Query

05/29/2009 4:12 PM

Trying to get my head round this. Lets take a 240V single phase supply powering a 60 watt light. If I take an amp-probe and clamp it round the phase conductor I will obtain the current flowing in the circuit. This said current is then flowing through the element of the light and back through the neutral to complete the circuit.

If this current is flowing through the element why if I put my amp-probe on the neutral wire can't I measure the current flowing back through the neutral. where does it go?

Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Query

05/29/2009 4:27 PM

If you clamp it around only the neutral you should read the same amperage. If you clamp around the phase conductor and the neutral at the same time you will read zero.

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: Query

05/29/2009 9:10 PM

If you clamp it around the neutral conductor, you will get no reading. When the current from the phase conductor flowing through the element of the bulb and because of the resistance in the element, the current will be restricted by the element resistance and causes the element to generate heat. The heat is then converted in to light. All the current will be used up by the element. That why, the neutral conductor will be zero.

You will not able to get any current at the neutral conductor.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#3
In reply to #2

Re: Query

05/29/2009 9:21 PM

Are we missing Kirchoff's current law?

The Post #1 is correct, the phase current and the neutral current will be equal in a single phase circuit. (the same is not true for a multiphase circuit of course)

Unless some one has connected the load across phase and earth of course (and you don't have the Earth fault MCB at your home switchboard)

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#4
In reply to #2

Re: Query

05/29/2009 11:35 PM

Simon... current flows from the source to the load then from the load back to the source. Current is not consumed.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #2

Re: Query

06/01/2009 4:37 AM

So, why does the lamp go out when the neutral conductor is disconnected from the supply, then?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5

Re: Query

05/29/2009 11:46 PM

How many conductors run to your 240 volt light? Three or four? What is the nature of the system? Is it a standard American/Canadian 120/240 volt single phase 3 wire consumer service?

If the system is a standard 120/240 volt 3 wire service, you should have two hot conductors, lets call them L1 & L2, and a bonding conductor going to your lamp. In this setup, there is no neutral connected to the lamp. Current on L1 & L2 should equal each other as current flows from the system source to a load then from the load back to the source.

Please describe the system type and the number of conductors going to the lamp.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#6
In reply to #5

Re: Query

05/30/2009 12:06 AM

What ever may be system, the tong tester or ammeter connected to any one side of the device( source side,return side) should show the same current.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7
In reply to #6

Re: Query

05/30/2009 10:15 AM

Obviously...

I asked for the nature of the system to try and reason why he sees no current on the "neutral". About the only way it make sense is if, there are four wires going to the light, two hots - a neutral (that is not used) - and a bond wire.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Power-User

Join Date: Mar 2009
Location: Egyptian in Saudi Aarabia
Posts: 112
Good Answers: 12
#8

Re: Query

05/30/2009 4:00 PM

measured current will not change , may you measured volt ?

if it's so, it will gave zero reading for neutral.

__________________
don't tell me who are you , what do you know is enough.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Query

06/01/2009 4:39 AM

One of the possibilities that there is no current in the neutral conductor is that the return path in the posted case is via the earth conductor. Never do this! The earth conductor is there for personal safety and should never carry current except under fault conditions while the circuit protective device operates.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856