POWER FLOW IN H.T. CABLE

10/24/2009 4:01 AM

I am posting this peculiar problem which I have come across for the first time in my service. I seek the view and advice of CR4 Forum Members, so that I can understand the problem and reach at a possible solution.

We have 2.5 MVA CAPACITY Transformer of 11 KV, Input Voltage and connected to 2 different Source of Power Supply feeding to this Transformer, with proper CIRCUIT INTER-LOCKINGS, and working for the 9th year.

The Power Supply is - one source from the Electricity Board, and other source from a Turbo Alternator of 6 M.W, WHICH IS ALSO FEEDING TO 2 OTHER Transformers of Identical 2.5 MVA CAPACITY, and there is no problem in these 2 transformers.

The problem with the first transformer is this: 1. When E.B supply is charged , it is holding and takes the load. 2. When we change over to the Alternator supply, it does not even works for a second and the breaker trips. The Breaker is alright. In order to clear the doubt we shifted the other breaker and installed, the same thing or problem repeated.

Now the question is: Either the Transformer Breaker should hold and take the load or trip in irrespective of E.B., or ALTERNATOR SUPPLY. But it is not so.

NOW THE CR4 FORUM members can give their view and share their experience, how and why it happened like that.

DHAYANANDHAN.S,

CR4 MEMBER,

INDIA.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Sep 2009
Location: Medan - Indonesia
Posts: 34
#1

Re: POWER FLOW IN H.T. CABLE

10/24/2009 6:15 AM

hallo dhayanandhan,

would you please to describe about your "proper CIRCUIT INTERLOCKING system" ?? (single line diagram will be best) …is that correct you say it happened after 9 years without problem??

Since the Turbo alternator supply to 3 transformer's CBs (A,B,C transformer) …have you double checked that the Interlock CBs are correct??

Based on your description I would suggest that you must localize your problem first by trying to do this step by step :

  1. - shut down the EB before change it to the Alternator supply
  2. - disconnect the transformer before do the change over
  3. - observe about what causes the CB trip, whether power reverse, over voltage, earth fault etc so that you can determine the fault.

thank you & cheers,

__________________
A Wise Man changes his mind, a fool never will
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#3
In reply to #1

Re: POWER FLOW IN H.T. CABLE

10/24/2009 9:37 AM

Dear Mr. Tootie,

Thank you for your immediate response and I will furnish the details such as single line diagram etc. shortly.

Thank you once again.

DHAYANANDHAN,

CR4 MEMBER, INDIA

Register to Reply
Anonymous Poster
#2

Re: POWER FLOW IN H.T. CABLE

10/24/2009 9:26 AM

And also check the type of load for the three transformers?

May be under some capacitive condition, this problem is happening. (the difference is between the infinite grid - EB vs finite power supply- alternator)

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6
In reply to #2

Re: POWER FLOW IN H.T. CABLE

10/25/2009 1:27 AM

Dear Guest,

Thank you or your response and advise. I will check up in the manner you have suggested and give you the feed back, so that it will be useful for CR4 MEMBERS.

DHAYANANDHAN.S, CR4 MEMBER,

INDIA.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#4

Re: POWER FLOW IN H.T. CABLE

10/24/2009 9:38 AM

Hi dhayanandhan,

Is the breaker trips on overcurrent or earth fault? Since the Panel is functional through the breaker from EB the rest of the HT panel and down stream distribution appears to be normal. You state that the breaker is also functioning normal.The points to be clarified are(i) when the changeover is being done supply from EB is available or not. (ii) Is the interlocking still functional.(iii) Is the breaker has draw out earthing system for safety if so weather it is functional? (iv) Did you carry out megger test of the breaker terminal point (v) CT & PT of the panel is checked for normal functioning and insulation? Did any Phase sequence done on cable either at EB side or Local Generator side. Please check and see weather you can locate the fault.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5
In reply to #4

Re: POWER FLOW IN H.T. CABLE

10/25/2009 1:26 AM

Thank you Mr. Abraham, for your response and advise. I will check up in the manner you have suggested and give you the feed back, so that you will know what could be the error, and it will also be useful for CR4 MEMBERS.

DHAYANANDHAN.S, CR4 MEMBER,

INDIA.

Register to Reply
Commentator

Join Date: Aug 2008
Posts: 82
#7

Re: POWER FLOW IN H.T. CABLE

10/25/2009 2:19 AM

When change over is opted for this trfr while other two trfrs are in cut off state -

response could be clueful .

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8
In reply to #7

Re: POWER FLOW IN H.T. CABLE

10/26/2009 7:05 AM

Thank you Mr. Sivaa, for your response. It is not possible to isolate the other 2 transformers. What is possible is while changing over to the Turbo-set Power it is possible to charge this transformer first and observe, then charge the other 2 transformers.

By trying this method there is a possible problem that the feed water pums starting cannot be delayed beyond a particular duration which will be in 40 to 50 seconds and by this time the boiler pressure will come down.

DHAYANANDHAN.S,

CR4 MEMBER,

INDIA.

Register to Reply
Commentator

Join Date: Aug 2008
Posts: 82
#9

Re: POWER FLOW IN H.T. CABLE

10/26/2009 9:38 AM

For this trfr ; O/P current rating when compared with second trfr ; with E.B. Supply - is it more ?

Connected load can be partially switched off { !! } for this trfr , while changing over - for observations , please .

As Interlock mechanism is considered for satisfactory performance , such parameters are to be considered . Else , we need to refer that .

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#11
In reply to #9

Re: POWER FLOW IN H.T. CABLE

10/31/2009 1:58 PM

Dear Mr.Sivaa,

The current rating is similar. The transformer has load of 5 to 6 % of full load.

Still the problem evades and mystery.

DHAYANANDHAN.S,

CR4 MEMBER,

INDIA.

Register to Reply
Participant

Join Date: Feb 2008
Posts: 2
#10

Re: POWER FLOW IN H.T. CABLE

10/28/2009 3:42 AM

Hello Mr Dayanandhan,

base on your description about your power system your are not synchornousing EB grid

with your TG supply. It seems the problem may be with the Ht cable connecting

between TG HT breaker panel to Transformer breaker panel or faulty relay or relay

setting.please check & confirm.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#12
In reply to #10

Re: POWER FLOW IN H.T. CABLE

10/31/2009 2:03 PM

Dear Mr. Kamalakar,

the relays are O.K. We are not synchronising with Grid. It is only cutting the grid and switch over to Turbo-alternatr supply. What could be the problem is still evading, and remains mystery. When it is O.K with grid supply it should be O.K for any supply.

DHAYANANDHAN.S,CR4 MEMBER.

Register to Reply
Anonymous Poster
#13

Re: POWER FLOW IN H.T. CABLE

11/01/2009 1:22 AM

It must be the inrush current that is handled by the generator AVR and making the breaker to trip, the grid impedance whereas will cause the voltage to drop, making current go down and saving the trip.

Did you try to cut off some loads on the transformer while change over and see?