02/27/2009 1:47 AM
dear all,
just a little thing that make me curious,...
why in NEMA/ ANSI motor, it uses "HP" for rating motor.while if we calculate for FLA , the formula is like below :
FLA = FLC = (HP*0.746)/(√3 * kV * cosθ * eff)
isnt it better if the name plate state power in KW only?? so, we dont need to multiply by 0.746 ?
Good Answers: 97
Re: why do we use HP for rating motor ?
02/27/2009 2:21 AM
It is the prerogative of a country to decide which units of measure will be used or which unit of measure will be allowed for import.
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing
02/27/2009 2:31 AM
dear
R U School student?
The motor is machine which works with Input as electrical energy unit of which is KW, convert it in to mechanical energy unit of which is H P (Horse Power)
NASCON
03/03/2009 3:17 AM
R U School student?
I am not talking on behalf of elect-ok. But, even if he is scholld student, he is right and you are wrong. You need to go to school again, in some other school, if your school has taught these things.
Electric motor input is in electrical form in watts and output is in mechanical form in watts.
I also get surprised, how we Indians behave like this ! Concepts of Indonesian are clear than you. Please read all the post very clearly and try to understand the concepts.
03/05/2009 4:03 AM
hahaha....
thank you GURU. Actually i have been working in Electrical Contractor about 4 years...start from Small House (residential) Contractor, now in Industrial Contractor.
I think this forum is very useful to share our knowledge......and to see how electricity installed in every different country...
Good Answers: 137
02/27/2009 3:39 AM
Yes, definitely. In most countries motor rated power is given in kW. HP is still used in USA for historical reasons.
Cheers..........Codey
02/27/2009 5:08 AM
Learn all the acronyms, find out which country it was originated and you will understand why NEMA and ANSI use HP instead of kW.
Good Answers: 103
02/27/2009 7:37 AM
Please check up, it is in one of the previous threads. It is just an convention (since a lot of people are still quite comfortable with HP rather than KW) -
To a lay man the 5HP pump is more meaningful than 3.7KW.
Since the motor is selected to drive the load and not the otherway around, the backward integration applies.
But now in SI units, we specify our loads in KW only and then the HP becomes redundant/confusing.
02/27/2009 7:46 AM
why call it hp? there is a very interest story. let me tall you all.
once upon a time, there was an engineer who was a friend of Farady, he invited motor by the secret paper given by faraday. one day faraday went to see his friend by horse, when he saw the strong machine, he asked how strong it is. and I hope to know. as see he ride a horse, his friend replied, ah, it has as strong force as three horse you ride. scince then people begine use HP for measuring the motor.
haha, is it interesting?
add score...
02/27/2009 1:18 PM
Cnpower has it sort of correct.
James Watt, the inventor of the modern* steam engine, needed some way to quantify the output of his new engine. Before the steam engine, motive power was supplied solely by draft animals. Watt decided to compare the power output of the steam engine to that of a horse. Hence, "horsepower." Watt was quite conservative. The amount of power represented by one horse power - 550 ft-pounds per second - is a level the horse can only exert for a short period of time, whilst a steam engine can output its rated power over its entire life.
This was all before the invention of the MKS - SI system of units. Note the modern unit of power is named after Mr. Watt. As others have posted, it is the prerogative of a sovereign nation to decide what units will be used. The USA has been trying for decades to shift from the English system (which the English abandoned decades ago) to the MKS-SI system, but our citizenry is just too set in its ways to respond. Myself included.
And sometimes, the MKS system is just stupid. For instance, there was the perfectly good dimension of length known as the centimeter, but it was not a triple order of magnitude away from a meter, so it can't be used. Result: engineering drawings either in meters or millimeters, only.
Take an aircraft. Aircraft locations are done by station numbers, which traditionally in the USA was does in inches. When the went to MKS, they had to use millimeters. 25.4 mm per inch, right? So now station numbers could be in the tens of thousands, instead of hundreds, and no extra useful information was imparted. Centimeters would have been a useful substitution, but - it's not allowed.
* Crude steam engines antedated Watt's by one hundred years, but Watt's refinements actually kick-started the Industrial Revolution.
Good Answers: 39
02/28/2009 12:01 AM
Just be glad a french initiative to metricate time and lat long degrees never came to pass. Some metric enthusiasts wanted our time keeping to be shifted to decimal time and divide the day into tens and hundreds units.
And the even more ridiculous notion to shift from 360 degrees in a circle to dividing the globe into decimal increments. Right now one minute of latitude equals one nautical mile. simple, easy to remember and easy to calculate/estimate distances. Needless to say that particular initiative did not stand up to a peer review. At least James Watts had a real world basis for his units of measurement.
Elnav
Good Answers: 68
02/28/2009 8:12 PM
Hello elnav,
For some things Metrication has made life easier. But as you say there is certain instances where the 'norm' was worked out hundreds of years ago and actually describes a length or distance precisely. It does not need changing.
Having said that, it is the 'jobs-worth' (more than my jobs worth to allow that etc) brigade who have the job of implementing this law. Sometimes they do a good job. Others, they make themselves and the country they are employed by look like idiots!
It was mentioned in a previous post about the airport parking stages. It makes no sense whatsoever! Critical small measurement like pipes etc fine. But when aircraft parking changes pretty often anyway with increasing plane sizes, it is a complete nonsense to use such a small measure to quantify that distance. It would have made more sense to have based that parking area for planes on the DC10 wingspan?
Take care................
02/28/2009 1:38 AM
emc,
The reason people like the Inch, foot, lb gallon is because it scales to the human body much more than the metric system. My thumb is 1 inch wide; my foot is 1 foot. A foot scales to a human's height and an Inch scales to a human's hand. I know what a in^3 is by my thumb, and I know what a ft^3 is by my foot. I can therefore design with it. When I hammer a nail and space it 1 inch, I can use my thumb… I have no idea what a cc^3 is, nor a meter^3, let along what a N, kg or anything is because it has no connection to anything I use. People who design houses know what I am talking about…
The inch system is based on the mean polar radius. The original proposal for the Metric system was also the mean Polar radius...but there is a problem...First, the inch already had that idea taken, second, to get that mean radius you need an orbital satellite...and this is 1800's… That inch is found in the Giza...someone knew that measurement... how?...Moses?...Pharoah? By using the inch, you are saying..."God" (or at least Captain Kirk or NASA) existed 3-5 thousand years ago…politically incorrect...and the motive of the French was to tear down the old order...so they chose the arc length from the north pole to the equator running through…Paris and other French places, which they actually measured, and not exactly accurately…
The polar mean radius is the longest straight distance on earth (and is how you would characterize a planet, since the center of gravity and the radius…). It is the most stable distance due that it is the longest dimension, whereas the arc is not something anybody would use as a standard, unless you are a politician….
The polar radius (cubit/inch system), and arc length through Paris (meter system), are both divided into 1/10 millionth. The original meter is therefore 1/10 millionth of the arc length from the north pole to the equator, and a ("sacred") cubit (25 inches exactly) was divided into 1/10 millionth.
Another reason the inch system is MUCH better is that it can be made factored by 2, 3, 4 and 5, whereas the meter is only by 5. The reason the cubit is 25 is that 5 is an important number and good for stepping off distances while walking normally. The number 6 is 2x3, and the second is a 60 base number, and there are 7 days… The equator radius is 1000 years in feet…
Which goes to the central issue of INCH vs METER. The inch is earth/earth. The meter is politics/earth. Time is based on the rotation of Earth (at least it was). Ask why they did not make a minute have 100 seconds if making decimals is the reason. Because the reason for going with meters is political, NOT scientific. The inch can be mille-inch, kilo-inch, centa-inch, and can be expressed in decimal form just like the meter. The meter and scared cubit (25 inch) are analogous.
The reason we use a dozen is because it can be divided by 2, 3 and 4. 10 of something cannot be divided by anything but 5. If you have 12 friend, you can send them by 2, 3 or 4, but if you have 10 friends (or board members) you cannot divided up tasks in whole numbers.
Most people don't realize that the Romans used a gallon with 216 in^3, which is 1/8th of a cubic ft^3 (12^3=1728…/8=216). The Roman gallon was 6 inch x 6 inch x 6 inch. It was a size that was small and useful, and when you look into history, that is what was used…along with all the scale sizing…of building and ancient technology…history…is lost with the meter, and the "patterns" are lost in the numbers when we switch to the meter….
Last but not least, the inch system is much easier to remember. Nobody knows what a centi, deci, kilo, Giga, mega, or whatever is…go ask your wife or kids…unless you are an engineer or science guy. You have to remember two things to know what you have, which is NOT efficient.
So, if we as engineers were smart, and honest, we would use the inch system, and have the gallon have 216 in^3 and not 231 in^3 found in our queens wine gallons. Which reveals that the English were dunk from all the wine they were growing in England…(midevil global warming?)… Hmmm, and the French were totally out of control and their measurement system was completely irrational…I see a pattern here… (nothing changes). It is sometimes easier to change a system that is totally broken (the French system before the meter) than a system that is a little "drunk" and arbitrary (wine gallon).
We need to fix the Inch system and base it in the human experience, and not French (now EU) politics. The mean polar radius is the only neutral measurement on the planet that includes all nations, and not just French people. We need to take the garbage metric system and toss it in the political waste heap of all such "French" ideas based on ego, hubris, and totally unscientific notions… You cannot call yourself scientific and base your measurement system on an arch length…sorry but at the foundation, the meter system is a joke. It is now based on the frequency of…which is based on time, which is time is based on…what? What a total joke… Our so-called scientific system is a circular loop and totally unscientific!
So, we need a power measurement system that relates to a human. A human can get on a cycle and pedal at about 1/12th of a hp. A human power "H" would therefore be 550 INCH-LB/sec, and not FT-LB/sec. In KW that is 0.11175 KW, or about 110 watts. How many people know what one human can produce in terms of power? Easy…1 H…
When you get in your car, you know how to relate it to you. A H= hp/12. Your 175 hp car has 2100 H power. Your car runs at highway speed on 1/10th (17.5 hp) or about 210 human power. A really good car should run on about 100 H power (8.33 hp, 6.2 KW). The average Joe can understand Human power, but has zero idea what a KW is. Can we just stop the Metric insanity…please…. If you want people to save energy, put it into terms they can relate to, and not a kilowatt…what is that…a spray to kill bugs?
So, if you ask the average person what a KW-hr is, they would likely say it is one hour of swatting flies as fast as you can! Please, stop this arrogant nonsense called the Metric system… We are Humans, not a cows, monkeys, horses, or pigs…we are humans, and last I checked, monkeys, cows and pigs don't go shopping, drive cars, live in houses, or engineer things. When a monkey can do the math, then maybe we should have a "universal" system that includes other creatures found on this planet. Woop, I forgot, we do have pigs and monkeys running our governments…now I understand…Maybe we need humans in our governments again before they send us all into complete Depression and world war…
In the mean time, lets straighten out the inch system, which is a truly scientific system because it is based on the mean polar radius, and eject the metric system from this planet, along with all the monkeys and pigs in our governments…
Good Answers: 103
02/28/2009 2:14 AM
So we go from converson from CuInch to Cu-ft with 123 = 1728 multiplication instead of a round figure of 103 ? to prove that we are not cows and....
Please also remember the SI system is not only in terms of the units but also it is a decimal system (ie the units are base 10),
Except the physical constants of course.
This is totally based on your architect's comfort. Over here our people are comfortable with some other units (and we too some times say that it is the best)
But end of the day the level of comfort is much higher for the SI system. and that is not for the units per se this is because of the unit convertibility factors.
Only the time and angles were not decimated due to historical reasons.
especially when you are going for complex calculations.
try Changing from Kg/m2 to g/cm2 it will be all in 10s
The same will not be when you do it with T/ft2 to PSI.
Next are you going to say that since we are not cows we will like to have the multipliers and converters as complicated as possible .
03/03/2009 10:25 AM
SB,
Every claim of "comfort" that you claim with the SI system could be had with a meter=25 inch = cubit = 1/10 millionth of mean polar radius.
Why have the meter based on an arc? It makes no sense.
Ask yourself why Napoleon would spend all that money to measure the earth's arc? Was it a "bailout" jobs program? Why would the French not just adopt the inch which the English had and was used by the Romans (Italians, Germans) and others back to Giza?
The meter is a long distance. It is just a length. Why are you so against change? Change we can believe in...
By doing what I suggest, the English system would have been absorbed into the metric and we would not have an issue. If you want to decimaltize the measurement, use the cubit-meter, if you want to use inch, then use it. Tools could be made that seamlessly mesh. Weights would also be made common, and we would have ONE standard. Now all we have is an arc length as a standard...what a joke.
Good Answers: 38
03/03/2009 7:14 PM
The French use the measuring system of their hated enemy the English, incroyable!
You forget nationalism is also a big factor to adopt a measurement system.
02/28/2009 3:23 AM
Fascinating insights - into your personality.
I agree units should be of useful dimensions, hence my example of using millimeters vs. inches.
To argue that the basic unit of power should be based on what a human being can exert only makes sense if humans are the basic source of motive power. Even before the Industrial Revolution, brute force labor was done by draft animals controlled by humans. Hence the unit of horsepower, as noted earlier.
I made and make no argument for the adoption of the metric system for general use in the USA. But as an engineer, if you are telling me I have to stop using Watts and Joules and have to calculate in BTUs per hour and velocities in furlongs per fortnight, I have a major problem with that. There is a tremendous advantage to a decimal based system; I see no specific advantage to the ability to divide by other numbers besides ten to get whole number quotients.
And I take issue with the generic statement that English units are intrinsically easier to remember and use. When I am cooking, I always have to stop and think: two cups to a pint, to pints to a quart, four quarts to a gallon. Three teaspoons to a tablespoon (I think). How many teaspoons or tablespoons in an ounce?
Compare that to the use of liters, deciliters and milliliters. Sorry, no comparison.
And here's a really good one. If anyone, and I mean anyone, forwards this to the Transportation Security Administration, I will personally come to your house and thrash you within an inch of your life. File this under the Clintonian heading: "That depends on what the meaning of an ounce is."
Like many, i have to travel, and sometimes I have to fly. Since 9/11 flying sucks. It sucks even worse since the benighted fanatics tried to smuggle ignitable chemicals on board aircraft, disguised as baby formula. The miserable result of that unsuccessful attempt is to limit carry-on of fluids to three-ounce containers.
Now I have a particular toothpaste I use, and it is not available in the travel size dispensers. It comes in six ounce tubes, which aren't allowed in your carry-on. But I can squeeze out the entire six ounce tube of toothpaste into a three ounce container specifically designed to be acceptable for this very purpose of carry-on liquid containment.
Now clearly there is some confusion at the TSA about ounces as measures of volume, or weight. I submit that if we were using the metric system, this wouldn't happen. If liquid quantity were to be controlled by volume, it would be milliliters, and if by weight (mass, actually), it would be grams. The fact that one milliliter of water masses one gram is not a conversion factor for any other liquid or substance...
None of this is an argument for the USA adopting the metric system. It is however a spirited rebuttal of a post which seems somewhat fanatical in its own right, and arguments that don't appear to have much if any logic behind them. In fact, I can imagine hotheads like Robespierre and Danton at the height of the revolution tossing off similarly vituperative rhetoric about the need to dump the old system and adopt the metric system; at least when they weren't calling for someone's head on the chopping block.
02/28/2009 1:04 PM
Both have their advantages and disadvantages.
Much has to do with what we're used to working with.
I have to deal with both because I do work for a French owned company.
02/28/2009 4:48 PM
emc,
The central issue was the mean polar radius vs. arc length. You just glossed over the 800 lb gorilla…. The other issue is that time is a 60 base system, and NOT a base 10 (deci) system. If the Metric system designers were honest and had even an spec of credibility they would NOT use a time system with a 60 base system, with 12 hours, and then base the length of that standard (meter) in a frequency, which is a time base (60 base) system. The metric is a mix of systems based on 60, 12, 10 bases. This is insanity!
If the foundation of a system is corrupt, then the entire system is corrupt and makes no sense. A house built on sand (arc length) will not stand.... Making it decimal (base ten) does not mean it has any advantage because the inch can be decimaltized also, with all the kilo, milli and prefixes that everybody cannot remember. The core is the standard and the metric is completely unscientific at the core. Any measurement standard should NEVER be taken on an arc. That is what the Meter is based in. It is garbage from the beginning...
I can make in^3 be called a linch and do Milli-Linch, deci-linch...now quickly tell me what that would be... you can't, but you could tell me what a gallon or pinch (pint) would be. If you were on an island, would the average Metric user know how a liter relates to a Meter^3? No! I am in the real world, and most Metric government types are in some chemistry lab. Nobody knows this stuff. Why? Human nature...more below...
The fluids should be based on the in^3 and Ft^3. This give two scales or ranges of sizes. A gallon should be 1/8 of a Ft^3 (216 in^3), and not 231 in^3, or 6 inch by 6 inch by 6 inch, which anybody can do in their head. Take that 6 inches in half you get 1/8 again and you have 3x3x3=27 in^3 or a Pinch (like a pint). These are basic blocks that people find useful, and this is how people think in real life. The world is not an even 10, which is the only time a deci system has any advantage, and the Inch, again, can be done in deci just as well. 500 ml? Why not 5 xL? Or 50 xl? It does not scale to people that is why. You get trapped in the big numbers. There is NO honest reason for the Metric system if your claim is that the math is simpler...it is not. Why? Human nature and how the brain works...
A drink should be in IN^3. People can use In^3 below 27, or just use In^3 all the time. The average human mind cannot really understand numbers above 25 or so. A mind is a 4-6 bit computer. One cannot visualize more than a dozen, and 24 is two dozen, which is two bits of information. To do metric, I need to know what a milli is, then I have to know what a liter is (a decimeter^3). Since there is no reference to my body (inch---thumb) I then only know what a Liter is because I am comfortable with it, which can be done also in INCH. I have no idea what a M^3 of water would weigh, nor could I ever lift one to get a feel for it. It is just a number of no meaning. A Ft^3 weighs 62.4 lbs, or about what I can lift at the limit without back pains. 1/8th of that (a Roman gallon) is about 7.8 lbs. Ah, now the mind can reference equal parts and say, give me…4 gallons, or about half of what I can lift.
Why don't people quote their height in inches and not feet? The mind thinks in rough cuts or relative blocks or real whole numbers, not in decimal and then the mind references it to something. 6 ft and 1/2 feet is much easier than 78 inches because of the way a person's brain works. The first reference is the foot, and there are 6 of them, and ½. That is three bits. To do that in metric is not possible, because nobody knows what a meter (39.37 inches, 3.28 ft) is. Second, what is 1.98 meters and how does that relate to other people…I know it is near 2 times the standard, but what is my wife's height at 1.77 meters…hmmm.. Lets see…98-77 is 21…ah millimeters…which is 21/100th of the standard…which is what…have no clue, because the standard is clueless, or relative to nothing I know. There is no natural scale to make the relative comparison to, whereas the foot is the scale of a human. You reference how tall you are by the relationship to the scale, not by the number. The absolute is meaningless. It is just a number…
Your thumb shows you what you get in an in^3, but I have not a clue what a decimeter...woops, was that cubic or linear...hence the liter...Get the point. You have to make the linear, area, and volume designation in a deci system, so you end up having to brand it with a unique names, such as liter to imply the volume, versus the linear decimeter... Which is totally confusing to 99% of the population...
1/3 is .3333333…. By saying one third, I am also saying the infinite series. Pi is 3.14159….. Why do we use pi instead of the deci 3.14, or 3.1415, or? Because you have full control of the accuracy. The human mind cannot understand 100, or 1000 directly. It can understand 10 because we have ten fingers at a relative quantity. The mind then thinks either 1 unit of hundred, or 10 x 10, but 100 is beyond the bit capacity or shelf space of the mind to visualize (key) what 100 units is. Try it. Visualize 100. You can't. One unit of a thousand is ok, and it only takes two bits of information to think with it. Why do we use trillion and not 1,000 billion? The mind thinks in scale blocks, and the deci system forces 100, and 1000, which the mind can only relate to via complex bit relationships. Just listen to any news cast. Ask the reporter what a trillion is in billions, which is what.
You have to remember the prefix code thousand, million, billion, trillion, which is different than the science code kilo, mega, giga, tera… Maybe the metric guys need to tell the money guys to change their system with all the banks going under… Ah, I get it, a bag robber gets money by killing (kilo), the white collar criminal get his money by doing mega frauds, and the government steals by giggling after they sign a law, and the "One" does it by tarring the fabric of reason from our eyes… The bigger the lie the better… Got it…
What is a watt? Do you have any idea? Let me help you. First off, a watt is a name of someone, and not an insect that gets into a light shade. Second a watt is a N*M/sec…but what is a N? N is a name of a person—Newton, and is not a cookie with fig filling in it. Ok. What does that have to do with anything? Ah, Ego… So, how big is a Meter? …show me… The average Joe is then looking around to reference that meter length to something he is familiar with…nothing on the body works, hands, foot, car door, a ladies rear, his rod, nose, dog, cat, hamster, ah, the mother in-law's rear… hmmm…help! relative to what is the first process that leads to an iteration and blank stare. This is what the mind is looking for, which the meter does not provide. There is a reference vacuum, just like a power vacuum, where crooks jump into steal people of their stuff.
So a Newton is what again? Is it a force like a weight, like a kilogram…which is…a mass, …please help me out here… Kilo=1000=10x10…Ok (just did three conversions, by the way), and a gram is what…a very small thing…indeed (wink, wink). So you want me to take a very small thing (you fill in the blank) , and multiply that by a large thing…wait a second…ah…a second is 60 base…I give up…this is VERY difficult for the average person. Ah, then that person goes to the store and buys a kg of cheese, and it weighs 9.81 time more Newtons, which means he must multiply 9.81 to get the weight. Hmmm. Try doing that in your head…good luck…pull out the cell phone guys… Lbf and lbs mass is much more easy for people who don't live on space ships…which is 99.999999% of the world…Get real…
The bottom line is you should make a system that serves the people and not the other way around. The metric system has many internal logic flaws, such as the decimeter/liter confusion, that destroys the ease of its use, and is founded on an arc, which any first grader knows is not smart. On the surface it looks simple (and so can a deci-inch system), but when you work it, it requires a lot of informational processing just to do simple things, which is NOT what the human mind does best. Just ask Al Gore…
Good Answers: 15
02/28/2009 3:30 AM
That discourse is the largest heap of bovine excrement I have read in a long time.
Chas
02/28/2009 10:57 AM
I think your ego is getting in the way of actually understanding what you read, if you really did read the whole thing.
If you're going to disagree with someone that has produced a well written piece on the subject then you should be producing something of your own to support why you disagree with it.
Other then it being easier to do math by 10's, and that's about the only argument I've ever heard for justifying the metric system, there's nothing else that supports it.
Even metric nuts and bolts have to have Loctite put on them to keep them from coming loose. It's because of this that Theodore Roosevelt ordered having a standardized nut and bolt size system established, after taking over the endeavor of building it, because of the metric fittings on the Panama canal being such a problem with everything coming loose all the time and none of the nut and bolt manufacturers in the United States made nuts and bolts that would fit those made by another company.
So what do I do to measure a distance without any tools?
I can pace it out, one foot in front of another and easily estimate a mile, but then I have to multiply my number by 5/8 so I can tell you what it is in kilometers. It's inefficient.
I know how the French are by nature. I work with them and they are stubborn. You have a company there in Roda, Spain that I work for division in the United States called MAF Industries. We have a few French Nationals that work here that have told us that they prefer working with us more then they do other French because we are easier to work with and get things done.
Good Answers: 15
03/02/2009 7:00 PM
I didn't know that loctite existed in Roosavelt's time!
I work with both metric and SAE threads. I have never had any issue with either coming loose when applied properly.
As for the argument about the mile versus the kilometre it holds no weight. Whether you pace out 1760 yards for a mile or 1100 yards for a kilometer the accuracy depends on your length of stride.
(ORIGIN from Latin milia, plural of mille 'thousand'; a Roman mile consisted of 1,000 paces (approximately 1,620 yards).
regards
Chas
03/03/2009 1:45 AM
Not sure how or why metric bolts come loose more or less than any of the other myriad of threads. I would be interested to hear.
It is even less clear to me what the preferences of French Nationals to working for or with people other than their own nationals has to do with this subject.
Nor, I must say, do I have any great need in my engineering profession to worry about how long your stride is if you have left your tools at home? Does not sound like a reason for maintaining a specific measuring system.
Good Answers: 120
02/28/2009 8:21 PM
The Furlong, Firkin, Fortnight system comes to mind, and then there is rating beuty in Helens, one Helen (H) is enough beauty to launch 1000 ships, from which we get the
other units mH, and uH.
and then there is the L, a unit of reproductive power equal to one E(Engineer) times one H.
and a host of others in first year Engineering in 1958, most of which are scarcely printab;e
Per Ardua Ad Astra
03/01/2009 12:43 AM
Aurizon,
You forgot to add in the metric system to the waste heap of measurement systems. Each system has a reason, which usually is to make the math easier, or scale something relative to some size so the a human can use it without a calculator.
What is the reason for the metric system? Politics?
It does not make the math easier, as I explained in depth above. It serves no purpose in science because it is not scientific, since no real scientist would use a system based on an arc, nor would they use one that has a circular loop of distance and time (definition of the meter is a function of time...), or would they use one that mixes three number base systems (60, 12, 10), and then claim it is simple. Most people don't even know what base anything is, let alone 60, 12, or 10. Can we get a grip here people???
Now we have kilo, mega, giga, tera in measurements of physical properties, in place of thousand, million, billion, trillion which are used in most other things, such as money and numbers in general, but when you use the EU mandated metric system you must learn some alien system...mega? giga? tera? Huh? What a load of garbage...and arrogance in the extreme.
Should we say that the bailout is 9.7 tera-dollars, instead of trillion-dollars? Or some friend of a congressman got 2 mega-dollars for their spotted howl research project? This metric system is insane....and it does not mesh with the English language, nor any other language, except French...ah, now we know... If you culture will be gone in 50 years make sure you force it onto people by legislation...
The Inch system is an ancient and universal system going back 4-5 thousand years when there was no such thing as English, French, German, American...get it? If you want to unite the world under one standard, why would you base it in France of all places. You would think that any country with one spec of self respect and honor would not adopt the arc length running through another countries territory. Maybe Indians should define their own meter running through the Himalayas, or from pole to pole instead of pole to equator, making it somewhat longer or short respectively...crazy as crazy gets....Sheeple in the extreme...
03/01/2009 1:00 AM
I don't know where guest is from, but I hope not from the USA - would be embarrassing. The metric prefixes are not French, they are of classical Greek and/or Latin origin, and they were universally understood in western civilization by educated people, who all learned Latin and/or Greek in school, back when the metric system was invented.
BTW, I am from the USA and don't espouse the metric system for everyday non-technical use in the USA, but it's the only way to go for science/engineering, and I am hardly alone in that assessment.
Guest made a few good points in his first post, which I acknowledged in my response to that post, but his obnoxious attitude does him no credit, and harms his cause.
03/02/2009 10:51 AM
Emc,
Latin? Where does French derive from? Who uses Latin? Japanese? No. Chinese? No. USA-- No. Why not make it so that each language can translate it into their own language via the universal language--math. Is that not the point of the 1000's etc? Japanese don't use 1, 2, 3... but math is universal in rules. Each language translates, then there is a true respect for other cultures and languages. The Metric system totally disrespects other cultures. If we keep it in math with a universal location (polar radius) then we include all, not just French "progressives" as they like to call themselves.
The point being is that the metric system was a political and cultural move, not a scientific move viable to ALL countries because of its construction.
Compare: Polar radius to arc radius... Polar wins because it is universal to all nations, makes common sense, has a well know relationship to a sphere and to the center of gravity. The arc is a part of many, not the core.
The time meridian should also not be in England, and should be on some remote small island where every nation of the world could "own" a piece of land along a longitude to call their own and to start the clock.
Since the meter was so inaccurately measured (off by 3%?) they could have just chosen 40 inches. But why not just choose the polar radius? Politics and anti religious notions, that's why. Read the history...
You can swap the meter for the "sacred" cubit (1/10 millionth of the polar radius) and get everything you have in metric system. You could then have all the so called benefits of the Metric system, and still have use of the inch standard. So why would they not do that? Such a move would have saved many trillions of dollars, or tera-dollars...could not resist...
Well did not because they would have to admit that ancient civilizations were MORE advanced than they were!
The theory goes that we "progress" over time, and the arrogant metric system designers were making a political statement of hubris and using our measurement system for their politics. They hijacked our very measurement system to make a statement against the old world!
The real world of reality is that civilizations progress and digress. The metric guys were saying that all their elders were dumb and the children (the metric guys) knew it all, just like the 60's generation has done to our horror...therefore we cannot use an established system in inches (sacred cubits), and nor can we use a Constitution... It is all the same PC arrogance, which makes me vomit.
Can we as CR4'ers just be honest about this and know the history?
By switching to the cubit (call it the "new meter"...like a "new deal" ) we would have instant world convergence of measurements old and new...peace. If their goal was as you say, that is what they would have done. Their goal, however, was not comfort, peace, ease of use, but revolution. Revolution... That was the goal, not science, not ease of use, just rank, arrogant ignorant revolution....politics by another means. The wanted to jerk people around with their inaccurate and arbitrary ways, just like the current politicians are doing. We call such people "tyrants" People love to get into power and make random decrees to show how important they are, and this is what is at the core of the metric system.
I say the we make the "new meter" equal to the old cubit (25 inches exactly) and have peace. Since the meter is now based on frequency, just change the number of waves. Because they were so far off in measuring the meter in their "enlightened" state, why don't we just do the switch? The meter has no foundation to it.
As for my obnoxious attitude, I find the metric system to be obnoxious at the core. It is time for a true "revolution" (rolling back) to occur. Off with the metrics head!!! We the people, needing a more perfect union of measurement systems, do hereby declare... Get the point. It is time to take the garbage out!!!!
Good Answers: 103
03/02/2009 11:40 AM
I am not very sure what is the exact problem you have with metric system- I am sorry to say, but none of the arguments hold much water.
You are saying
Can we as CR4'ers just be honest about this and know the history,
It may be pointed out that the users of FPS systems as we call it were not the oldest one. There were civilisations before. Pl check up Indian Civilisation, if you want in Wiki, and the accuracies of the measurements at that time (approx 5000 -6000 Yrs ago) were much higher.
Living in the past is what has in fact spoiled our civilisation. We progress and that progress is not by sticking to the past.
You have said the rule of the thumb- but are they same ? or the foot measurement, then why do we have shoes ranging from #5 to #9 (for adults) ?
No measurement that is variable is likely to be standard. If you really want to standardise, then let us take a basic quantity
Say speed of light in vacuum as a unit - for length
Mass of one Hydrogen Atom as a base unit of Mass (or say I take 1027 Hydrogen atom's mass as one base unit)
Second is a bit difficult - say 1 day = 10 Hrs, 1 Hrs = 10 Minutes, 1 Minute = 10 Sec - so we can have a new second or some other name
Problem is in deciding months and years 365.25 is the problem- it can not be easily metricated, so let us slow doen the earth ? and also make the moon go faster ?
The end result - I am sorry to say - looks to be frustration - without result.
If there is a definite draw-back (technical) it can be discussed- but since it is developed by somebody other than me/us hence it is bad is not the scientific attitude.
Do you measure the inches by thumbs or scale. Foot by stepping or tape/scale ? Weight ?
If you are going to use a measuring device anyway, how does it really matter what is the size of a unit ?
Good Answers: 15
03/02/2009 12:16 PM
SB,
say what?
Good Answers: 103
03/02/2009 1:07 PM
The total argument is that it is french hence it is no good. Well I have been to Fra and met quite a bit of them but the said "It is difficult" was never encountered, except in language. In fact if you understand the attitudes of the people you normally dont have much problem. But that does not mean you have to bend your rules to meet their demands. It is just try to understand and not to have culture clash.
03/02/2009 4:22 PM
SB,
The argument is NOT "that it is french" as you claim. My argument was the arc vs radius. The French made the metric system French and are proud of it. Where does the word meter ,or metre come from? Japanese? Russian? English? German?...let me guess...French. That is the point. The meter system is NOT international...it is French, and was derived by an arc which was a French mistake. No rational culture would pick an arc for a standard. Get it?
The Inch is NOT English, any more than Giza is American. It is an ancient measurement standard, well before the Arabs were doing algebra, and the only thing that will unify ancient with modern, and American with EU.
The central issue is that the arc length is irrational, unscientific, and just unwise.
By making the cubit=meter=25 inches, you then ABSORB the English system INTO the "new" metric system. The "metric" aspects that people like about the current metric system become and extension of the inch and not a competitor. We can have both without ANY problems. We have peace and a world system.
Why is this so hard to understand?
An American company can sell parts in Europe, and visa versa. We have one standard. Just make the meter=cubit=25 Inches exact. Simple. It can be done quickly...
Good Answers: 15
03/02/2009 6:42 PM
Dear Guest,
some excerpts from the Oxford English dictionary:-
metre1
(US meter)
• noun the fundamental unit of length in the metric system, equal to 100 centimetres (approx. 39.37 inches).
— ORIGIN French, from Greek metron 'measure'.
meter1
• noun a device that measures and records the quantity, degree, or rate of something.
• verb measure with a meter.
— ORIGIN originally in the sense person who measures: from METE.
mete
• verb (mete out) deal out or allot (justice, punishment, etc.).
— ORIGIN Old English, measure;
I suspect from your allegiance to the sacred cubit you may belong to the funny handshake brigade. I wouldn't want you to do any masonry on my house as i think the foundations would be very shaky!
Good Answers: 38
03/02/2009 7:06 PM
So it is "probably" French. Bummer
It has been chosen as a standard, there is not always a logical reason why a standard is chosen, with Videotape VCC was better than VHS, HD-DVD Vs Blu-ray and so on, The most important thing about Napoleon is not that he choose "le metre" but that he made standardisation compulsive in his "Empire" thereby helping trade and technical advancement.
03/02/2009 8:44 PM
The most important thing about Napoleon is that he was defeated. BTW, I liked your tag line better when it was pie on the carpet.
Good Answers: 38
03/02/2009 9:58 PM
What is this hatred against the French? they gave use, haute cuisine, Croissants, wine and the guillotine
Cannot please everybody
Good Answers: 103
03/02/2009 10:32 PM
And FTV
03/03/2009 4:19 AM
Dont be silly Epke, most Americans dont know what they are!
03/04/2009 12:04 AM
I did not say anything about hating the French, nor did I imply it. I do wish people would stop making heroes out of dictators and butchers.
Good Answers: 38
In reply to #60
03/04/2009 2:00 AM
I was making a comment in jest, sorry if i insulted you.
Who is/was a dictator, Butcher or Hero depends wholy on who writes down the history after the fact.
03/03/2009 11:42 AM
sb,
Why is what I say so hard to understand?
Do what I suggest and we would have one system now, not two.
We have 12 hrs in a day. 360 degrees in a circle. You must remember those. Why not 100 degrees in a circle, or 100 hrs in a day? Or was that 1000 degrees in a circle and 1000 hrs in a day. Remember, the cm is not official, so you cannot use 10 for anything. You must use 1000. Why? 10 x10 x10=1000..volume. So now we have volume and linear confusion, so we end up with names...which defeats the very purpose of the system...giga, tera...
Why increments of 1000, and not 100, like on money? You claim it is simple, but it is not. Even with the full force of government for 100 years, or should I say 0.1 thousand years, we still have the inch system. Why? People use what is easiest. If the metric system was easier, then I would use it. I took engineering in both.
Ah, but we allow 100 degrees (is that an angle? I thought there were 360 degrees ...) Centigrade. Why not 1000 C between water freeze and boil? But why are we referencing a particular element, since we cannot reference the human element in the system used by humans only? Why don't we use only Kelvin and drop Centigrade? Last I check, different -minority...hmmm...smell of discrimination...- liquids freeze at different temperatures than water. Load water with salt and it freezes at ...negative what degree? How do we have a negative temperature anyway? Is that a negative energy below 0 deg C? Hmmm.
The reason the meter should be as I suggest is because it could have absorbed both into one. The reason the meter was chosen relative to the arc is because of politics and anti-religious old world order bias, and a profound distain for humans being the center of measurement, even though humans are the only creatures who care or who will use it...
In reality, the inch is NOT a scale of the thumb. It come from cubit/25, which is based on the polar radius. The foot is 12 times an inch (like 12 hrs x 2 in a day. It makes the system divisable by 2,3,4 and 5. You can use the cubit and stay in base 5 and 10, or go to the inch and have 3 and 4, do the math, and then go back to the cubit...get it? The cubit has EVERYTHING that a meter has, and the inch and foot allow 3 and 4 division. The arc based metric system is void of this advantage because it does not deal with the math. Without a calculator, decimal is difficult to perform by hand. There is a lot more than moving a decimal point...I doubt most politicians could do even simple hand calculations...
As for your other cultures of the past...the only contenders were the english and metric systems because they were world powers. This was a French against English thing. Constantine chose "Christmas" for december 25th. Why? Christ was born in the spring, not in the winter. Constantine was smart...wise... In contrast, the metric system was an "in your face" French power play, with heavy "progressive" anti-religious backing, and it is still just that. A smarter play would have been to absorb english into metric, which would require the meter=cubit...yes, wisdom of the wise man is foolishness....
As for minutes, why not just say there are 1000 hours in a day, and a minute is 1/1000th of a day? There are 1440 current minutes in a day, so that is close. A second would be 1/1000 th of a minute... Why not 13 months of 28 days (moon cycle) with one extra day, and two extra every fourth year. Hmmm. Why 7 days in a week? Why not 10?
Which begs the question of why 1,000 and not 100? Why "," vs "." as in 1,000 vs 1.000? Why three significant digits? Maybe slide rulers were only 3 digits accurate... In the EU 1.000.000 can mean 1,000.000? Hmmm. Why this confusion? Follow the money...and power...
03/03/2009 1:34 AM
As you have remained a "Guest", though I would guess that you are a regular, I shall do the same. I have read your comments with great interest. I do however substantially disagree with you.
What I find disturbing is your apparently fervent belief in the correctness of the Sacred Cubit to the exclusion of a system that is embraced by a very large portion of the world population.
Good Answers: 103
03/02/2009 3:21 AM
WIKI
Standard weights and measures have existed in the Indus Valley Civilization since the 5th millennium BCE. The centralized weight and measure system served the commercial interest of Indus merchants as smaller weight measures were used to measure luxury goods while larger weights were employed for buying bulkier items, such as food grains etc.[5] Weights existed in multiples of a standard weight and in categories. Technical standardization enabled gauging devices to be effectively used in angular measurement and measurement for construction. Uniform units of length were used in the planning of towns such as Lothal, Surkotada, Kalibangan, Dolavira, Harappa, and Mohenjo-daro.The weights and measures of the Indus civilization also reached Persia and Central Asia, where they were further modified. Shigeo Iwata describes the excavated weights unearthed from the Indus civilization:
A total of 558 weights were excavated from Mohenjodaro, Harappa, and Chanhu-daro, not including defective weights. They did not find statistically significant differences between weights that were excavated from five different layers, each measuring about 1.5 m in depth. This was evidence that strong control existed for at least a 500-year period. The 13.7-g weight seems to be one of the units used in the Indus valley. The notation was based on the binary and decimal systems. Eighty-three percent of the weights which were excavated from the above three cities were cubic, and 68% were made of chert.
Rulers made from Ivory were in use by the Indus Valley Civilization prior to 1500 BCE. Excavations at Lothal (2400 BCE) have yielded one such ruler calibrated to about 1/16 of an inch—less than 2 millimeters. Ian Whitelaw (2007)—on the subject of a ruler excavated from the Mohenjo-daro site—writes that: 'the Mohenjo-Daro ruler is divided into units corresponding to 1.32 inches (33.5 mm) and these are marked out in decimal subdivisions with amazing accuracy—to within 0.005 of an inch.
<that shows that decimal system exists approx 6000 yrs before the french>
And searchin around you can find the other units too (weight, volume, time etc)
But Like English Language (courtesy colonial empire ) a certain tradition/methodology becomes more common and hence slowly creeps in and becomes unoversal.
It takes place due to
a) Ease of use
b) Majority wins (democracy)
c) Pure force. (dictatorship)
in reverse order.
And as this spreads over, it becomes easier and easier to work in the pre-valent system.
We do talk about the decimal system. But what is it ? Its popularity is due to spread (unfortunately/fortunately) of so-called indo-arabic civilisation.
There were other bases too, if I am not wrong Mayan Empire had base 12 ? Now Computers have base 2.
The main aspect is as far as the base is same it becomes simpler and easier. Let it be 10, 20 or 100 or even 12.
But the problem takes place when you have measurements in base 12 (inch to ft), 660 (furlong to ft) or 8 (furlong to Mile).
This is the aspect that has been taken care of in the metric system and that hs made it popular and not how much is one mm or one Kg or so on.
The problem of time measurement is much more complex and has been unfortunately related to the movement of stars and the planets and those could not be controlled and neither can be forced to follow the decimal system.
The same can be said about universal constants like G, Pi etc.
Here the point is not so much that who is good or who is bad. The point is there is system now already adopted by more that may be 75% of civilisation (if not more).
Now do we keep our heads down and say we don't conform. Or join with the others and continue.
The basic problem of non-conformity will be made clear from customer angle. We do get some items from USA with imperial threads. Anything from anywhere else (including the mother of the imperials - the UK) are metric.
We land up in problem of arranging spanners, Allen Keys, tap sets, Kack screws and so on whenever we import these.
And we are OEM, what is the condition of end user, who gets 3 components with imperial threads and 18 with metric ?
We do specify now a days for metric threads (with due regards to imperialistics ) but once in a while things like lifting holes , forcing screw threads etc are in inches and we have a hell of a problem especially when we can not make a new hole (eg in a bearing or a hardened gear )
The post is longer than intendend and there may be incoherence since even I don't feel like reading back and revising.
Good Answers: 15
03/02/2009 6:16 PM
Well written SB,
That is really the point, that the measurements should be to the same base as the number system in common use.
Should we go to binary, decimal, hexadecimal?
There is a good argument for binary, apart from its use in computers & control systems, in that we have an innate ability to see symmetry and thus to divide by two. Since giving names to numbers in a pure binary would be something of a challenge going to hexadecimal would seem the most logical, only we would need to agree on the names for the extra numbers since the system of using alphabetical characters above nine would be confusing.
The choice of 60 as a base for time is because that has a high nº of factors (2,3,4,5,6,10, 12,15,20,30).
There is no reason NOT to have a metric division of the day / hour / minute. The year, the month and the day are both real, or natural, time measurements in that they are time periods that affect our very being and a failure to plan by these would reduce us to hunter /gatherers, and not very good ones at that.
It seems very strange that America, the first colony to mutiny in the British empire should maintain the imperial (not English) measures longest. Even stranger that it seemed to espouse the metric ideal by discarding the £.s.d ( twenty shillings each of 12 pence, for those who don't remember it) for the more logical 100 cent dollar.
I grew up with both systems and believe me the metric system is ten times better than the imperial.
Chas
Good Answers: 103
03/02/2009 10:35 PM
I remember in my not so child hood - some discussion was going on in metricating the time , I dont think it was exactly 100s something like 25 hrs/day and then 100s.
Sudednly it fizzled out (never know it was rumour or actual) No internet or PC to even know the truth (no TV either ) to do the propoganda.
02/28/2009 10:28 AM
Wow, no chicken power here! Guest, please register so we can tear you down properly. BTW, the metric system is used in many US products. I don't care which system they use, but I wish there was only one. I have a lot of inch tools and cabinets full of inch bolts, and a few metric of each. It's disgusting to try to fit an inch Allen wrench into a metric bolt or strip the corners off a hex bolt because the socket set is a little to big.
03/01/2009 5:43 PM
that was the most needlessly lengthy and confusing reply to a simple question in the history of man/cows.
i understand how the imperial measurement system can be useful to those familiar with the quantities that it's based on. But these familiarities with common Imperial lengths / weights can only extend so far... Many engineering calculations contain quantities that are too large or too small to envisage in terms of everyday lengths or weights - the 'layman' won't know the difference between 204567239 lb and 92790138 kg... though they are identical. Same with 0.0039 in - try measuring that with your thumb! (its about 1mm, 10^-3 times a metre).
Engineers will know what i'm talking about.
though i guess in the end its just what you get used to!
dave
03/02/2009 1:27 AM
You are reading book, but Im making a joke. although I know it has something to do with horse.
this point, you are right, steam engine had been invented many years ahead of Watt, till watt invented adjustor, the manchine had been put into safe, practice use.
You induced a topic of system. we all use MKSA system, I was told only your american still instead on inch system.
its unconvinient for us to convey them. because many software also use inch system, like pcb, etc. as well as electronic devices size. why your usa was so indenpendent.
03/03/2009 3:05 AM
I understand, you conduct poles to decide the units. This I read in one of the editorials of Applied Optics in 1980s. Effectively you are still using FPS system, miles, inches, pounds/gallons etc. Here in India, people never noticed, when the units got changed. Now over last 30 years, even villagers use Kilometers and Kilograms.
I remember one documentory on Nation Geography about Air Crash Investigation: Pilot filled fuel assuming that the units of volume for fuel filling system are changed. So he filled XXXXXX units of fuel. According to his understanding, those were XXXXXX Kgs. But actually XXXXXX pounds of fuel was filled. Effect: Plane was out of fuel while still away from the airport. Please correct me, if I am not correct in putting the story, which I saw long back.
02/27/2009 7:55 AM
Because CP ( or more commonly known as " chicken power" ) just didn't have the right connotation to get the point across.
CARPE CRUSTULORUM!
02/28/2009 3:29 AM
Well I don't know about that.
"Hey my sports car's got 500,000 chickens under the hood, just listen to that baby cluck!"
02/28/2009 12:49 PM
We should ask Del how about the CatPower...
Aged man is not old man...
Good Answers: 38
03/01/2009 7:42 PM
Like CNpower said it is History wise that Horsepower, inches and feet measurements, they were based on what they new then.
i thought in the 90's it was all Girl power?
Good Answers: 103
03/02/2009 3:26 AM
No Girls were never powerful.
It was always Women-power (it was earlier too - it was from the background now it is in the fore-front) pun unintended but true.
For explanation think about the animals- monkeys- humans developement of women-power.
Good Answers: 38
03/02/2009 6:56 PM
I guess you never heard about, the spice girls(en vogue, destiny child, Girls aloud etc.) and the marketing power "they"(the record company) posses
Good Answers: 103
03/03/2009 1:49 AM
And also the power-puff girls (i forgot about them)
They had the power .
But then why the horse power why not mare-power(MP) or better filly-power (FP) ?
Which is more ? Of course logically
MP>HP
But FP is ?
(This is On topic but I take a sadistic satisfaction in marking it Off Topic)
Good Answers: 38
03/03/2009 2:10 AM
I guess Pony-Power (PP) sounds better
"Jacq ow much PeePee isz yur Vioture"
Powerpuff girls was more silly Power(SP) or like Ren & stimpy Absurdity Power (AP), Monthy Python's Flying Circus has a lot of AP.
Good Answers: 804
Re: Why Are Motors Rated in Horsepower?
02/27/2009 3:18 PM
To further the discussion, the issue of choosing Watt's name as the SI was because being a name, it would be the same in any language and always abbreviated as W. "Horse Power" when translated became many different acronyms. That is why you sometimes see older machines with ratings such as CV, which was used for Latin based languages such as French, Italian, Spanish and Portuguese because of the word for Horse starting with C, or PS, which is German for Pferdestärke or "Horse Strength". It got too confusing.
But here in the US, we just have a hard time changing things to accomodate people on other continents.
Good Answers: 15
03/01/2009 12:52 AM
Jr,
Try going to the EU and selling Inch based products. The EU is going to ban such the inch system in the EU. The USA is the most accomodating country in the world...give us your tired, poor...and crazy metric system... I get it...agree with the EU or you are not accomodating... Up is down, backwards is forwards... black is white... smoke and mirrors... got it...
02/27/2009 5:08 PM
Another reason is that the engineer providing circuits for the motor is interested in the max ampacity required of the motor which is given in KVA rather than KW. The motor tables list the motor in HP, Voltage and amperage. KW is an unused quantity.
Good Answers: 15
03/03/2009 1:43 PM
Go to http://en.wikipedia.org/wiki/French_units_of_measurement and all will become obvious. Why should the French use the English measures when they had their own set of measures which were non standardised.
If we have to go to old English measures then lets do so. Banned will all mention of "city blocks", turning on a dime and anyone using of pounds (avoirdupois) above 13 will be severely castigated. (14lbs/stone). This will be in turn limited to 7st 13lbs whence it moves up to hundredweights (cwt).
The Dollar will have to be sacrificed on the altar of antiquity also, especially as this is a metric based quantity.
The liquid measures will have to be regulated so that the pint equals 20 oz and thus the gallon will weigh 10lbs.
Perhaps our Guest would like to go to the wiki article :-
http://en.wikipedia.org/wiki/Avoirdupois#American_customary_system which may dampen his desire for his customary units in light of his obvious xenophobia about the French.
regards
Chas
03/03/2009 3:17 PM
capblanc,
You seem to not have read my comments very well. It is NOT about France, French people, or the like, and I don't dislike them...both my parents spoke french...I learned french as a child to some extent, I now speak German...some Japanese, and my brother speaks Italian, my wife speaks Portugese, and I would love to learn many more languages and live in many different countries.
That said, the metric system is NOT universal, nor well thought out. It was because the French did their old system so randomly that people just said ok, bag that junk, and let's try this new metric system. The reason the "English" system, which was actually an old system that Europe used during the Roman empire, was able to stand up so long to the metric system was because it made sense in a large measure, and likely helped England usher in the industrial revolution, for without a reasonable system, like the INch system, little engineer was possible, or at least it is slowed. The furlong, and such things have been forgotten, as they should.
The central point is if you want a world system, then you should start with a standard that the world can agree on, and not something that favors one culture over another. What I propose would be ok with Chinese, Indians, Polish, and all nations as it was not something that is derived by one dominate (at the time) culture. By making the "meter" = cubit, then you can add in what works in the old Inch system and what works in the new decimal based "metric" system and then they are the exact same! But by making it based on the arc, the French forced a contention where none should have existed.
Do you want to combine the systems or not? I would suggest you stop mocking and first understand what I am saying...
Good Answers: 15
03/03/2009 5:57 PM
Dear Guest,
I can read your posts but I cannot understand your hatred of the metric system. No system can be perfect. Ideally all the measures would tie together seamlessly with nice easy relationships between each entity but that is impossible due to the nature of the universe and the constants therein.
The metric system is a lot easier to use, and more importantly, has been adopted by more of the world as the standard than the customary units used in the US (and to a lesser extent, the UK). With a world population of 6.764 x109 versus 306 x 106 in the USA it is fairly obvious who is dancing out of step. You may say that not all of the world has adopted the metric system but by the same argument I would counter that the American academia has fully embraced the metric system and a sizeable proportion of the engineering community also.
The metric system is a live system, being modified by international accord as the technical needs dictate. The USA is a full member of the ISO organization and has a hand in setting the standards.
Jump down off your soapbox, dust away the cobwebs and get on with the realities of the this world. If you want to keep some quaint measures for keepsakes, the pint, an acre or whatever, then do so, but please don't try to convince anyone that imperial measures are a system of any kind.
Regards
Chas
Good Answers: 103
03/03/2009 11:42 PM
There is one point that you should understand, The SI system whether good or bad is now universal (well except a couple of pockets) and now including the standards of these (including US) have the metrics (or at least equivalents)
Do you understand what is the effect of changing the base units now? World over all the engineering softwares will become useless in one go. (and if you gradually bring- you land up in 3 systems working parallelly FPS, Cubit and SI- do you get the confusions that will be created ?)
A basic question was raised here too- why should one learn English ? it is a foreign language. Why not change all text books etc in the local language and get away with it. But some sane person(s) went above the local politics and understood not only the task involved but also the effect - the translation vs original. And it happens in the basic units too.
We still land up in components (that we manufacture) with dimensions say 381.127 + 0.127 (this could easily have been 381.13 + 0.13 or 381.15 +0.10 or things like that but due to blind translation without getting into the concept is what has happened here. And when the scale becomes large, people do not have time to think and understand and everything is now with calculator, these becomes norm (in fact this specific dimension was there with us for approx 15 years till a couple of years back till we paused during our design reviews and asked why)
As I said earlier, the thing is now too late to dig-up (as we could do with Indian system of measurement -BTW did you know that the system was nearly binary long long back ie in terms of 2n ? - or Sanskrit as language (most structured and computer friendly ?- and put English in the waste bin ? ) The best way is to learn live with the imperfect system and try to make it perfect.
Again names do not matter. Does it really whether I call it metre or cubit ? why should an engineer bother ?
In reply to #59
03/04/2009 12:35 AM
SB,
Because with the cubit (25 inch meter) you can have the best of both worlds, that's why. Of course there are many other things that need changing...
We need a system that is math based, not language based, so that all cultures and languages around the world are respected, and not just French, Latin or English. We need a system that the average poor person can understand in a math logical basis so the it can be translated into the home language via common translations. Horse power HP is Pferdestaerke (PS) in German, and every German can relate to that better than a kilowatt.
The reason people still use HP is because the KW has no connection to anything. Ask anybody what a Watt is. Try it. I asked my twice over Phd/doctor father-in-law who used ml in 40 years of practice and he had no comment. When a person looks at their electric bill, they have no idea how much energy they use and therefore waste it.
A Human power would be about 1/12th that of a hp or 1/16th that of a kw. When you tell them that, then they realize just how much energy it takes to sustain their lifestyle. A gram is way to small, and centigrade is much to course.
Think about it: The amount of warming claimed from ALL the last century from "global warming" due to co2 is 0.5-0.7 C. It does not even register on the nightly news! "Today the temperature is 15 C in New York, but if we had less co2 it would be 14C." If the Temperature is really 15.4, you still have to round up to 15! 1 C is too large for even room temperature comfort range on many indoor systems! And I don't have any sense of what the number means. When I say 100 F I know that is the limit of hot. Where is that in C? 37.7C? 35? What is 35 mean? Nothing... Numbers don't mean things to many, if not most, people. Relationships is how the mind works, and the metric system is void, like some chem lab, of relationships. Life is about relationships...
I am do working with hydraulics. BAR is a useful measure. Why? Metric outlaws that...or at least all the mocking by the "cow" folk would imply that scaling to something useful is just old fashion nonsense. Why do all Hydraulic manufacturer do it? Think about it...
Enough said... You want to let a bunch of EU dictators run your life...you go ahead...not me...
Good Answers: 38
03/04/2009 2:11 AM
Well Guest,
start Lobbying for it then, if the cubit is the best system then it will be implemented
in the world in no time. Instead of arguing about it you should go out and make it
happen!.
Good Answers: 58
03/19/2009 4:34 AM
Not meant as a specific answer to this post, but I thought this was a rather interesting introduction to a paper written in the 19th Century.
WEIGHTS MEASURES AND MONEY OF ALL NATIONS. COMPILED BY F. W. CLARKE, S.B., PROFESSOR OF PHYSICS AND CHEMISTRY IN THE UNIVERSITY OF CINCINNATI.
ENTERED, according to Act of Congress, in the year 1875
IN the following pages the compiler has sought to arrange, in a manner convenient for reference, the weights, measures, and money, of all nations. The work is naturally divided into two parts : first, a classification according to countries, arranged alphabetically; and, second, a set of tables in which the value of each unit is given both in English and in metric standards. This use of the metric system, coextensively with the ordinary system, may be regarded as the characteristic feature of the book. Of course, its introduction on so broad a scale doubled the labor of constructing many of the tables in the work, but the writer believes the labor to have been profitably spent.
The metric weights and measures are now legal in this country, and are used by at least twenty nations besides ; surely, then, they deserve as much attention as our own more locally familiar but more bungling systems. Our three sets of weights, our three different gallons, and our two dissimilar bushels, all unrelated to each other, or to the units of length, must soon give way before the simplicity and elegance of the metric system. That this event may soon happen, and that the weights and measures of the world may before long be reduced to metric uniformity, is the sincere wish and hope of the writer.
F. W. C.
In reply to #65
03/20/2009 2:04 PM
Prof,
Do you have a link to the Clarke reference you cite?
Why would a rational person want a standard based on an arc length? Are you a professional and rational person? I assume you are, and invite you to first peacefully understand my points, and not to rush into wanting something that a rational person would not consider, namely an arc length as a standard.
The relationship between a meter and inch is 25 * PI/2 * EF (error factor). When the arc length going through France was measured, they were off an amount. The meter is therefore, not only inaccurate from its birth via a ground measurement, but is disconnected to all of history. The meter was adjusted to be equal to exactly 2.54 cm later on.
Set 1 inch = 2.54 cm (cm is now not legal, by the way) = .0254 m. One cubit =25 inches. 0.0254 *25=.635 meters
1 Cubit =.635 meter, exactly.
Multiply: 0.635 * 3.1415926… / 2 and you get .997455. The original meter was changed by 1.000000-.997455= 0.002544 to link both systems by the common factor of 2.54 cm.
Why bother with such nonsense? Why have a standard (meter) based on an arc?
Look, draw a circle, and divide it into four parts for four arcs. A full circle circumference is 2 * PI * radius. One fourth is the R* PI/2. The relationship between the meter and cubit is PI/2, or the relationship between the radius and the length of the quarter arc length. No scientist would base a foundational length on an arc length. Only a linear length would be allowed, and therefore the meter (quarter arc of the planet /10 million) should not be allowed...
It is NOT a matter of debate that an arc length standard is NOT rational. We hold these truths to be "self-evident" and fundamental to reason. The meter is not based in reason…
If you took the time to read my previous posts, you would see that by making the meter exactly =25.0000000….. inches, we could have had a common standard long ago, and that standard would have been 25 times an Inch, or a cubit. We did not realize this however, until after WWII. Newton himself looked into this matter...
All of your claimed advantages found in the decimal based meter can be found in a decimal based cubit that is renamed "meter," or measurement. The meter is political, and therefore not valid... Sorry...
Register to Reply 66 comments
Anonymous Poster (14); aurizon (1); babybear (1); capblanc (6); cnpower (2); Codemaster (1); elect-ok (1); elnav (1); emc_c (3); Epke (8); gsuhas (2); Hendrik (1); jack of all trades (1); Janissaries (2); JRaef (1); nascon (1); not so smart (1); Qqberci (1); sb (10); seaplaneguy (2); StandardsGuy (3); The Prof (1); wareagle (1); zmun (1)
Previous in Forum: Using a Step Down Transformer as a Step Up Transformer   Next in Forum: Transmission Line Voltage Level and MVA Capacity