Position Transmitter

04/16/2009 1:49 PM

Dear Frnds

1) Is it possible to get the Control valve feedback without using position transmitter /Limit switch. I have the option of Postioner Smart ( DVC 6010)

2) If possible-- is dis scheme Reliable & does it give accurate info

dis is a very critical apllication, unfortunately i didnt consider feedback during detail, but now client wans f/b

Regards

Jose John

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator
India - Member - ADIL MOULA Engineering Fields - Instrumentation Engineering - Adil Moula

Join Date: Jun 2008
Location: India
Posts: 95
Good Answers: 1
#1

Re: Position Transmitter

04/16/2009 2:27 PM

hi john

what we are having is a limit switches for open amd close indication

and there no feedback confirmation signal in dvc 6010 as it is only receiving signal

4 to 20 ma only .

Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#2

Re: Position Transmitter

04/17/2009 2:11 AM

Hi there,

Without an actual transmitter giving you the position feedback - it is impossible to get the real valve position.

The smart positioner will tell you where it thinks the valve is, but this might not actually correspond with what is happening in the field.

Regards,

Craig

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Position Transmitter

04/17/2009 3:06 AM

It is unusual to require valve position feedback in 3-term control loop applications. Usually the measured variable is some process parameter, not the valve position. If only the valve position is available, then some correlation between the valve position and the process parameter is required, which often isn't available.

The valve position will strongly correlate with the 3-term controller's output signal. Could that be used instead?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#4

Re: Position Transmitter

04/17/2009 3:15 AM

Hi

I do not agree with earlier comments. There are a few smart positioner which give correct feedback.

DVC is a good example. I have installed all positioner as these in couple of plants only few feedbacks have been taken though and they show correct value.

Valtek positioner with magnetic feedback also gives good feedback and i use this very effectively in turbine applications to control the nozzle. I have added some logic in the processor if there is a difference btw Input to positioner and feedback more than a certain value.

Naveen

Reply
Anonymous Poster
#11
In reply to #4

Re: Position Transmitter

06/21/2009 3:11 AM

how to do the calibration

Reply
Anonymous Poster
#13
In reply to #11

Re: Position Transmitter

07/09/2009 5:23 AM

Hi,

If you are using DVC6000 Series or DVC2000 the calibration is very simple and straight forward.

TSE

Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#5

Re: Position Transmitter

04/17/2009 3:49 AM

Hi Naveen,

I do not agree with you there.

The position feedback arm is for the positioner itself to function.

If you want to be 100% certain of the actual valve position you will need a position transmitter. The positioner calibration might be out - and then that feedback arm is useless. The same would apply to valve stroke etc.

Regards,

Craig

Reply
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#6

Re: Position Transmitter

04/17/2009 5:15 AM

Hi Craig

Understand what you are pointing out at.. One of the positioner i use for feedback aswell. This uses a magnetic feedback system.

http://www.westlockuk.com/assets/downloads/Westlock_IOM_TECHUK-20_ATEX_ICoT_5000.pdf

Yes this guides the positioner absolutely True. The position is fed into the Microprocessor of the Positioner. when we do the setting we set the full travel then the 100% 95-100% 0 % 5-0%. and these positions are fed to the positioner. So except these value are changed or wrongly fed no problems with respect to the feedback as such, In event that the positioner is failed or the microprocessor memory gets failed yes, then you will not know where the valve is.

But then wont that happen if the fuse in the input line or the wire disconnection happen.

Naveen

Reply
Commentator
India - Member - ADIL MOULA Engineering Fields - Instrumentation Engineering - Adil Moula

Join Date: Jun 2008
Location: India
Posts: 95
Good Answers: 1
#7

Re: Position Transmitter

04/17/2009 6:15 AM

hi john

try with LVDT www.transtekinc.com generally they are used in hydraulic actuators

I have seen some controlvalve in waste heat recovery system having LVDT as feedback positon

regards

Adil

Reply
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#8

Re: Position Transmitter

04/17/2009 6:27 AM

Hi

LVDT will help., yes but only in case of linear displacement. also saperate controller will be required in most cases

Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#9

Re: Position Transmitter

04/18/2009 9:52 AM

Yamatake has a line of smart positioners that provide a 4 to 20mA position feedback to the PLC or other. The positioner, therefore, has two cables going in and out of it. One is the position command signal and the other is the position feedback.

Specific model is the AVP-301.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Reply
Participant

Join Date: May 2009
Location: Abu Dhabi
Posts: 2
#10

Re: Position Transmitter

05/13/2009 9:25 AM

Hi John,

Actually DVC6010 (Sliding Stem Application) providing the features of information, such as: supply pressure, output pressure and travel target. Through the hart communication, we can take this information by using Tri-Loop (HART to Analog Signal Converter) from Rosemount.

So you will get analog output information about the travel/feedback of your valve. Beside that of simplicity in the wiring. Tri-loop is very usefull for application using mulivariable transmitter. All the information for this Transmitter (D/P, temperature and gauge pressure) can be convert from digital HART signal into three additional analog signals.

Hope this usefull for you,

Regards

Golf Alfa

Reply
Anonymous Poster
#12

Re: Position Transmitter

07/09/2009 5:20 AM

Hi,

1. Yes, it is possible for fieldbus positioner like DVC6000f series. For HART Protocol you can consider DVC2000 with options (built-in position transmitter and two Limit switches).

2. Yes, it is also reliable and accurate.

TSE

Reply