Phase Sequency Changing Problem

09/03/2009 4:30 AM

Good day to all,

I have faced some problem my Data Center Power related issue.

My problem as follows:

1. Some times our commercial power supply company changing the phase sequence (RYB to YBR or BRY).

2. As a result our Air-con are stoped for performance (Compressor stoped) and given phase failure alarm , then manually we changed the power cable .

3. Please give me good solution for that problem

4. Which is suitable for us , we put Automatic Voltage Regulator (option of phase correction funtion)

5 Or any Phase sequence correction relay put on Air-con side

Emran

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Phase sequency changing problem

09/03/2009 5:00 AM

One possibility is to introduce a variable frequency drive into the motor starter. The drive will provide the correct phase rotation on the outlet leads at all times, whatever the inlet power is doing.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#2

Re: Phase sequency changing problem

09/03/2009 6:30 AM

From your post, your phase rotation stays the same. RYB=YBR=BRY

Now if it changed to say RBY that would change the rotation.

It sounds like you are getting power interuptions to one or more phases intermittantly which is tripping the Air Conditioning units.

At this point I would suggest you get loggers put on the supplies and watch what is happening with your power.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#5
In reply to #2

Re: Phase sequency changing problem

09/05/2009 12:59 PM

DEAR,

EXACTLY THE SAME.

I THINK THERE IS A SINGLE PHASING .

__________________
Exploring the Science of Electricity
Register to Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#3

Re: Phase Sequency Changing Problem

09/04/2009 7:41 AM

Given on what it would take to swap phases in a grid system, it would be hard for me to believe that this would be happening on a consistent basis. If you compressors are shutting down on a "phase loss" thats probably is what is happening. If thats the case there is not much you can do about it except install a redundant system to run until the grid is repaired and goes back on line.

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4
In reply to #3

Re: Phase Sequency Changing Problem

09/04/2009 10:34 AM

It is surprising that the utility company changes the phase sequence but it happens, especially in the third world. I worked in a utility company at the very beginning of my engineering career and it was a common practice there to change the phase for balancing the loads in the distribution lines.

To avoid this problem, the only good solution is to use the VFD as suggested by PWSlack. However, you can use a three pole manual transfer switch (see the figure how to connect the transfer switch). This doesn't prevent the Air-con service interruption, but you can do the change very quickly – don't need to change the power cable every time it happens.

Hope it helps,

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Sep 2009
Location: Houston, TX
Posts: 118
#6

Re: Phase Sequency Changing Problem

09/13/2009 6:50 PM

Sir, with all do respect I think someone is yanking your crank! Remember, your utility company has motors too and I can't see their electricians swapping cables when they would decide to do this.

__________________
Thank you for your help - By far the best info site!
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

GRAY HAIRED OLD GOAT (1); harry potter (1); jraubsr (1); msamad (1); PWSlack (1); Sapper (1)

Previous in Forum: Circuit Breaker MCB   Next in Forum: Converting Live Loads to Dead Loads

Advertisement