Replacement of Transformer

12/18/2009 3:15 AM

Currently I have 2 transformers of 500KVA and 315KVA and the cable to the transformer comes thru the utility company's Electrical pole via H.T. 11KV line.

2 separate cables 3corex95mm and 3corex185mm are connected to 315KVA and 500KVA transformer from the pole respectively.

Due to expansion in 2010, now I wish to remove these both transformers and replace with Pauwels Trafo 1800KVA Transformer with specs as required by the utility company, ONAN HV-Volts-11KV, LV-Volts-433 frequency 50HZ 3Phase.

Will these 2 in-coming cables from the pole of 95mm+185mm suffice to be connected to this new 1800KVA?

Or will i need a bigger cable?

If I need bigger cable what size is needed?

My current consumption thru the 2 transformer is 570KVA and the expansion is about 320KVA.

Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Replacement of Transformer

12/18/2009 4:16 AM

The supply cables and their circuit protection device(s) require assessment. In the UK, BS7671 contains algorithms that can be used to evaluate what to do. These algorithms are based upon the cable type and length, its method of securing, whether it is thermally insulated anywhere and by how much, etc., etc.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Nov 2009
Posts: 14
#2
In reply to #1

Re: Replacement of Transformer

12/18/2009 6:39 AM

I would prefer to put a new cable even if existing ones are well in size (and they are suit 1800 kVA trans, imho)

- you are to retrays these cables partially and relocation is not good for insulation of used cables (how old them are) ,

- will length of existing cables suit you ?

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Replacement of Transformer

12/18/2009 7:55 AM

It is a good electrical engineering practice that when you have multiple runs of cables to or from a feeder/equipment, all the runs must be of the same cross section.

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#4

Re: Replacement of Transformer

12/18/2009 12:28 PM

It is a VERY bad idea to parallel cables of different sizes. The conductor resistance and the cable impedance both will act to unbalance the load between the cables.

It does not appear that the cables are sized based on the load of your present installation. A 500KVA load draws 26A at 11KV. The 95 mm2 cable is rated for 300A, and the 185 mm2 cable is rated for over 400A. In a long cable run, the conductor size may need to be increased to account for voltage drop, but this still seems excessive. If your 500KVA transformer was 5,000 meters from the pole, you'd still have 10.965KV at the transformer.

The new 1800KVA transformer will draw 95A at full load, less than 1/3 of the smaller rating. I would feel comfortable using either existing cable by itself to supply the new 1800KVA transformer.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Anonymous Poster
#5

Re: Replacement of Transformer

12/19/2009 7:40 PM

If you ask these questions, you are not qualified to perform the work.Refer this work to a qualified company for the safety of all concerned.

Register to Reply
Participant

Join Date: Oct 2009
Posts: 4
#6

Re: Replacement of Transformer

12/20/2009 11:57 AM

Selection of HT Cable is based primarily on the Fault Level of the Substation from where you are getting the supply, the required ampacity comes next which more or less gets taken care of when Fault Level is considered.

No Using the Old Cable is not recommended 1. due to different cable sizes, fault current carying capacity is different 2. The age of cable to be considered and 3. No. of Joints in the cable to be checked.

Register to Reply