mccb

03/16/2009 5:07 AM

hi all

i am using a 100 A mccb but requirment of 32A Mcb can any one tell me what will be it drawback

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: mccb

03/16/2009 5:33 AM

When your load current reaches 33A, whatever the 32A MCB was supposed to protect will begin to overheat, eventually catching on fire probably long before the 100A MCCB will trip.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Commentator

Join Date: Mar 2009
Location: delhi india
Posts: 79
Good Answers: 2
#2
In reply to #1

Re: mccb

03/16/2009 5:42 AM

cant understand

i want to know can i use 100A mccb instead of 32A although i know load current is not more than 25A

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3
In reply to #2

Re: mccb

03/16/2009 5:46 AM

You can use 100 A MCCB but this will not protect your devices for over load beyond 25 A.This MCCB will have normal thermal settings 0f 80-100%.Therefore for any current beyond 80 amps only this MCCB will trip and isolate the circuit.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Commentator

Join Date: Mar 2009
Location: delhi india
Posts: 79
Good Answers: 2
#4
In reply to #3

Re: mccb

03/16/2009 6:29 AM

what will happen at time of short circuit . as i know current will be very large at time of short ckt

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: mccb

03/16/2009 6:37 AM

Either the 25A device, or the cable feeding it (whichever has the lower rating), will go BANG!

Last out the building is a cissy...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #4

Re: mccb

03/16/2009 9:19 AM

You will then have the opportunity to design and install a proper circuit, assuming the building is still there.

Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#7

Re: mccb

03/16/2009 6:34 PM

Actually, a short circuit might well trip the 100A MCCB, but there will be no protection from overloading and burning up the 25A load. CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM