E-Stop Circuits and Risk Assessment

03/17/2009 9:50 AM

We are working on a hazards project and using lot of automation drives through "PLC" operations. We provided e-stops through the automation for risk assessment process. However we have to determine "Category of E-stops Circuits" in terms of Risk Assessment. I was told that "NFPA" has guidelines for such assessment. Would you let me know, which section of NFPA and/or any other reference that may help me find these "E-STOP" category.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: E-stop Circuits in terms of Risk Assessment?

03/17/2009 10:04 AM

On safety grounds, it is not permissible to rely on software for personnel protection where either electrical or mechanical hazards exist.

  • For example, a technician is delegated to change a pump motor. On breaking the coupling, what is there to prevent the motor turning while spanners are in the mechanism? On opening the motor terminal cover, what is there to prevent the terminals becoming live while being unscrewed?

So there has to be a way of locking-off the power sources to enable this to happen, and a way of controlling it under Permit To Work arrangements to assure a high degree of safety (which is a low level of risk). Lock-off isolators adjacent to the rotating device are best practice: both the permit signatority and the technician can apply padlocks should local procedures require it. Then, even if the PLC says "run", the motor will remain stopped.

E-stops must break the auxiliary supply to the starting contactor when pressed. Local standards will determine whether or not these buttons are to have key-turning releases.

Does that help?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: E-Stop Circuits and Risk Assessment

03/17/2009 3:30 PM

Yes, I just finished a system design for category 1 and category 3 emergency stop and safety relay systems, and the information available is a little vague and varies from application to application.

One of the main standards is EN 60204-1 (European). As I didn't have access to the standard at the time most of my design data came from safety relay company literature and data sheets (which show example solutions and different ways for achieving the different category levels of safety). I am not sure if the NFPA guidelines are a copy of the EN 60204 guidelines.

Try the websites of Duelco, Pilz, Omron and Sick (possibly) for literature and data sheets which give design examples.

Alternatively try a web search, the answer regarding NFPA categories is there somewhere.

__________________
jack of all trades
Reply
Active Contributor

Join Date: Mar 2009
Posts: 10
#5
In reply to #2

Re: E-Stop Circuits and Risk Assessment

03/18/2009 8:05 AM

FYI, yes, that is NFPA 79. Thank you.

Reply
Power-User

Join Date: May 2008
Location: Europe
Posts: 285
Good Answers: 9
#3

Re: E-Stop Circuits and Risk Assessment

03/18/2009 7:30 AM

Dear Guest,

Check out the link beow. Not sure if it is what you are looking for but it might provide some additional information.

http://www.schneider-electric.co.uk/internet/pws/literature.nsf/luAllByID/JRIS-6RWJS4/$file/How_to_use_BSEN60204-1_2006_Safety_of_Machinery_SE5941_full.pdf/

Regards

Mr. W.A Snow

Reply
Associate

Join Date: Jan 2007
Location: Raleigh, N.C.
Posts: 49
Good Answers: 1
#4

Re: E-Stop Circuits and Risk Assessment

03/18/2009 7:54 AM

NFPA 79, "Electrica Standard for Industrial Machinery". If this section doesn't have what you need, it has references to other areas of the NFPA that should. As a note, PLC, DCS type systems are not allowed to function as an emergency stop, unless it is rated as such. These are dedicated systems, manufactured to function in this capacity. This is covered in the NFPA. Just remember, the NEC is the minimum required. Be safe!

__________________
"You can fool some of the people all of the time and you can even fool all the people some of the time, but you can never fool all the people all of the time." Abe Lincoln
Reply
Active Contributor

Join Date: Mar 2009
Posts: 10
#6
In reply to #4

Re: E-Stop Circuits and Risk Assessment

03/18/2009 8:12 AM

Thank you. I do not have NFPA 79. Is it possible to have me that part copied & send me! Thanks again.

Reply
Associate

Join Date: Jan 2007
Location: Raleigh, N.C.
Posts: 49
Good Answers: 1
#7
In reply to #6

Re: E-Stop Circuits and Risk Assessment

03/18/2009 8:22 AM

Sorry, can't do that, but it is available thru the NFPA, non-member price: $39.50.

http://www.nfpa.org/catalog

__________________
"You can fool some of the people all of the time and you can even fool all the people some of the time, but you can never fool all the people all of the time." Abe Lincoln
Reply
Anonymous Poster
#9
In reply to #7

Re: E-Stop Circuits and Risk Assessment

03/18/2009 1:38 PM

Love your quote, unfortunately today you only need to fool some of the people enough of the time to get rich or elected!

Reply Off Topic (Score 5)
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#8

Re: E-Stop Circuits and Risk Assessment

03/18/2009 9:54 AM

Guest,

I concur with all the previous posts. There are PLCs that are rated and approved for such applications, but I have never worked with them.

One addition--in designing your automatic controls it is very wise to have the PLC system monitor the status of the e-stop circuit(s). This can be by inputs from auxiliary NO or NC contacts at the individual e-stop locations or by auxiliary contacts on the e-stop relays or master control relay. The rule being followed here is that you always want the PLC logic to know and be able to respond to all conditions in the equipment it operates. That way it can provide supervisory notification (such as a graphical operator interface showing what e-stops have been activated so operators/workers can respond appropriately). Another approach I frequently use is to have all e-stops be with an illuminated operator that is on a PLC output; programmed so the activated one is blinking and all others are illuminated steadily (this alerts workers everywhere that the system has an e-stop activated and pinpoints the exact one for appropriate worker response).

--JMM