Lagging in steam traps

03/21/2009 4:46 AM

What do we mean by term 'LAGGING' in steam trap functioning in steam system ? I read somewhere that lagging is not recommended for thermostatic traps as they are prone to water logging. But didn't get the meaning of this term.

__________________
annu
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#1

Re: Lagging in steam traps

03/21/2009 8:19 AM

In India/Pakistan/UAE/Saudia Arabia & other hot areas/countries you do not need to lag steam traps. These are required only in very cold areas/countries say like Canada/USA/Russia etc where there is extreme far below 0C temperatures that steam traps may freeze and fail to operate , thermostatic or any other types.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
2
Power-User
Engineering Fields - Piping Design Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Aug 2008
Location: Europe
Posts: 287
Good Answers: 27
#2

Re: Lagging in steam traps

03/21/2009 10:00 AM

Yes, yes, I know: This has nothing to do with bolts. However, steam was my first love...

"Lagging", as you've probably surmised from the less-than-direct answer above, is merely insulation.

You are correct about the issue of lagged thermostatic steam traps (those that discharge condensate as a function of temperature rather than density difference). The more that these traps are insulated, the greater the amount of upstream "trapped" condensate. This might be acceptable for applications such as tracing lines but certainly not for drip legs or for most temperature-controlled processes. In those instances, the immediate interface between steam and condensate that a float or bucket trap provides is much more suitable. "Thermodynamic", or colloquialy known as "disc" traps, operate at the other end of the spectrum. These are fine for drips and for tracers where a higher temperature is required. They're not suitable for throttling loads or those where non-condensible gases are present.

__________________
Best regards, HeviiGuy
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#3
In reply to #2

Re: Lagging in steam traps

03/21/2009 12:50 PM

You do have a good knowledge. Put a Steam Trap photo on your avtar.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Aug 2008
Location: Europe
Posts: 287
Good Answers: 27
#4
In reply to #3

Re: Lagging in steam traps

03/21/2009 8:12 PM

The one and the only "Spirax Man". Ask C. Ball, if he's still around ;-)

__________________
Best regards, HeviiGuy
Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#5
In reply to #4

Re: Lagging in steam traps

03/21/2009 10:10 PM

Correction one more. not only. 8 years Spirax Man

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Guru

Join Date: Sep 2006
Location: Western Pennsylvania, USA
Posts: 761
Good Answers: 9
#6

Re: Lagging in steam traps

03/22/2009 8:35 AM

Insulation covered with, usually a metal shield, causes condensation and creates the problem you are concerned about.

I have worked on many systems and Steam Traps and Pigtails are bare, all ancillary piping and vessels can be lagged or insulated.

Think wearing extremely heavy clothes in a sauna.

Register to Reply
Associate

Join Date: Mar 2008
Location: Southern California
Posts: 46
Good Answers: 2
#7

Re: Lagging in steam traps

03/22/2009 9:25 AM

All steam traps require heat to be radiated to ensure proper function or they could steam (vapor) lock and the trap will not be able to flow the stated capacity.

The only time a steam trap should be lagged/insulated is in instances where they pose a safety/burn hazard.

If the trap needs to be insulated, then the distance between the trap inlet and the main line or process should be extended to accommodate condensate backing up.

Regardless of where you are located in the world, unless your ambient air temperatures exceed 212 deg F, optimal insulation thickness for pipe should be used to reduce:

1. Fuel source consumption (natural gas, heating oil, etc)

2. Reduce CO2 emissions

3. Reduce water used

The above savings are achieved through reduced radiant heat loss to ambient temperatures.

If you are looking to insulate your steam system, I would focus on:

1. Storage tanks

2. Heat Exchangers

3. DA Tanks

4. Boilers

5. Steam distribution pipe

6. Condensate return pipe

7. Condensate return pumps

8. Moisture separators

9. Control valves

10. Regulators

A great resource to determine optimum insulation/lagging is:

http://www.pipeinsulation.org/

If you are fortunate enough to be located in California, the local gas utility companies are offering $3.00 per linear ft rebate to insulate steam & condensate pipes.

Best regards to all!

Register to Reply
Associate

Join Date: Oct 2007
Posts: 25
Good Answers: 1
#12
In reply to #7

Re: Lagging in steam traps

02/17/2010 10:03 AM

It is not true that all steam traps need to radiate heat. Venturi steam traps, having a fixed opening, will not "vapor lock" (actually the result of a vacuum being formed when the steam valve is closed, the mechanical trap is closed, and the trapped steam condenses thereby taking up a tiny percentage of the volume that the steam had.) This is why Air Handlers, using mechanical traps, add a vacuum breaker.

Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#8

Re: Lagging in steam traps

03/22/2009 12:52 PM

Insu-Pak™

Now you can insulate the in-line traps in your plant without complicating regular trap maintenance. Insu-Pak, a simple reusable insulation package, cuts the time and cost of in-field installation because it goes on in a snap. And it comes off just as easily. The Insu-Pak can prevent trap freeze-up when used with a properly designed condensate manifold. Designed for use with Model 2010 and Model 2011 traps.

Courtesy Armstrong international

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply Score 1 for Off Topic
Associate

Join Date: Mar 2008
Location: Southern California
Posts: 46
Good Answers: 2
#9

Re: Lagging in steam traps

03/22/2009 1:32 PM

In areas where a steam trap could freeze, the following things need to be done:

1. Do not use bucket traps, as it is impossible to get all of the water out of the units due to them requiring a water seal to ensure the trap will close at the presence of steam (all bucket traps required this -it's usually referred to as the "prime").

2. Freeze protect the traps that do not require a prime by adding a liquid expansion trap to the drain port of the trap. The liquid expansion trap fill is designed to make the trap open and drain out the water in the trap when the condensate temperature drops to at least 35 deg F (above the freezing point).

No insulation will prevent a steam trap from freezing if the steam is no longer flowing to the trap. Your only recourse is to be VERY careful on the trap type used, and install the trap so that all of the water in the trap drains out under near freezing conditions to prevent the condensate in the trap from freezing & cracking the trap wide open.

The following is an excellent link on freeze protection hook-up:

http://www.spiraxsarco.com/resources/cad/applications/steam-trapping/preview/steam-mains-drainage.asp?drawing_id=72

Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#10
In reply to #9

Re: Lagging in steam traps

03/23/2009 12:10 AM

Excellent. You deserve a vote.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Power-User

Join Date: Feb 2009
Location: India
Posts: 155
#11

Re: Lagging in steam traps

03/23/2009 2:22 AM

Your question is what is Lagging? It means thermal insulation.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13

Re: Lagging in steam traps

04/21/2023 7:26 AM

<...LAGGING...> is also there to provide thermal protection to persons. If protection can be achieved in other ways, such as by segregation of the hot surface from persons, then <...LAGGING...> might not be necessary.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

b v rao (1); BoltIntegrity (2); ducon (5); Dweezle (2); joltnjny (1); PWSlack (1); qaqcpipeman (1)

Previous in Forum: Query   Next in Forum: How To Obtain Actual Weight of Stairway

Advertisement