Currently I have 2 transformers of 500KVA and 315KVA and the cable to the transformer comes thru the utility company's Electrical pole via H.T. 11KV line.
2 separate cables 3corex95mm and 3corex185mm are connected to 315KVA and 500KVA transformer from the pole respectively.
Due to expansion in 2010, now I wish to remove these both transformers and replace with Pauwels Trafo 1800KVA Transformer with specs as required by the utility company, ONAN HV-Volts-11KV, LV-Volts-433 frequency 50HZ 3Phase.
Will these 2 in-coming cables from the pole of 95mm+185mm suffice to be connected to this new 1800KVA?
Or will i need a bigger cable?
If I need bigger cable what size is needed?
My current consumption thru the 2 transformer is 570KVA and the expansion is about 320KVA.
Thanks.