Selecting Cables and Breakers

04/16/2009 6:17 PM

in one circuit there are 12 light poles each has single luminaire of 600 watts. can u plz tell me how to select the cable for that circuit and what should be the size of the breaker.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: selection of cable, breaker and voltage drop calculation

04/16/2009 8:35 PM

What is your voltage?

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: selection of cable, breaker and voltage drop calculation

04/16/2009 10:10 PM

Is this a homework question (it sounds like a simple civil illumination engineering one), or do you really not know 'ohms law' and basic electrical cable sizing calculations?

If it is the latter AND the lights are running off either single-phase 120V, 230V or 240V AC (which I also suspect) I would suggest that you get a professional electrician to do the job least your inexperience results in loss of life and/or personal property due to electrocution and/or fire. Single-phase mains wiring and design is not something an untrained person should be doing (and voids insurance in most cases).

Can you please provide more information on what you are doing and why (by your writing style I am assuming you are a student and this is homework)?

__________________
jack of all trades
Reply
Anonymous Poster
#7
In reply to #2

Re: selection of cable, breaker and voltage drop calculation

06/28/2009 7:39 AM

I knew Ohm's Law .I'd like to know relationship of Breaker and Amp List.Please give me

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8
In reply to #7

Re: selection of cable, breaker and voltage drop calculation

06/28/2009 3:24 PM

Please see previous posts and threads on CR4 regarding this commonly-asked (and answered) question.

__________________
jack of all trades
Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#3

Re: selection of cable, breaker and voltage drop calculation

04/16/2009 10:14 PM

OK..This looks like a home work question...so a little hint.

Look at the Wiring Regulations and Standards for your country.

These will dictate what is acceptable and legal in your local area.

You will need to know:-

  • Supply Voltage
  • Cable Length
  • What type of Luminaire (This will effect the actual current)
  • Is the cable arial or burried?
  • In conduit or armoured?
  • What is allowed voltage drop?

Hope this points you in the right direction.

Thanks & Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: selection of cable, breaker and voltage drop calculation

04/17/2009 2:59 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#5
In reply to #4

Re: selection of cable, breaker and voltage drop calculation

05/19/2009 4:26 AM

u can use 1.5mm2 cable and MCB is 6A

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6
In reply to #5

Re: selection of cable, breaker and voltage drop calculation

05/19/2009 3:13 PM

The original question was 12 * 600W lights, and it still cannot be answered without knowing (or guessing) the voltage anyway, which obviously effects the current and therefore the size of cable. The same goes for the length of cable (with regard to the permissible voltage drop).

All of which are clearly indicated in the local wiring regulations (which the original poster should be working to if this is a real electrical job or project and not some homework question).

__________________
jack of all trades
Reply
Reply to Forum Thread 8 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); jack of all trades (3); PWSlack (1); Sapper (1); wareagle (1)