Anonymous Poster

Calculating Cable Size and Length

11/19/2009 12:29 AM

I have One rosemount Pressure transmitter , loop powered 24VDC and Loop impedance 600 ohms...it will be installed in the Zone 1 divII

pls tell me how to calculate cable size and length.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2008
Location: East Tenneesse, USA
Posts: 685
Good Answers: 46
#1

Re: cable

11/19/2009 2:17 AM

The transmitters work on a current loop 4-20ma or one of the communications like Hart, field bus, or others. Current loops only one transmitter per loop. Hart communications in multi-drop off one line can have up to 15 transmitters with the analog current set to 4ma output.

I have run upwards of 2000ft on 24ga wire to a transmitter in analog current.

Charles

__________________
Metal is the material, The forge is life, The anvil and hammer bring character and soul.
Reply
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#2

Re: cable

11/19/2009 2:44 AM

Cable Length You will Find from the-- Instrument location layout diagram

Cable size Your Client specs will specify

As a general if Wire size is 18 AWG

Then,

1)600 Loop Impedance

2)assuming 250 ohms for Control system impedance you have(600-250)= 350 ohms for cable

3) For 18 AWG Wire size 10 ohms for single wire ,(10*2) ===20 Ohms for pair cable

4)(350 /20)*1000 FT= 17500 FT

If your finding the length is more , With respect to plot plan increase the wire size to 16 AWG

Regards

Jose

Reply Score 1 for Good Answer
Anonymous Poster
#3
In reply to #2

Re: cable

11/19/2009 3:28 AM

8 more transmitters are there in the same loop.Total 9 pressure transmitter are there of same feature (24Vdc,600ohms)

Communication protocol is HART. mean to say Bell202+4-20maanalog

should voltage drop also be taken care.

is there any selection chart for Metric cables viz: 1.5sqmm/10ohmsfor each cable

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Calculating Cable Size and Length

11/20/2009 3:06 AM

Just use BS5308 cable. Size and length won't cause energy-storing capacity that exceeds the parameters applicable to EEx i circuits.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); josej (1); metalSmiths (1); PWSlack (1)