Capacitors for Single Phase Motors

05/23/2009 3:20 AM

my company bought three one horse power motors which am supposed use for our dough mixing machine.

my qn.

1.the motors have the four leads out from the terminal block,when i measure resistant to determine the starting winding am geting like 6.3ohms in both.how do i know the starting winding?

2.how do i know the vaue of the capacitor, since it is shown in the name plate ?

info. one of the motor has 6.3 ohms and 4.6 ohms

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Capacitors for Single Phase Motors

05/23/2009 6:11 PM

If the information is not marked on the nameplate on the side of the motor or inside the terminal cover, and the labels on the capacitors are not legible (or are missing) then rather than us taking a guess you would be better off looking on the internet at the motor manufacturer's website for exact wiring details and capacitor sizes for your specific motors.

Also have a look at previous CR4 threads and posts on the subject.

__________________
jack of all trades
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#2

Re: Capacitors for Single Phase Motors

05/24/2009 2:20 AM

If they are capacitor start motors, there should already be a capacitor mounted on each. Are you sure these are not three phase motors?

If that information is not given on the name plates, then send the motors back and buy some from a reputable dealer!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Feb 2007
Location: Next to the Prime Merridian (51°29'34.50"N 0°13'32.85"W)
Posts: 780
Good Answers: 1
#4
In reply to #2

Re: Capacitors for Single Phase Motors

05/24/2009 5:28 AM

'Are you sure these are not three phase motors?'

Lol!!! this is a damn good question coz what if they are?

__________________
Making mistake is part of learning.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#5
In reply to #4

Re: Capacitors for Single Phase Motors

05/24/2009 9:07 AM

As they only have two field windings, how can they be 3 phase?????

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Feb 2007
Location: Next to the Prime Merridian (51°29'34.50"N 0°13'32.85"W)
Posts: 780
Good Answers: 1
#7
In reply to #5

Re: Capacitors for Single Phase Motors

05/24/2009 12:41 PM

By failing to install the third phase (called; manufacturing defect).

C'mon Andy! Lets just have some fun today. In my part of the world it's still sunday all day and will remain until midnight. So, no need for you to come along nd spoil it. You can get more serious from tomorrow, yeh?

Meanwhile let the OP have some fun by himself, he has more dough on his hands to play with than the rest of us combined u comprendo?

__________________
Making mistake is part of learning.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #7

Re: Capacitors for Single Phase Motors

05/24/2009 12:59 PM

OKay

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#9
In reply to #5

Re: Capacitors for Single Phase Motors

05/24/2009 1:02 PM

Since he did mention only two resistances, you're probably right, but 4 wires could be three phases and neutral for a wye connected motor.

It's hardly clear, since first he says 6.3Ω, than says one motor has 6.3 and 4.8Ω... He did not specifically say there was no connection between the two pairs.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10
In reply to #9

Re: Capacitors for Single Phase Motors

05/24/2009 1:27 PM

I would assume (dangerous?) that he did not get a connection between one pair and the other pair......then it has to be single phase.

There is no neutral connection in a Wye connected motor, check this web site, you will notice that Neutral is never mentioned in conjunction with any 3 phase motor...

Believe me, neutral is never needed when 3 phases are used.....unless single phase equipment must be connected.....

I hope this helps your understanding further....

By the way, for reasons of maintenance, especially on larger 3 phase motors, a fourth connection (the connection of the "other ends" of the field coils) is sometimes brought out to allow resistance checks of each field coil individually.

It could be that both ends of all 3 field coils are brought out and connected to each other, allowing each field to be disconnected for checking of insulation values for example......

This connection is a "neutral point", but must NEVER be connected to neutral.....that is something else!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#11
In reply to #10

Re: Capacitors for Single Phase Motors

05/24/2009 3:26 PM

AH! You're right, as usual!

I have only worked on one wye-connected motor (actually a wye-start, delta-run motor, 10 or 15hp, on a Romanian horizontal boring mill of 30 years ago), and did not remember that there was no connection to neutral. I took a look at the diagram, and saw that I had placed a note on it that the only neutral connection on the entire machine is through the bolts to the floor (which hardly counts).

I was asked to look at this motor because the wye start does not work - it hums but does not spin until it switches to delta, which of course then has a large surge of start-up current. I checked the wye contactor, and all three pairs of contacts measure at the lead resistance of my DVM when closed. Any suggestions?

Ok, now what would happen if that "neutral point" were connected to supply neutral?

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#12
In reply to #11

Re: Capacitors for Single Phase Motors

05/24/2009 5:16 PM

As this is normally never done, nor is there a need either, I will have to guess a little (a lot!), I would think that if the motor is built reasonably accurately, no current will flow.....in practise, I am pretty sure that some heavy currents may flow back through the neutral wire.....

I am not confident though.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#13
In reply to #12

Re: Capacitors for Single Phase Motors

05/24/2009 8:50 PM

The next time I go to San Diego (in about a week, I think), I'll try to measure the voltage between that 'common, or neutral', and the chassis, which is the closest to power neutral that exists on that machine. I may have to do it with a 'scope, since it is only in the wye condition a few seconds.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#15
In reply to #13

Re: Capacitors for Single Phase Motors

05/25/2009 3:27 AM

Good move....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#3

Re: Capacitors for Single Phase Motors

05/24/2009 2:59 AM

I have no idea what power system you have as you do not have a location (5th dimension ) They sound like single phase, only two field windings. So only connect between phase and neutral. NOT PHASE TO PHASE!!!

You will need a clamp AC current meter as test equipment. Attach motor so that you can check current to each winding individually.

The question is do they have the centrifugal switch internally to switch out the start winding, or are they rated for continuous usage (this implies a far better quality capacitor is required!) (No start switch).

Also, I did not understand correctly, do you know what value of cap is needed?

If yes, to be safe, by ONE cap for continuous start winding. Attach to one field, start and see what happens. Check to see if current is running through BOTH fields or only one (Cent switch activated). If only one, this is the "run" winding, attach cap to the "start" winding only. Test again.

Make sure supply is fused.....have a good supply of fuses available.....be careful!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jul 2008
Posts: 4
#16
In reply to #3

Re: Capacitors for Single Phase Motors

05/28/2009 12:36 PM

thanks alot for ur info.am in kenya and am using 240vts single phase.(phase to neutral).the value of the capacitor is not known.thro ur info have managed to run one of the motors with a 10 microfarad cap(it has a cent switch).the other doesnt have am working on it .i will keep u informed otherwise thanks. we are in a very remote area where internate is not readly available therefore sorry for my delay.

Register to Reply
2
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#6

Re: Capacitors for Single Phase Motors

05/24/2009 10:03 AM

Do you have a model number and name of the manufacturer known to you or was it purchased from junk yard scrap?

1kW motor may work well with 6uF to 10uF paper capacitors of 400V. However for proper power factor, you need to trim the capacitor value.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply Good Answer (Score 2)
Member
Philippines - Member - New Member

Join Date: May 2009
Posts: 6
#14

Re: Capacitors for Single Phase Motors

05/25/2009 2:52 AM

I believe from your test results from point of view; high current starting would have a lower resistance winding, from the formula itself they are inversely proportional and the higher resistance would be the running winding, try to open the internal structure of the motor and look the starting capacitor rating but dont alter the connection inside. If you are indoubt, but you are only after which wiring is starting or running. that's all.

Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (6); dkwarner (4); Isti80 (2); jack of all trades (1); nzioka (1); ohmarglen (1); Shyam (1)

Previous in Forum: electrical projects for engineering students   Next in Forum: "Does a DC motor run on AC current"

Advertisement