Hi can someone help with this question?

Can a potentiometeric joystick connected by an I.S. barrier be used in a Zone 2 area without any additional certification.

Our supplier is offering a choice of two a basic joystick or one Atex certified as

EEX d IIC T6 for the switches

EEx de IIC T6 for the resistive track

I am tempted to pay the extra £1000 for peace of mind but is this the way to go?

Regards Al

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Joystick Selection

07/27/2009 3:43 PM

So from what you are saying one joystick is Ex rated and hence requires no intrinsic safety barrier (or intrinsic safety isolator) and the other is a standard joystick which is protected by an intrinsic safety barrier (or isolator).

Yes. Either would be fine for Zone 2 BUT for the standard joystick with intrinsic safety barrier (or isolator) option you need to ensure the intrinsic safety conditions are met and the correct barrier(s) (or isolator(s)) are specified. This shouldn't be a problem if it is a standard passive resistive element joystick (becomes more complicated if the joystick has active elements such as motorisation).

IS requires a bit more work to initially design but will likely be cheaper (even when taking the equipotential earthing into account when using zener barrier(s)). In the end both options are acceptable so you can use either (they are just different hazardous area protection techniques).

__________________
jack of all trades
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Joystick Selection

07/28/2009 3:48 AM

<...Can a potentiometeric joystick connected by an I.S. barrier be used in a Zone 2 area without any additional certification....>

Yes, provided all circuits are protected by certified Ex i barriers and the L/R ratios of the cables fall within Ex i parameters. Switches and potentiometers are "simple apparatus" under Ex i, as they are non-energy-storing devices.