Water pipe and pressure

02/14/2009 7:58 AM

I'm running a water pipe from a spring and would like to know if there is any advantage in installing a larger pipe for more pressure, I know I would get more volume, but I'm not sure about pressure due to friction loss. The run is apx 300 ft with 50 Ft on head and I'm thinking of running 3/4".

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#1

Re: Water pipe and pressure

02/14/2009 8:15 AM

If we are talking about schedule 40 pipe the larger the pipe the less pressure it will handle. You will need to look at pressure ratings for what ever type(steel, PVC, CPVC) you plan to use to see if it will handle the head pressure.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
6
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2

Re: Water pipe and pressure

02/14/2009 8:37 AM

The size of pipe that you are talking about - the post looks like the pipe is for some domestic water requirement (not generating power )

The pressure will be lost in the pipe and less is the diameter of the pipe, more is the pressure loss. More is the diameter, less is the pressure drop (ie more is the pressure available at your end) and more is the cost.

For your application with only 50f head any schedule will do.

To know about the pressure drop, you should know the flow rate that you expect from this pipe.

look at this table

http://www.engineeringtoolbox.com/pressure-loss-steel-pipes-d_307.html

say you want 10 lpm water = 0.16 lps (liter per sec)

Then for 3/4" schedule 40 pipe, you have a drop of 1862 mm of water per 100 mt (almost your 300 ft)

So at your place you get a pressure equal to about 50 ft - 1.86mm = appr 44 ft of water

But same one when say you are drawing 30lpm water drops by 15.153 m ie at your end the pressure is almost zero.

having a 1" pipe would have dropped it by 4.3m (approx 12 ft)

and 1.5" by 0.5 mt (approx 1.5 ft) ie you get 48.5 ft equiv pressure.

Look at the tables mentioned in the link (with a pinch of salt ) since it assumes straight pipe, no bends, no joints (and no choking up )

Slightly overdesign for future friction lossed due to age.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Good Answer (Score 6)
Guru
Engineering Fields - Systems Engineering - New Member Popular Science - Weaponology - New Member

Join Date: Jun 2006
Location: Borrego Springs
Posts: 2636
Good Answers: 62
#4
In reply to #2

Re: Water pipe and pressure

02/14/2009 10:04 AM

GA!

__________________
"If you want to get somewhere else, you must run at least twice as fast as that!"
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#13
In reply to #2

Re: Water pipe and pressure

02/15/2009 7:44 AM

Hello sb,

Wish I was as clever as you.........Good explanation Sir........GA!

Take care .........................

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#3

Re: Water pipe and pressure

02/14/2009 9:10 AM

If you use a bigger pipe with the same flow your pressure will increase. The friction loss decrease with pipe size.

However outlet points or emitters will discharge more water when the pressure increases.

For normal domestic and watering animals you will almost be assured of a higher pressure with the bigger pipe. With the same number of emitters it is impossible to have a lower pressure.

Note the pipe class should be determined by the static height (closed valve situation) and not the reduced pressure due to friction loss.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#5
In reply to #3

Re: Water pipe and pressure

02/14/2009 11:23 AM

That is easily taken care of by reducers and taps as well as smaller diameter tapping points at the user end (it is done with the domestic water line isn't it ? the water is usually transported in a few ft dia pipelines.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#6
In reply to #5

Re: Water pipe and pressure

02/14/2009 3:45 PM

Hi sb

A lot of people mistakenly take increase of velocity in a smaller pipe as an increases in pressure.

In my youth I was assisting in a column in a farmers periodical regarding technical questions and came across some funny ideas.

One farmer had a siphon over a valley with a smaller pipe on the uphill side. He and his neighbours assured me he gained a few feet that way. He did not trust my theodolite proof as well.

We have a case here on a golf course housing scheme where the pipe class was reduced because they are using PRV'S only to find out that the PRV's do not work on small flows and the pipes are bursting.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#7
In reply to #6

Re: Water pipe and pressure

02/14/2009 10:55 PM

you can use the PRVs on smaller flows as long as you have a pressure relief valve. This means some water loss, bu on a gold course this water bypassed by the relief valves can be returned to a watering system and used when they water the grass.

__________________
Per Ardua Ad Astra
Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#10
In reply to #7

Re: Water pipe and pressure

02/15/2009 1:30 AM

Not in this case (it is a 800ha housing scheme with a golf course)

The cost of the piping to drain the "leaking" water to the nearest common point is more than the original saving on the lighter pipe class.

It is also dolomite area and a leak into the soil will cause a sinkhole.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Participant

Join Date: Aug 2008
Posts: 3
#8

Re: Water pipe and pressure

02/14/2009 11:38 PM

First of all let us understand the relations beween the capacity of water flowing through the pipe measured in GPM /LPM etc and pressure or head of water column and the diameter of the pipe. If we keep the the pipe diameter as constatnt at 3/4" then with increase in the capaciry there will be higher friction losses which will result in requirement of higher pressure or head of water column for pump to dvelope to deliver the water up 50 fet verticle head. Assuming that flow capacity is constant, pipe size constant with 300' running pipe and 50' vertical head, pump will be required to devlope a pressure head that will be equivalent to 50' of water column(A lbs/Sq Inch) plus the Friction loss head due to the water flowing through 1) 300 feet horizotal pipe( B lbs/Sq Inch)+ 2) 50' verticle pipe ( C lbs/Sq Inch) + 3) Friction losses through the number bends, couplings etc in 350' pipe line( D lbs/Sq Inch)

Since cpapcity of flow will be available in pump performance chart the friction losses can be found out from the friction loss tables generally available with all pump manufacturers. Thus the the total head / pressure required to be developed by the pump will be equivalent to A+B+C+D Lbs/Squ Inch. Since the cpacity and head developed by a pump are limited by the size & the hp of the pump selected, only thing that can be made variable will be the pipe diameter. With increase in delivery head / discharge pressure due friction losses the pipe size has to be increased to minmise the firction losses to deliver whatever capacity of water available through the pump to 50' of water column.

Chitaranjan Nagrecha

Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#9

Re: Water pipe and pressure

02/15/2009 12:40 AM

Hello digger,

If you increase the pipe diameter, you will increase the flow rate, but decrease the pressure.

You say that you are thinking of running 3/4" pipe - instead of what?

What is your desired flow rate?

You have not given enough information as is so frustratingly prevalent on this site.

Mike

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
3
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#11

Re: Water pipe and pressure

02/15/2009 1:53 AM

"If you increase the pipe diameter, you will increase the flow rate, but decrease the pressure"

This or similar statements are untrue.

Let us consider this case.

1 Spring in the hill 50ft higher than the use / discharge point.

2 300 ft of gravity feed pipe.

3 Fixed number of outlets and use.

Say he has one sprinkler working at the end of the pipe.

With 3/4" pipe the sprinkler will discharge Q at a working pressure of P. Where P = 50ft - losses.

If the pipe is now changed to 1" the sprinkler will discharge more.

For the sprinkler to discharge more you will need a higher working pressure (check on the performance chart of sprinklers)

Any outlet or orifice places restrictions on flow and more flow must require more pressure.

Don't mistake velocity for pressure.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply Good Answer (Score 3)
Member

Join Date: Apr 2008
Posts: 5
#25
In reply to #11

Re: Water pipe and pressure

02/26/2009 3:54 AM

Its 2.5 k.g. pressure

Register to Reply
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#12

Re: Water pipe and pressure

02/15/2009 2:30 AM

Pertinent is of the number of elbows and T's in the 300' run

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply
Associate

Join Date: Jan 2009
Posts: 47
Good Answers: 1
#14
In reply to #12

Re: Water pipe and pressure

02/15/2009 10:15 AM

What I'm doing is running a 3/4" line gravity feed from a spring to a barn apx. 300 ft with the black water pipe with no bends or 90's to a watering tub and a hose which I would like to have a fair amount of pressure, If going to a larger pipe will give me more pressure that is what I will do, the flow seam to be not a problem, there is a 3/4" pipe already there that we are replacing due to age. we would just like a little more pressure if installing a large pipe would do the trick. The spring is apx. 50 ft above the barn.

Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#16
In reply to #14

Re: Water pipe and pressure

02/15/2009 10:27 AM

Hello digger104:

Not sure if you have been reading the other posts at all? It seems as if you have the idea that a larger dia pipe with give more pressure?...................IT WON'T!!!

If you want a larger capture then use a drain pipe if you want but, reduce it to ½" and you will have brilliant pressure.

You will be wasting your time if you run a larger pipe all the way to your greenhouse. All you will have is a good pond filler.

No offence meant here OK?

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#17
In reply to #14

Re: Water pipe and pressure

02/15/2009 12:26 PM

Hi digger104

I disagree with babybear

If you replace your gravity pipe with a bigger pipe you will get higher pressure because of the lesser friction losses.

It will however never be higher than the 50ft static.

For using the hose for cleaning purposes a bigger pipe with a smaller nozzle would be the best. The hose should be limited in length because it also reduces pressure due to friction loss.

Ask your pipe supplier for friction curves,

You can determine the maximum percentage volume increase by going horizontally on the curve.

Your maximum pressure increase can be determined by going vertically on the graph.

Your actual duty point will be somewhere between the 2 maximums - that is higher flow and pressure.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#18
In reply to #17

Re: Water pipe and pressure

02/15/2009 1:43 PM

Hi digger104

From sb's tables

At 4.8 GPM your pressure at the outlet will increase by about 40%

At equal frictions your flow will increase by about 40%

A rough guess with a 1" gravity line your flow and pressure might increase by 20%.

That is 4.8 to 5.7 GPM and 32.6 to 39.2 ft pressure.

Whatever you do don't go for a 1/2" pipe your flow may drop to 3 GPM and your pressure may drop to 20 ft.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#19
In reply to #18

Re: Water pipe and pressure

02/15/2009 3:09 PM

Hello Hendrik,

Hope you are OK?..................With regard to my post I did say he coulc run a drainpipe to the user end. And although I did not make it clear, I meant run 1/2" for the last 6", to allow connections at the spray end to be high.

Can you confirm that would actually give a higher pressyre on the spray?

Take care.....................

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#20
In reply to #19

Re: Water pipe and pressure

02/15/2009 5:02 PM

I did not read much further than the won't ,

A 1/2" (or smaller) nozzle or short pipe at the end should give him a higher velocity for some tough cleaning jobs.

He would for sure get a better pressure with 1" pipe.

A bigger than 1" pipe will give a better pressure but the gain will now be small and it will not be cost effective.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru
United Kingdom - Member - Not a new member!

Join Date: Jun 2008
Location: USA/Europe
Posts: 4547
Good Answers: 68
#23
In reply to #20

Re: Water pipe and pressure

02/15/2009 11:03 PM

Hello Hendrik,

Just wanted to clear a point up in my own mind, thank you ........

Take care...............

__________________
Take it easy, bb. >"HEAR & you FORGET<>SEE & you REMEMBER<>DO & you UNDERSTAND"<=$=|O|=$=>"Common Sense is Genius dressed in its Working Clothes"<>[Ralph Waldo Emerson]
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#21
In reply to #14

Re: Water pipe and pressure

02/15/2009 5:47 PM

Keep the 3/4" supply add a manifold and a tank with capacity of water necesary for hose use, plus a bladder to increase pressure.

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply
Guru
Popular Science - Cosmology - New Member

Join Date: Feb 2009
Location: Halcottsville, NY
Posts: 665
Good Answers: 16
#15

Re: Water pipe and pressure

02/15/2009 10:21 AM

FROM PRACTICAL EXPERIENCE: I have a similar setup and 3/4" plastic is fine for domestic use. Anything larger than 1" is overkill. One possible problem is air lock, which I remedied by adding a "T" port and access at a hump in the line. Use an oversized strainer at the springbox and keep surface runoff away from your collection area. Freeze up is another problem here in the Catskills of NY.

Good luck, Carl

__________________
De gustibus non est dispudandum.
Register to Reply
Anonymous Poster
#22

Re: Water pipe and pressure

02/15/2009 8:51 PM

50 ft of positive head will give 21.65 PSIG of pressure.At a no flow condition, a gauge will read the same at the end of a 300 ft pipe of any size. When flow begins, losses begin., the pressure drops.The more flow, the more loss.The larger the pipe, the less loss per linear foot.A 1 inch pipe will carry 4 times as much water as a 1/2 inch pipe.Your pressure will never exceed 21.65 psig no matter the size of pipe.The velocity, however, can be increased at the end of the line by reducing the diameter of the tap off, such as a nozzle.The pressure will remain the same, however,but it will appear to have more pressure due to the increased velocity. I would go with a 1 inch pipe.It will carry nearly twice as much as a 3/4 pipe.The cost difference is negligible compared to a 3/4 pipe. Good luck. ------------------------------- HTRN-----------------------------------------------I am a kleptomaniac, but when it gets really bad, I take something for it--------

Register to Reply
Anonymous Poster
#26
In reply to #22

Re: Water pipe and pressure

02/28/2009 9:07 PM

It seems like everybody has been arguing apples vs oranges. Pipe size will not effect static pressure... as stated above it is the same with any size pipe. Pipe size will effect dynamic pressure; entirely based on the volume passing through the pipe.

Register to Reply
Guru
Hobbies - DIY Welding - pipewelder

Join Date: Apr 2007
Location: North Georgia, USA
Posts: 671
Good Answers: 33
#24

Re: Water pipe and pressure

02/16/2009 1:19 PM

Hello, If it were me I would run a 1"-1-1/4" pipe. If you use the same size nozzle you will increase the pressure closer to the maximum 50ft head because less friction. But I don't think it will be a very big pressure increase any way you go because 50ft of head is what your pressure is derived from. Personally I would not go any bigger than 1-1/2" though because the increase in pressure will not be great enough to justify the cost of bigger pipe IMO. I also would not run run black pipe for water but rather hot dipped galvanized pipe because it will last allot longer. If you want more pressure look into installing a booster pump with a stand pipe in order to prevent cavitation.

__________________
pipewelder
Register to Reply
Register to Reply 26 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); aurizon (1); babybear (4); bwire (2); CHITUBHAI969 (1); digger104 (1); edignan (1); Hendrik (7); Mikerho (1); ozzb (1); pipewelder (1); sb (2); sudhirpatel (1); Tippycanoe (1)

Previous in Forum: About piezo buzzer   Next in Forum: Graphic Card question .

Advertisement