the pressure switch is close enough to the PLC so that the cost of the cable doesnt outweigh the cost of the PLC and pressure switch you wont have a problem. If you are going to spend $k on cable then using an existing comms cable or telephone network may be a better option.

__________________
"Multa ferunt anni venientes commoda secum, Multa recedente adimiunt". (The years as they come bring many agreeable things with them; As they go they take many away).
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#4

Re: voltage drop

11/19/2008 7:24 PM

Dear all,

Voltage drop will not be a problem as many have already mentioned.

However, in case of AC, cable core to core capacitance will allow some current back into the PLC input even the contact is open. If the cable is long, PLC always detect the high signal even the contact is still open. if the cable length is 500 m or greater, use DC is better.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#5

Re: voltage drop

11/20/2008 11:10 PM

Controller,

The specifications for the PLC's input module should include two vital items: minimum voltage for it to turn on, and current flow through the input. Your good old Ohm's law will then be used: R=E/I = (voltage difference)/(current when on). This will tell you the absolute maximum value the resistance of the circuit can be. Then, given a table of cable resistances, you can determine the maximum length of cable. Since it is a two-way trip, this length needs to be divided by two to give the maximum possible distance to the switch. Finally, you need an engineer's margin of safety, such as a factor of 2 or even 3. Take this maximum possible distance and again divide it by the margin of safety. This will give you the design criteria for your job (such as "cable with cores not less than XX diameter, and length not greater than ZZ meters", using units and wording appropriate for your area).

As an example, assuming 15mA current flow and minimum voltage of 85 volts, R = 25/0.015 = 1667Ω. With a wire of resistance 45Ω/1000' and a safety factor of 3, the permissible distance is: D = (1667/45)*1000/2/3 = 6,200'.

OK? --JMM

Register to Reply Score 1 for Good Answer
Participant

Join Date: Nov 2008
Posts: 2
#6

Re: voltage drop

11/21/2008 3:45 AM

thanks guys for all your comments :)

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Akihito Shigeno (1); Bill (1); coconutpete (1); Controller (1); jmueller (1); PWSlack (1)

Previous in Forum: piezometer   Next in Forum: instruments cabling engineering

Advertisement