neutral current

11/17/2009 5:33 AM

please let me know,what does it mean if the neutral current in a 3 Ph circuit is higher than the other 3 phases,,,as ex::R=17O A ,y=180 A ,B=175 A,,,,,but the neutral current is about 280 A !!!!?????does it mean that there is a leakage current or what??????

regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#1

Re: neutral current

11/17/2009 7:50 AM

needtoknow; is the neutral warm/hot to touch? are you reading harmonics? perry

Register to Reply
Active Contributor

Join Date: Nov 2009
Posts: 12
#7
In reply to #1

Re: neutral current

11/18/2009 6:30 AM

perry;;;it is littel bit warm???is it risky ???

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #7

Re: neutral current

11/19/2009 3:14 AM

It is risky if the current exceeds the neutral conductor's carrying capacity. Is the neutral the same cross-sectional area as the other conductors?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2009
Posts: 12
#11
In reply to #9

Re: neutral current

11/23/2009 7:17 AM

pwslack

yes it is,the neutral cable cross section is the same as the three Ph's which is 4c*95mm2,and as i know this cross section can carry up to 270-280 A,so in order to avoid any problem i would decrease the load,,i thought that the un balance between the three Ph's doesn't mean this much less,,cause i think when we say un balance ;means more than -+(50)A between the 3Ph's

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: neutral current

11/17/2009 8:05 AM

Is there a single phase generator connected to one of the three phases downstream of the measurement location?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Nov 2009
Posts: 12
#8
In reply to #2

Re: neutral current

11/18/2009 6:38 AM

pwslack;;no..there is no single phase generator connected to any phase...but i am getting the power to my 3 phase load from this 3 ph generator as usuall,and i am using a digital ammeter to cheack each phase current,but the neutral still higher than the 3 ph's .

Register to Reply
Anonymous Poster
#10
In reply to #8

Re: neutral current

11/22/2009 5:27 AM

In case any of the three phase load is a motor, it wouldn't have survived. In any other of the various typical 3 phase circuits also the single phasing is ruled out - (two phases connected at source).

Did you check up the voltage - phase-phase and phase to neutral? This would have given an insight to what is happening.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: neutral current

11/17/2009 9:23 AM

It definitely implies presence of Triplen Harmonics in your system. Do undertake a Harmonic Study.

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#4

Re: neutral current

11/17/2009 11:13 AM

Oee have to doubt over the harmonics.......may be you have many nonlinear loads,switching devices n all..........

__________________
"Know something about everything and everything about something"
Register to Reply
Active Contributor

Join Date: Nov 2009
Posts: 20
#5

Re: neutral current

11/17/2009 7:11 PM

Multiple earthing also cause circulating current ,if your system has multiple neutral grounding

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#6

Re: neutral current

11/17/2009 8:26 PM

Check the voltage between phases. If you happen to have two of the phases connected together at the source you would get neutral reading as you are showing.

Register to Reply Score 1 for Good Answer
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); giri (1); JOSHIKD (1); needtoknow (3); perry (1); PWSlack (2); wareagle (1)