Selection of Generator for Motor Starting With a Soft Starter

11/19/2008 1:48 AM

Dear All,

I need to find out rating of the Diesel generator which is required to start a 75 kW motor with maximum starting current of 325 A (only for 2 seconds) with a soft starter. Please advise me how to select the suitable rating of the generator with their special features (if any).

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: selection of generator for motor starting with a soft starter

11/19/2008 4:30 AM

Hello Asitha

Please advise your Location and Country (easily done by you in your Member Profile, then it auto-updates through all your Topics and Posts, including this one)

Is there any other equipment to be connected to the Alternator?

Advise Voltage/Frequency of the motor you have on-site please.

What equipment is that Motor running?

Any other useful factors.

Reply here with and you may receive some assistance.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Commentator

Join Date: Dec 2006
Posts: 88
#4
In reply to #1

Re: selection of generator for motor starting with a soft starter

11/20/2008 11:55 PM

Dear All,

Thanks for your help.

Motor voltage is 3 phase 400 V / 50 Hz use as a high light pump to pump water from a sump to a water tower.

Here i also like to know who much generator can be overloaded for few seconds during staring periods of a motor.

Regards,

Asitha

Register to Reply Off Topic (Score 5)
Associate

Join Date: May 2008
Location: City : Chandigarh, Country : India, Continent : Asia, Planet : Earth, Galaxy : Milky Way, Universe
Posts: 54
Good Answers: 1
#2

Re: Selection of Generator for Motor Starting With a Soft Starter

11/19/2008 10:52 PM

With Soft-starters, the general practice is to over-rate the DG by a factor of 2 i.e. to support start-up of 75 KW motor, 160 KW / 200 KVA DG should be sufficient. Moreover, in majority of the soft-starters, the ramp-up time can be varied upto 20 seconds or so.

Rgds

Sanjeev

__________________
Karma is Dharma
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Selection of Generator for Motor Starting With a Soft Starter

11/20/2008 1:12 PM

I agree, a factor of 2 on the motor kW is a good general rule. So you would use a generator rated for 150kW continuous as a minimum.

You failed to mention the settings of the soft starter by the way, i.e. is that 2 seconds at 500% current, or is it 2 seconds at 350% current? If the latter, you MIGHT be able to get away with a slightly smaller generator, say 1.75 x the motor rating, but that would be taking a chance.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply