pressure and temperature dew point for compressed air

12/01/2009 1:21 AM

hi all

can anyone clarify the different of pressure dew point and temperature dew poing for compressed air.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: pressure and temperature dew point for compressed air

12/01/2009 7:00 AM

Pressure dew point is the pressure, at the system temperature, at which relative humidity reaches 100% and droplets of dew will form.

Temperature dew point is the temperature, at system pressure, at which relative humidity reaches 100% and droplets of dew will form.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Nov 2008
Posts: 16
#2
In reply to #1

Re: pressure and temperature dew point for compressed air

12/01/2009 8:20 PM

dear PWslack

why the pressure dew point is using the unit DEGREE CELSIUS , and the temperature dew point also same.In this case ... is it the 2 degree celsius of pressure dew point is same with the 2 degree celsius of temperature dew point.

Actually 'im having problem water carry over ( more condensate) in the air dryer.

is it the pressure dew point is related to the condensate discharge produced by air dryer.high pressure dew point in the air dryer system means more condensate discharge from the dryer.?

syachah

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Nov 2008
Posts: 16
#3

Re: pressure and temperature dew point for compressed air

12/01/2009 9:41 PM

why the pressure dew point is using the unit DEGREE CELSIUS , and the temperature dew point also same.In this case ... is it the 2 degree celsius of pressure dew point is same with the 2 degree celsius of temperature dew point.

Actually 'im having problem water carry over ( more condensate) in the air dryer.

is it the pressure dew point is related to the condensate discharge produced by air dryer.high pressure dew point in the air dryer system means more condensate discharge from the dryer.?

syachah

Register to Reply Off Topic (Score 5)
Participant

Join Date: Dec 2009
Location: USA
Posts: 4
#4
In reply to #3

Re: pressure and temperature dew point for compressed air

12/01/2009 11:54 PM

You are having water carry over for several reasons. But first, we need to know the air flow going into the dyer, type of dryer ( refrigerated/ desiccant), inlet temperature to dryer, ambient temperature at dryer location, humidity of ambient air, size of dryer (rated flow). Then I can give most likely suggestions for cause of water carryover.

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Nov 2008
Posts: 16
#5
In reply to #4

Re: pressure and temperature dew point for compressed air

12/02/2009 1:44 AM

Dear Amed

The air dryer specification as follow:

type:refrigerated air dryer ( R22)

Max.working pressure:10 barg

Max.working temp:45 degree celsius

Air flowrate:13.3 m3/min

ambient temperature : 35 degree celsius.

Pressure Dew point: 2-5 degree celsius

Voltage/phase/frequency:230/1/50

The actual problem is the pressure dew point is abnormal...out of design range.

we have measured the pressure dew point using the DP 300 mobile dew point instrument and we get the reading is 18 degree celsius at the outlet of the dryer.with this temperature , more condensate accumulated in the system and cause the water carry over.

you have any idea?

syachah

Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#6
In reply to #5

Re: pressure and temperature dew point for compressed air

12/03/2009 2:08 AM

Do you have in-line moisture separators with an air trap at the bottom to drain condensate PRIOR to the Air Filters of the Air Dryer?

While you solve your problem, personally to safeguard my system - I always do this immediately to take away 95% of the load off the air filters.

Steam in-line Moisture Separator : Spirax Sarco/Ayvaz/Gestra

Application: Suitable for air, gas and steam applications

were the entrained liquid load does not exeed 40%

(by weight) of the separator.s maximum gas flow

capacity. This is a traditional looking separator and

many engineers simply prefer this configuration because

they are accustomed to it.

Performance: The Wright-Austin Type T entrainment

separator, when properly sized, installad and drained,

will remove 99% of all liquid droplet and solid particle

entrainment where the droplet and/or particle size

equals or exeeds 10 microns.

Operation: Moisture-laden gas enters the inlet of the

separator where it is deflected in a centrifugal downward

motion. The entrained moisture is thrown to the outer

wall and separated by a reduction in velocity. The

separated liquid falls below the .Vortex Containment

Plate. (VCP) where it cannot be re-entrained. Dry, clean

exit gas is drawn from the vessel center and it flows

upward through the outlet of the separator.

ASME Code Construction: These type T separators

are of welded steel construction in accordance with

section 8. Division 1 of the ASME Code for unfired

pressure vessels. Inlet and outlet connections can be

rotated radially upon request.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Participant

Join Date: Dec 2009
Location: USA
Posts: 4
#7
In reply to #5

Re: pressure and temperature dew point for compressed air

12/03/2009 7:57 PM

I do have a few ideas. First your outlet dewpoint is indeed high. On a service call I would be looking at the following things-----is the condensor coil clean ?---what is the temperature of the air going into the dryer ? the airflow you list--is that what the dryer is rated for ? what is the flow going in ? how compressors are feeding the dryer ? what kw are they? do you have an air receiver between the compressors and the dryer? does it have an automatic drain on the bottom ? is it working ? where in the system are you seeing the water ? how far away from the dryer ? I know this is a lot of questions, but it helps diagnose the problem and come to a solution.

Register to Reply Off Topic (Score 5)