Connecting a Moving Coil Meter to a 4-20mA Signal

06/28/2009 3:36 PM

I hooked up a moving coil dc meter to a 4-20mA signal in the hope that it would display my loop current value, as I could see it on my digital Fluke meter. On the Fluke dc mAmp scale it shows 12mA but nothing displays on the analogue moving coil meter. Is this due to the impedance of the meter and how can I overcome this? This moving coil meter does work when I drive it with a Fluke process calibration unit. The voltage I get from the Allan Bradley analogue output is between 0v to 5v dc.

__________________
Observe-Plan-Execute-Monitor-Control
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: How to connect moving coil meter to 4-20mA signal.

06/28/2009 7:12 PM

What resistance do you measure, using the Fluke DMM to look at the moving coil meter (nothing else in circuit)?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Associate
Safety - ESD - Inspect all things, keep the good things safe! New Zealand - Member - PalmerstonNorth -hub of the Manawatu.

Join Date: May 2008
Location: Australasia
Posts: 26
#12
In reply to #1

Re: How to connect moving coil meter to 4-20mA signal.

06/30/2009 2:12 AM

Hi, when measuring the resistance over the mA meter`s terminals, I get on my Fluke 2Mega Ohms??? I know this sounds bizaar, since an amp meter shouldn`t have any resistance or very little, but a volt meter should have high resistance.

__________________
Observe-Plan-Execute-Monitor-Control
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#13
In reply to #12

Re: How to connect moving coil meter to 4-20mA signal.

06/30/2009 2:36 AM

Sounds bizaar? Sounds more like broken. If the needle isn't bent from wrapping on the stop pin, someone may have applied ac to it and fried it.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#14
In reply to #12

Re: How to connect moving coil meter to 4-20mA signal.

06/30/2009 9:39 AM

There are two fuses (one per input current range) for all Fluke multimeters models that I have used. Since the fuse only exist in the ammeter circuit, you've probably had it blown for awhile and not known it.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#15
In reply to #12

Re: How to connect moving coil meter to 4-20mA signal.

06/30/2009 12:53 PM

You say that you used a Fluke meter set to measure resistance of the meter and got 2 megOhms.

If it is a Voltmeter and if the needle moves freely and is was not resting tightly on the peg the Ohm meter connected should have at least caused a small deflection.

A 50 microamp 2 megohm meter would take 100 Volts DC full scale.

I previously mentioned that the meter face usually has information about what the numbers on the scale represents with multipliers or shunts installed and/or the actual meter movement characteristic like "50uA FS" unless it has been modified since.

How about some more info to work with?

Register to Reply
Guru

Join Date: Dec 2005
Location: Etats Unis
Posts: 1871
Good Answers: 45
#2

Re: How to connect moving coil meter to 4-20mA signal.

06/28/2009 10:59 PM

Measure the resistance of the moving coil meter out of circuit then monitor the voltage across the meter. I=V/R.

__________________
The hardest thing to overcome, is not knowing that you don't know.
Register to Reply
Guru

Join Date: Jan 2009
Posts: 1011
Good Answers: 25
#3

Re: How to connect moving coil meter to 4-20mA signal.

06/28/2009 11:58 PM

"On the Fluke dc mAmp scale it shows 12mA but nothing displays on the analogue moving coil meter."

Did you connect the Fluke meter set to measure current and the moving coil Amp Meter in series and apply a current? Current on the Fluke but nil on the analog meter?

What current from the Fluke Process Cal unit made the meter needle move?

Most analog meters show their current rating on the meter face near the movement. Sometimes people put current shunts inside them and don't record the new value.

I have received new D'Arsenval Meters that had no connection at all.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: How to connect moving coil meter to 4-20mA signal.

06/29/2009 3:22 AM

Are these two meters wired in series or in parallel?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2005
Location: Etats Unis
Posts: 1871
Good Answers: 45
#5
In reply to #4

Re: How to connect moving coil meter to 4-20mA signal.

06/29/2009 3:58 AM

Sounds like he put them in parallel. Current meters must be put in series.

__________________
The hardest thing to overcome, is not knowing that you don't know.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: How to connect moving coil meter to 4-20mA signal.

06/29/2009 8:15 AM

Quite.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7
In reply to #5

Re: How to connect moving coil meter to 4-20mA signal.

06/29/2009 10:55 AM

It also sounds like the digital meter has a lower input impedance.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Dec 2005
Location: Etats Unis
Posts: 1871
Good Answers: 45
#8
In reply to #7

Re: How to connect moving coil meter to 4-20mA signal.

06/29/2009 12:52 PM

Of course, but really a minor issue since hooking ammeters in parallel is not a good plan from the start. In theory you could simply add the two readings but practically speaking it's a bad idea.

__________________
The hardest thing to overcome, is not knowing that you don't know.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9
In reply to #8

Re: How to connect moving coil meter to 4-20mA signal.

06/29/2009 1:05 PM

Of course ammeters should be used in series to get confirming results. I was just trying to add another layer of detail for others to figure out what is happening. Particularly why two parallel ammeters that ideally should have no resistance would not display an even distribution of current. A simple application of KCL, KVL and either loop or mesh analysis will inform a novice what happened.

I was merely dotting some i's and crossing some t's for those unfamiliar or unwilling to do the task.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 4)
Guru

Join Date: Dec 2005
Location: Etats Unis
Posts: 1871
Good Answers: 45
#10
In reply to #9

Re: How to connect moving coil meter to 4-20mA signal.

06/29/2009 5:05 PM

No such thing as an ideal ammeter, they all have resistance and often different for different meters. I often need to meter down to micro-amps and most meters insert anywhere from 100 to 1000 ohms to read that low. Problems arise when it is a circuit that then "wakes up" and goes into 10's of milliamps but crashes since the series resistance drops too much voltage. Moving vein meter probably has more resistance to operate than solid state meter that doesn't require as much power to move a mechanical component.

__________________
The hardest thing to overcome, is not knowing that you don't know.
Register to Reply Off Topic (Score 5)
Anonymous Poster
#11

Re: Connecting a Moving Coil Meter to a 4-20mA Signal

06/29/2009 11:08 PM

try a 250 ohm resister in the loop

Register to Reply
Register to Reply 15 comments