motor single phasing or double phasing

11/20/2009 7:25 AM

what i can do to save a motor from burning or breaking down if a phase had been lost from a connection to motor ??????????

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Dec 2007
Location: Cypress Calif
Posts: 741
Good Answers: 23
#1

Re: motor single phasing or double phasing

11/20/2009 7:50 AM

I'm assuming you're referring to a three phase motor. Typically three phase motors employee Mag starters, basically a contractor that incorporates some sort of current protection. If a phases is lost the protection will open and require a Manual reset.

Now day's many magnetic starters are adjustable, and of course to be effective they must be set for the full load rating of motor. MAG starters also commonly employed what was referred to as a heater on this type of MAG that heaters must be sized to match the load rating of motor.

Sometimes OEM Equipment such as large air conditioners utilized three phase motors internally. In this case there's commonly no MAG starter to protect the motors from over current conditions caused by a phase a loss.

In this situation the OEM Motors employee internal thermal overload protection, I've run into situations with the contractors have replaced the OEM Motors with three phase motors without the internal overload protection, in the event of a single phrase condition the motor will quickly fail and potentially become a fire hazard.

Of the two types of protection the Manual reset required by the MAG starter is the best, the internal overload production will prevent the motor from catching fire, and will protect it from a temporary phase loss. In the event of a permanent fault there is a good chance that the motor will damaged by the time the situation is discovered.

__________________
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore all progress depends on the unreasonable man" George Shaw
Register to Reply
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#2

Re: motor single phasing or double phasing

11/20/2009 10:08 AM

Many VFDs have phase loss protection. If your system has a VFD you may look into replacing it with one that is capable of detecting a phase loss.

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Register to Reply
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: motor single phasing or double phasing

11/20/2009 10:53 AM

If you are referring to a low voltage (440V) motor, the most effective protection against single-phasing is to use a thermal O/L relay with SP protection. Less than $ 10. Mechanically operated thermobimetal device. Awesome accuracy at this price.

If it is an expensive motor of high HP or at medium voltage, electronic relays are available.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: motor single phasing or double phasing

11/20/2009 11:06 AM

If one phase is lost the motor will stall. An overcurrent protection device installed in the drive circuit can then be used. It will trip on overcurrent during the stall condition.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5

Re: motor single phasing or double phasing

11/20/2009 11:27 AM
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: motor single phasing or double phasing

11/20/2009 1:51 PM

Hmmm... some potentially dangerous generalization here...

Bi-metal thermal overload relays are NOT a good way to protect a motor from single phasing. This has been grossly over sold by the IEC motor control manufacturers. It only works if the motor is almost fully loaded when the single phasing occurs, and only if it is already running. If the motor is not running when a phase is lost, it has no idea and will allow you to attempt to start. By the time it trips, damage may already happen.

It works via a system called a "differential trip bar" in the trip mechanism that relies upon equal force being applied by all 3 bi-metal strips. If one is "cold" because no current is flowing through it, the bar moves slightly against the other two bi-metal strips so they will trip QUICKER under a loaded condition. But if the motor is not fully loaded to where the other two bi-metal strips are bending in the first place, the overload will NOT trip at all! Unfortunately when you single phase a 3 phase motor, it creates a lot of what is called "negative sequence current" as a result of one of the phases being un-powered for portions of each cycle. Those negative sequence currents cause anti-torque pulsations in the rotor, so in essence the rotor begins to "fight itself" and heat up. Than means you often will get rotor damage even though the overall current going to the motor stator (as seen by the remaining 2 bi-metal strips) is still below the tripping threshold.

And by the way, this "differential trip bar" ONLY is found in IEC thermal overload relays. NEMA style OLRs do NOT have that feature at all, so they do NOTHING to protect against single phasing. The same is true for eutectic melting alloy OLRs.

As waross pointed out, the best way to do it is to use a Phase Monitor Relay. Of those, the best are ones sensing current, not voltage, because the voltage type can be fooled by regeneration off of a spinning motor, i.e. if the phase is lost while the motor is running, it may not detect it. Current based Phase Monitors look at the total current in each phase. It is not only fool proof, but they usually also provide phase current imbalance protection. Some solid state OLRs now have this kind of protection built-in, that's another good way to go.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: motor single phasing or double phasing

11/20/2009 9:01 PM

Well, perhaps yes, the bimetal relay with differential slider needs a minimum current (NOT necessarily mechanical load on the motor) to operate .. 33% in the case of a relay i had the privilege to work on. Very sensitive differential slider with mechanical amplification of differential movement. Happily, no-load currents of IEC motors turned out to be quite high, most often >40%, thank you very much. Maybe things are different in the USA. Relays here have therefore proved to protect motors against single phasing even at "no load". Of course, as i said before, if expense is no object, many sophiticated electronic relays are available.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
3
Member
Ireland - Member - New Member

Join Date: Nov 2009
Posts: 9
Good Answers: 2
#8
In reply to #7

Re: motor single phasing or double phasing

11/23/2009 5:34 AM

........and also motors draw much more current than no load current when single phasing (making the application for phase loss protection of the simple IEC thermal overload or motor starter / cb more likely to offer some protection).

Register to Reply Good Answer (Score 3)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: motor single phasing or double phasing

11/23/2009 5:56 AM

Thanks

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#10
In reply to #8

Re: motor single phasing or double phasing

11/26/2009 5:58 AM

Two posts and both GA !

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Carol (1); EElectrician (1); JRaef (1); kvsridhar (4); PWSlack (1); wareagle (1); YWROADRUNNER (1)