12 VDC Home System

12/22/2009 4:51 PM

We've been living in our house for nearly 40 years. I built it when I was a kid in my 20s. We didn't have (grid) electricity and couldn't afford to get it run 1/2 mile through the woods to our house. So, I built a 12 volt DC system for all our lights. We are using 12 volt incandescent standard house type screw-in bulbs. Some are 25 watt some are 50 watt. Our lights are powered by a very large 3,000 pound gel cell 12 volt battery bank. In the house, I used 14 ga Romex wire. The Romex comes from all directions under the house to a central hub. There is a pair of large 1 ga cables running from the hub under the house to the storage battery about 10 feet away. All these years, I haven't been using any type of protection on this 12 volt system.

My question is this. Do I need some kind of circuit breaker? Can I use the normal type of circuit breaker that is commonly used in 110 volt systems? If not, what type should I use?

We are now on the grid like normal people and the battery system is only used for lights. There are 10 lights in the system, several in each room. We never have more than 2 or 3 lights on at any given time so we are not talking about very much draw.

Our house is very small, 600 square feet. We live in a very remote area in the Siskiyou National Forest and there are lots of power failures especially during the winter, thus the need for the battery/lighting system.

As I said, we've been using this system for many years without a problem but now days I'm starting to worry about such things....

__________________
'Consider it all entertainment'
Register to Reply
Pathfinder Tags: 12 volt DC home system
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: 12 Volt DC Home System

12/22/2009 4:59 PM

An automotive-style fuse block and fuses ought to be inexpensive, easy to find, and ideal for this situation. Fire is a possibility even with 12 VDC, so the gain in safety will surely justify this project.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 4)
Anonymous Poster
#16
In reply to #1

Re: 12 Volt DC Home System

12/23/2009 8:06 PM

.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#17
In reply to #16

Re: 12 Volt DC Home System

12/24/2009 7:13 AM

Can you try and kerb your writing!! Just keep to the point and don't waste so many words each time!!!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Cosmology - New Member

Join Date: Feb 2009
Location: Halcottsville, NY
Posts: 665
Good Answers: 16
#2

Re: 12 VDC Home System

12/22/2009 5:31 PM

I'm in a similar situation. 3- 44watt solar panels plus a 24 watt wind generator. Recently hooked up to a 200w (400w start-up) converter via a 240ah marine battery that I can isolate from grid power. It gives me all the illumination I need from CFL's around the house when the power is down.

The alternative is to go to a marine catalogue and buy 12vdc CFL's. 2-3 times the price of 120vac CFL bulbs. I may have to buy one anyway, as bathroom lighting is strictly 12vdc, and I hate to miss the toilet at 2 AM. All my CFL's are less than 20w, and it has shown up in my monthly energy bills. I am typing this with a 9w CFL bulb overhead. Plenty of light.

Use the excess energy to run fans, blowers, pumps, etc..

__________________
De gustibus non est dispudandum.
Register to Reply
Guru

Join Date: Oct 2008
Location: I'm outa here
Posts: 1924
Good Answers: 196
#7
In reply to #2

Re: 12 VDC Home System

12/23/2009 1:15 AM

"I hate to miss the toilet at 2 AM"

Tippy -- Try sitting down. Nobody will see you anyway and whoever cleans the bathroom will appreciate it. Or do you insist on an audience like our spoiled dachshund?

Ed Weldon

Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Aerospace Engineering - Member United States - Member - Army Vet in the aviation industry

Join Date: Mar 2008
Location: Bridgewater, Va.
Posts: 2175
Good Answers: 119
#13
In reply to #7

Re: 12 VDC Home System

12/23/2009 1:14 PM

ROFL

I clean my bathroom and I appreciate it.

It didn't take me long after becoming single to find that it makes a big difference in cleaning effort if I sit rather than stand.

The only mistake I made was telling male co-workers about it and I still get razzed about it.

Oh, and now I never forget to put the seat down. No falling in at 2AM for me and no need to turn the light on.

Hooker

Register to Reply Off Topic (Score 5)
Anonymous Poster
#10
In reply to #2

Re: 12 VDC Home System

12/23/2009 9:26 AM

...I hate to miss the toilet at 2 AM.

Wow, are you aiming from the bathroom door?

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#3

Re: 12 VDC Home System

12/22/2009 6:58 PM

The 12 volt 13 watt CFL's hit the shelves locally this year at the home building supply center(Menard's). They are about a $1 more than the 120 Volt ones.

As far as circuit breakers you can use the standard ones in a low voltage application if necessary. I have done it a few times with out any problems. They just don't take the arc from a higher voltage DC very well. At twelve volts they don't have much problems.

Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#4

Re: 12 VDC Home System

12/22/2009 10:13 PM

Boats have nice electrical panels, with breakers, voltage meters, even amperage meters. Check marine suppliers for a fair price, keep in mind marine supplies are way overpriced, so shop around. You may find the same thing for RV wiring.

__________________
mike k
Register to Reply
Power-User
Engineering Fields - Control Engineering - Control Engineering Technical Fields - Education - Industrial Training Engineering Fields - Manufacturing Engineering - Manufacturing Training Engineering Fields - Electrical Engineering - Electrical engineering Training Engineering Fields - Instrumentation Engineering - Instrumentation Engineering United States - Member - New Member Engineering Fields - Energy Engineering - Become part of the larger group, change your world.

Join Date: Apr 2005
Location: Las Vegas, NV
Posts: 266
Good Answers: 1
#5

Re: 12 VDC Home System

12/22/2009 10:19 PM

Becuase we might not know the specifications on any particular 120v circuit breaker, I would stick with a CB specificaly desinged for 12 volt system. Wether you place protection on each individual circuit (best) or just a main CB based on total circuits wired.

Like the CBC-HB Stud-Mount Circuit Breaker (12 Volt, Type I) you might be able to save some money with an ebay search for these too.

They go from 10 -50 amp with lower amparage at less than $10. I think this http://terminalsupplyco.com/Store/Product.aspx?pc=CH-30062-20 is pretty nice for your 14 ga (20amp) wire.

You can search google and find great deals like this 20Amp Breaker for only $5

__________________
AB PLC Training onsite, On-Line, training software and more. BIN95.com
Register to Reply
Power-User

Join Date: Feb 2009
Location: TORONTO, CANADA
Posts: 134
#6

Re: 12 VDC Home System

12/23/2009 12:08 AM

Fusing is used to protect the wire from burning. The fuse "burns" instead and saves the wiring from burning your house down. With a 3000 lb battery supply you have the potential to do a lot of frying of wiring.

As with a house wiring system, a main fuse is used to limit the total current to the input wire size (use the amp rating for the wire from the electrical code based on wire diameter).

The smaller wired branch circuits require individual fuses again based on the wire size.

Does this seem excessive?, probaly not considering the consequences (Surprized an animal hasn't discovered the under house wiring yet.)

Marine supply has water resistant fuse blocks with nice heavy clamps etc. perfect for this application.

__________________
Bin there, done that, then done that again and again and now I forgot where I was.Is this what it means to get old?
Register to Reply
Associate

Join Date: Nov 2009
Posts: 34
#8

Re: 12 VDC Home System

12/23/2009 1:41 AM

14 AWG wire is good for 15A; regular circuit breaker will probably work (I see no reason why 110 V AC circuit breaker should not work on 12 V DC). #1 AWG wire is good for 110 A for aluminum or 150 A for coper (for two wire system; you can protect only one wire). It is better to protect 40 years-old wiring!

Now LED (light emmiting diod) lamps are available; they take even less energy than florecent lamps; it is like2-3 wats for the same amount of light from 60 W incandecent bolb. Good luck!

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#9

Re: 12 VDC Home System

12/23/2009 7:10 AM

You can use circuit breaker for 110 volt system,but it must be appropriately rated to protect your equipment.

Patrick Whowha

__________________
Patrick Whowha
Register to Reply
Power-User

Join Date: Oct 2007
Location: S. California, USA
Posts: 279
Good Answers: 12
#11

Re: 12 VDC Home System

12/23/2009 12:22 PM

I would use a standard house circuit breaker panel and protect the branches with 15A circuit breakers.

I would choose this standard electrical equipment over marine equipment because:

(1) anything rated for marine is expensive;

(2) if you ever do get connected to a grid, the conversion to AC will be less;

(2) standard house circuit breakers have the right trip curve to protect Romex house wiring and you will not be bothered by nuisance trips.

Current and time determine the trip point of a circuit breaker. The voltage and voltage type (AC or DC) set the opening of the circuit when tripped. 120vac circuit breakers can break 12VDC without fear of the DC voltage arcing across the breakers contacts when they open.

How do you keep the battery bank charged? I presume you have a generator. Is the generator protected from the battery bank?

Does each battery have fuse protection? If not, I would add standard automotive fusible links.

Register to Reply
4
Associate

Join Date: Sep 2009
Location: Southern Oregon
Posts: 39
Good Answers: 1
#12
In reply to #11

Re: 12 VDC Home System

12/23/2009 12:58 PM

When I first built the house, I used a 1947 CJ2A Jeep to charge the batteries. I simply ran jumper cables from the Jeep to the storage battery. That didn't last too long....Then I developed a spring on the mountain behind us and used gravity water for a pelton wheel. The spring dried up during the summer. So, that didn't last too long. I then purchased solar panels. We live deep in the woods and only had sunshine in the middle of the day and hardly any at all during the winter. That didn't last too long. All the while, I was working at the local (independant) telephone company and rubbed elbows with the PP&L guys as we shared the telephone/power poles with them. Everyday, they would give me their scraps of drop wire left over from their days work. Every evening when I got home from work, I would lay the latest piece of scrap drop wire end to end with the previous pieces of wire through the woods aming toward our house. After about a year, I had laid out wire all the way from the highway to our house. Then the PP&L guys placed a "temporary" power pole next to the highway and gave me "temporary" power to that pole. Then they loaned me a huge crimper and gave me a couple of boxes full of special water-proof connectors. I crimped everything together and POW!...We had power! The next thing I did was purchase a large, gas station type of commercial battery charger. Hooked it up. Batteries are now charged any time I wanted without worry...We lived this way for another ten years. During this time, I was using a string of huge C&D, glass cased, lead/acid batteries that I gleaned form the telephone companies surplus yard. About ten years ago, I burried 1-0-1 aluminum cable all the way from the power pole to our house. We now have 220 back here. Its still considered temporary power by PP&L. But, we are on the grid! Now days I can weld and do lots of other things that weren't possible in the early days. Of cource, I didn't run the aluminum through conduit when I burried it so there is the worry of gophers chewing through the insulation and grounding out the copper which would turn into an open and more problems. But, so far so good.....Oh. also about ten years ago, I scored the 3000 pound gel cell bank of batteries. They are great, no upkeep. Just keep em charged. No worry about freezing in the winter, no worry about fluid level etc.

__________________
'Consider it all entertainment'
Register to Reply Good Answer (Score 4)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#14

Re: 12 VDC Home System

12/23/2009 1:17 PM

You did a really good job 40 years ago, but you are right, some fusing is called for......

You have enough sources from all the posts and the ideas for using 12 volt LED lighting is also excellent.

May I also suggest that you put a cheap LED with a 1K resitor across each fuse, when it blows the LED will glow.....makes finding the blown fuse a doddle, day or night!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#18
In reply to #14

Re: 12 VDC Home System

12/24/2009 12:39 PM

"May I also suggest that you put a cheap LED with a 1K resitor across each fuse, when it blows the LED will glow.....makes finding the blown fuse a doddle, day or night!!!"

That is a GREAT idea! While probably useful to 4123 (thus deserving the GA), I am pretty sure I will incorporate (at least some version of) this into several of my future projects. Thanks!

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#19
In reply to #18

Re: 12 VDC Home System

12/24/2009 2:39 PM

I have actually seen, some years ago, resettable car fuses with a LED across them....

The biggest problem with the LED is that even though the fuse is broken, whatever it supplies must be effectively switched on to light the LED....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#20
In reply to #19

Re: 12 VDC Home System

12/26/2009 7:49 PM

Most of the equipment manufacturers make a pre-wired version of a fuseholder with an LED tell-tale built in.

Personally iI would always use a breaker. No temptation to put the wrong size fuse in when you get a trip!

One place where there should be a fuse is the main fuse which should be as close as possible to the battery terminals.

3,000 lbs of battery is between 3,00Ah and 4,000Ah (Dependant on battery type) with a short circuit capability upwards of 70,000A!

You are extremely lucky that you have had no faults in forty years.

Regards

Chas

__________________
En la casa del herrero, cuchillos de palo!
Register to Reply
2
Power-User
Hobbies - Hunting - Deer and Birds Hobbies - HAM Radio - Achieved Ham Radio license in 2008 Hobbies - Fishing - Fisherman United States - US - Statue of Liberty - Know freedom, no tyranny.  Know tyranny, no freedom. Hobbies - DIY Welding - Beginner

Join Date: Sep 2009
Location: Pacific Northwest USA
Posts: 223
Good Answers: 19
#15

Re: 12 VDC Home System

12/23/2009 2:32 PM

Like Andy said you have plenty of great ideas and sources to consider from posts above. I just wanted to let you know I actually use an automotive fuse block panel in my DC system at my home. My batteries (charged by solar panels) provide DC to my inverter for 5000w AC but I also have a number of DC items (Ham radio, a few lights, some DC chargers for other items, etc.) and so I ran a + and a - off the feeds coming from the battery bank straight to an auto fuse block panel then to the items. Works great, been in use for about 10 years. I've blown a few fuses, and since they are all visible in one spot it was easy to find and replace. If you fuse lines in place, Andy's LED with res idea is excellent. FYI, the 9w CFL put out great lighting!

Matt

__________________
Go green, use a solar powered light saber...
Register to Reply Good Answer (Score 2)
Anonymous Poster
#21

Re: 12 VDC Home System

01/06/2010 4:40 PM

The battery you describe can create a huge arc for a long time. You must install overcurrent protection. Many circuit breakers are rated for ac and dc. The DC rating is less because it is harder to extinguish a DC arc (it never crosses the zero point like AC). #14 should be fused at 15 amps. Never use automotive fuses. You must use UL listed components to be legal. I would fuse the positive lead from the battery and then set a small panel with 15 amp fuses to connect to each romex. The home and life you save may be your own.

Register to Reply Score 1 for Good Answer
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: