400-hp Motor Amperage

09/10/2009 3:47 PM

Good afternoon to all contributors.

We have an issue at our facility with a 400 hp 3 phase 60 Hz ac motor.

The motor is a 12 lead 3 phase motor that is currently running extremely hot.

Phase A = 64 AMPS Phase B = 67 AMPS Phase C = 147 AMPS

The motor was recently repaired 2 to 3 weeks ago, and our incoming voltage to the motor is : Phase A -B = 477 VOLS Phase B-C = 477 VOLTS Phase C-A = 480 VOLTS

Motor starter component have been verified and everything checks O.K.

Could the reason for the inbalance on current be associated with improper repairs of the motor windings?

Individual winding coils were checked with the following results:

Coil 1 = .2 ohm, Coil 2 = .2 ohm ,Coil 3= .3 ohm ,Coil 4 = .2 ohm ,Coil 5 = .2 ohm

Coil 6 = .2 ohm

Comments are greatly appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#1

Re: 400-hp Motor Amperage

09/10/2009 4:15 PM

The only way I know of that a single phase line an ever read higher than the other two combined phase lines is if you have a shorted winding taking power to the grounding system. Check your neutral and ground lines at the power source and see if it changes when the motor is running.

Register to Reply
3
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: 400 H.P. MOTOR AMPERAGE

09/10/2009 4:22 PM

Could the reason for the inbalance on current be associated with improper repairs of the motor windings?

Yes. It looks like a problem with the motor windings, immediately take the motor out of service if you have not already done so.

What are your A-B, B-C and C-A resistances? If they are all the same I would suspect one (or more) of the windings has been reinstalled back to front and are acting against the other windings causing excessive heating and the current imbalance. Consult the motor repair shop for clarification and rectification of the problem.

__________________
jack of all trades
Register to Reply Good Answer (Score 3)
Power-User

Join Date: Jan 2008
Location: kuwait
Posts: 132
Good Answers: 2
#10
In reply to #2

Re: 400 H.P. MOTOR AMPERAGE

09/12/2009 4:16 PM

i do agree with you and recomend him to check the coil to coil insulation also , in normal every coil should be isolated from the others with open ends.

this problem seems the parralel coils togather.

and for this reason the internal resistance is droping and creating less or reverse

tourqe to all sets.

regards

__________________
love4everyone
Register to Reply
Commentator

Join Date: Sep 2009
Posts: 59
Good Answers: 3
#3

Re: 400-hp Motor Amperage

09/10/2009 8:37 PM

The inbalance of current ( causing the over heating )while the motor is running could be due to improper neutral earth at the supply.That can be unconnected earth or resistive earth ( hot neutral cable if it is under size ).This can be checked with the phase to phase terminal voltages of the motor when it is running.One reading should be quite different from the other two.

The resistive ohm of the coils are quite equal but it cannot tell as thick conductor coil can have a few turns less or more and contribute to differences in reactance/impedence thus inbalance loading.

Kindly let us know the outcome,I wsh to learn more.

Regards,

Khor.

Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#4

Re: 400-hp Motor Amperage

09/10/2009 9:16 PM

You should check coil to ground resistance on all coils with a megger- use nothing less than 1000 V test voltage for your 480 V system- higher would be better (i.e., 5000 V).

Register to Reply
Active Contributor

Join Date: Apr 2007
Posts: 14
#5

Re: 400-hp Motor Amperage

09/11/2009 5:29 AM

I think it is due to motor winding coils start and end connection not don properly. For Exmp: A1-a2,B1-b2,C1-c2 like all the 6 coils.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6

Re: 400-hp Motor Amperage

09/11/2009 6:43 AM

What sort of meter did you use to measure your OHMs?

Did you check for shorts to ground?

Did you seperate the leads before measuring?

Is it possible that one of the coils has been reconnected backwards?

Do you know how to check each coil's polarity? If yes, do that for each coil.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Aug 2006
Location: Adirondacks of NYS
Posts: 136
Good Answers: 7
#7

Re: 400-hp Motor Amperage

09/11/2009 6:50 AM

Because the motor has 12 leads, it is possible they may been miss-labeled during the rebuild, causing you to place coils A & B in series, as in a 480V connection (normal amps), and C coils in parallel, as in a 240V connection. Or Jack could be correct, one or both are installed in the opposite direction. Take it back or get the shop to bring a motor analyzer to the site, which ever is easier.

__________________
If I hear hoofbeats, why don't I ever think a Zebra might be around?
Register to Reply Score 1 for Good Answer
Participant

Join Date: Feb 2009
Posts: 3
#8
In reply to #7

Re: 400-hp Motor Amperage

09/12/2009 2:45 AM

I suspect that Spark Chaser is on the right track. This sounds like that one or more coils are reversed in polarity. If the wiring was changed inside the motor I would check this real close. The other option that I have seen is several loops of a set of coils being shorted.

Register to Reply
Power-User

Join Date: Sep 2009
Location: Houston, TX
Posts: 118
#9

Re: 400-hp Motor Amperage

09/12/2009 10:28 AM

If the motor has ever been repaired because it blew a hole in the rotor, it will always run hot as laminations were damaged. Make sure your check voltage at the motor and NOT the starter! I'm also assuming that you've checked connections for tightness. I'm also assuming you have ground detector lights or some sort of continuous insulation monitor. If your using a soft start, insure that the bypass contactor kicks in and that your not running below rated rpm. I don't really know why you mentioned that it was a 12 lead machine unless you suspect someone connected it wrong! That'll do it every time!

__________________
Thank you for your help - By far the best info site!
Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard