sir , i want to calibrate my dp transmitter on -1 bar.
i have no vacuum pump. can any aternate method to calibration.
if i give 1 bar pressure on LP side and open HP to atmosphere?
thnk
hitesh
United States - Member - USA Engineering Fields - Control Engineering - Never enough money
Re: vacuum type dp transmitter calibration
02/02/2009 2:17 AM
In most vaccum applications the LP side is connected to the process and the HP side is open to atmosphere which means you will need to apply 1 bar to the HP side and open the LP side to atmosphere in order to do a calibration.
Good Answers: 54
02/03/2009 8:31 AM
Technically, yes, if you have a dp transmitter your method will produce a dp transmitter that is calibrated to -1 barg.That is, your -1 bar is referenced to gauge pressure which is atmospheric pressure.
If you need absolute pressure, it gets a little more involved.
regards,
Vulcan
02/07/2009 1:42 AM
It is correct, you apply 1bar pressure to LP side and open HP to atmosphere to calibrate transmitter with rang below zero.