Anonymous Poster

Circuit Breaker MCB

09/03/2009 1:43 AM

As per my understanding,we can connect the live power cable on any side (top or bottom of the switch) of the MCB. But today one of our senior customer was mentioning to one of my colleagues that we should connect it only at the top. Is he right and if he is, what is the logic?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Circuit breaker MCB

09/03/2009 3:13 AM

What does it say in the MCB manufacturer's instructions?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#2

Re: Circuit breaker MCB

09/03/2009 4:05 AM

Unless specifically required by the manufacturer, the MCB will not be effected by how the load and supply are connected.

However, various Standards, Federal, State and Utility regulations will impact how the MCBs are installed.

In Australia the Standard does not care about the direction of connecttion, only that all the breakers operate in the same direction (i.e. Closed is Up) on all breakers in that DB.

Beyond that, it may have been specified in a particular way at the desing stage, or he\she has their own preferences.

Regards,
Sapper.

__________________
It's all about the Boom! - MythBusters
Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#3

Re: Circuit breaker MCB

09/03/2009 4:15 AM

Circuit breakers often have connections labeled L1 (L2,L3) and T1 (T2,T3) - it is usual (and may be necessary) to connect the line (live) side to the L terminals.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#4

Re: Circuit breaker MCB

09/03/2009 5:14 AM

Your senior customer was correct. As an electrician or an engineer, we always follow the standard procedure to do the connection, either to the MCCB or to the contactor down to the relays. The top is always the incoming and the bottom is the outgoing.

Standardization is the best policy and everyone will knows that the top is always the incoming cable.

Of course, at some time, there is some cases there we need to use the bottom of the MCCB as the incoming. But you need to put some danger tag indicating the incoming cable.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Anonymous Poster
#5
In reply to #4

Re: Circuit breaker MCB

09/03/2009 10:44 PM

Standardisation is good. But I think the user was looking for a technical reason. Is there any?

Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#6

Re: Circuit Breaker MCB

09/06/2009 3:19 AM

MCBs that are made for connection in only one direction are explicitly marked for identification of LINE side (and sometimes LOAD side).

unmarked MCBs are assumed to be made for connection in either direction. i however contend that good manufacturers should mark on the device clearly that it suitable for connection in either direction. MCB users are not always technically trained.

the limitation when specified by the maker is for good reason. the mechanical design of the trip mechnaism, fixed/moving contacts and arc spaces available are some of the criteria for this requirement. the arc quenching that happens during break requires heat dissipation and also has to happen within specified time. this is possible if the arc elongates in the desired direction as the moving pole withdraws from the fixed pole. during this process the flow of energy in the right direction aids and accelerates the opening by creating repulsion forces.

read also -

http://www.maintenanceresources.com/referencelibrary/ezine/eleccircbreak4.html#line

Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2008
Posts: 24
#7

Re: Circuit Breaker MCB

09/06/2009 8:16 AM

Thanks guys. Appreciate all your comments.

Reply Off Topic (Score 5)
Reply to Forum Thread 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); EngineerInTheMaking (1); JohnDG (1); PWSlack (1); Sapper (1); Simon Wan (1); soebfatehi (1)

Previous in Forum: Electrical Feeders and Panels   Next in Forum: Phase Sequency Changing Problem

Advertisement