Gentlemen,
I am looking into the possibilty of supplying a 6" fire hydrant ring main through a 3" mains water supply pipe. The 6" water main has been reduced down to 3" to supply a refinery. The pressure of the mains is approx 4-6 bar.
I am concerned about the ability of the 3" pipe to replinish the fire hydrant if a number of points are used to fight fire. There are eight 2 1/2" hydrant points. The hydrant has to supply 1500 lpm @ 1.5 bar as recommended by the fire service. I guess what I am asking is whether a 3" pipe @4-6 bar will supply sufficient water to a 6" ring main which requires 1500lpm @ 1-2 bar.
Are there any calcs I can do to prove if the 3" supply feed is "man enough". There is a flow meter installed, however this pipe does supply a large refinery.
What do you guys think? If you need any more info, please let me know.
P.S Apologies for the long winded nature of the question.