Control Valves and Line Size

06/08/2009 2:40 AM

This is regarding control valves.

-We are reducing control valve size from that of line size. Why?

My understanding is for better performance & hence to save cost.

-W are treating XCV, MOV, FCV, etc. as control valve but we are reducing valve size only for FCV & not in case of XCV, MOV. Why?

__________________
Be simple and specific for a great success in Life
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: control valves

06/08/2009 4:00 AM

What does the Process Description document say on the topic?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#2

Re: control valves

06/08/2009 8:43 AM

Hi there,

You need to look at this as an overall picture.

1. What is the required flow rate (Cv)

2. What is the process data

3. What is the line size, and the valve size to be.

You then need to do a few calculations.

It would be very expensive indeed to make all your control valves the same size as the line size. You would like to know whether you have chocked flow, turbulant flow etc.

I would advise you to get hold of the ANSI/ISA-75.01.01-2002 standard (Flow equations for sizing control valves). You should also dowload the fisher control valve hand book. www.emmersonprocess.com

This will explain to you the effect and the maths behind reducers and things that go with the control valve.

Regards,

Craig

Register to Reply
Anonymous Poster
#3

Re: control valves

06/08/2009 8:56 AM

Control valves that perform a regulating function ( not full open or full closed) need to be sized. They act as a "pressure bank" in the system and therefore have to be carefully sized to obtain the desired control. Hence the Cv of the valve must be calculated. If this is done properly, you will find that tuning in the valve to operate automatically will be easy and your desired setpoint will be maintained well. Generally you will find that the size of the valve will be smaller than the line size ( not always!). Hopefully you have your line size properly calculated as well.

Register to Reply
Associate

Join Date: May 2009
Posts: 41
#4

Re: Control Valves and Line Size

06/11/2009 4:58 AM

Genrally the valve port size will be smaller than the pipe line, it is so, because to reduce cost. this type of valve is called as reduce port size valve and the valve which have port size equal to line is called as full port valve. valve port size should not be less than 50% of the line dia. CV value plays an important role in determining the size of the port in control valves.