VFD Faults

01/05/2010 6:04 PM

I am hoping someone could help me with the following issue.

I have been working on a project using a VFD, and we notice that there is a fault each time.

The VFD is used to power a conveyor. The power source is set to 3 phase 480 V 60Hz 6.5 Ampers (1.5A to 9A) which leads to the VFD which is set at 60 Hz 6.5 Ampers (Model: Eaton MVX9000), which leads to the motor which is set to 68Hz and requires 1.5 Ampers.

The VFD keeps faulting out. When we bypass the VFD everything works fine.

Any suggestions?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: VFD Faults

01/05/2010 7:48 PM

Does the VFD indicate what it is "faulting out" on? Over load? Over voltage? Under voltage? Stall? You have to give us something to work with here.

Generally, things like this tend to be commissioning errors, i.e. you have programmed something incorrectly or failed to program something necessary for the application.Do you know what you are doing with VFD programming or did someone just throw this on there and expect it to work?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#2

Re: VFD Faults

01/05/2010 9:38 PM

What is the fault error. It should say on the VFD, or a sequence of blinking lights that states in the manual.

And when does it fault?....start-up (ramp-up), after its been running, you need to give us something more.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Active Contributor

Join Date: Apr 2009
Posts: 12
#3

Re: VFD Faults

01/06/2010 2:24 PM

Sorry for the limited information. I was able to further discuss the issue with the Electrician, and I will be able to test on the weekend. In my initial post I mentioned that a power source was connected, however, it happens to be an ELR (Phoenix motor starter). The ELR faults out after 5 seconds of the system running. After the ELR is reset 5 to 6 times, then it will work for 4 to 5 hours and then the fault happens again. The VFD shuts down because the ELR does not supply anymore power. Keep in mind, when the VFD is by passed the system works fine. There is not error codes on the ELR.

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#5
In reply to #3

Re: VFD Faults

01/07/2010 12:31 AM

It is somewhat unusual to use a motor starter ahead of VFD. What features does it provide?

It is more common to use a 3 phase contactor.

Not knowing the specs of your "ELR" starter it may be it cannot handle the harmonics that the drive presents to it.

Input reactors are often used ahead of VFD's to help mitigate some of the harmonic issues.

Give us a single line of your system from the main transformer through to the motor with part numbers (or links to the parts) and we may have more than opinions to offer.

Register to Reply
Anonymous Poster
#4

Re: VFD Faults

01/06/2010 11:59 PM

VFD =3 phase 480 V 60Hz

Motor=68Hz

To me it seems that the VFD will fall out because the frequency of the VFD and the frequency of the motor are not the same. The motor frequency should be set at 60Hz.

Register to Reply
Associate
Jordan - Member - New Member

Join Date: Nov 2008
Posts: 27
Good Answers: 1
#7
In reply to #4

Re: VFD Faults

01/07/2010 2:52 AM

No sir,

VFD means Voltage/Frequency Drive, and it's also called Frequency Inverter, in the VFD you control the speed of the motor by the variable freuency and usually it ranges from 0Hz to 200Hz depending on the application and the motor windings, so that is not the problem here.

for Taki , u still didn't give us the fault code that u have either on the VFD or on the motor starter,and i agree with the people who say u don't need this starter as it can cause conflict.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: VFD Faults

01/07/2010 2:47 AM

No idea what "ELR" stands for.

AcronymDefinition
ELREnvironmental Law Reporter
ELREverybody Loves Raymond (TV series)
ELREmergency Locking Retractor (seat belts)
ELREast Lancashire Railway (UK)
ELREuropean Load Response (test cycle; ECE-R24 EU regulation)
ELRElectronic Lab Reporting
ELRElectronic Learning Resources
ELRExtended Long Reach (Cisco)
ELREnvironmental Lapse Rate (meteorology)
ELREddie Lawson Replica (Kawasaki motorcycle model)
ELRExtraLife Radio
ELRElectronic Loan Review (Affinity Corporation)
ELRExtra Language Resources (Interactive speech pathology resources)
ELREndangered Language Repository (yourDictionary.com)
ELREmployment of Last Resort
ELREngineers Line Reference (UK railways)
ELREmployment and Labour Relations (Canada)
ELRExtra Long Reach
ELREsther Lavonne & the Rottens (band)
ELRextra-long-range aircraft (US DoD)
ELRElevated Leg Rests (wheelchair)
ELREngineering Liaison Request
ELRElement Level Review
ELRElectronic Line Replacement (cinematography)
ELREvent Likelihood Ratio
ELRExtended Live Range

I can guess maybe it's some sort of Electronic or Solid State Overload Relay? If so most, if not all, are unsuitable for use with VFDs, whether on the input or the output. The reason is, they typically cannot properly deal with the harmonics created by the VFD and the RMS current readings are thrown off. All modern VFDs now provide motor overload protection themselves, so if you have one ahead of it, it is redundant and unnecessary. Remove it and let the VFD do the motor protection.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Apr 2009
Posts: 12
#8

Re: VFD Faults

01/07/2010 11:30 AM

Please see the link below for the ELR Motor Starter.

http://eshop.phoenixcontact.no/phoenix/treeViewClick.do;jsessionid=LGLVrQmWMMwtBBz0hYGGqJllVnwC21PBZZYjSwVMzLM2wVNxGTdP!-144951299?UID=2297060&parentUID=852411055&reloadFrame=true

Your help is appreciated with such limited information. I will get the error code on the ELR at the latest tomorrow when I am able to test.

Thanks,

Register to Reply
Active Contributor

Join Date: Apr 2009
Posts: 12
#9

Re: VFD Faults

01/07/2010 12:20 PM

I have the ELR fault codes and they are as follows: Symmetry - The two motor currents deviate by more than 20 %. OR Phase failure - One of the two measured motor currents is zero or the phase shift between the two motor currents does not equal 120°, but 180° I hope this helps, and thanks again

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#10
In reply to #9

Re: VFD Faults

01/07/2010 12:31 PM

Don't use the ELR ahead of the VFD.

If you want backup then use a simple contactor for the VFD, then if the VFD is out of commission use the ELR.

The drive will look after itself and the motor if set up properly.

Normally a VFD should not be started and stopped via the three phase power.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#14
In reply to #9

Re: VFD Faults

01/11/2010 10:51 PM

Taki R,

I agree fully with the recommendations by the others. I suspect that if you were to discuss this with Phoenix Contact, they would also concur that their ELR cannot be used on the input (or the output) of a VFD. Because the VFD begins with a diode bridge to convert the incoming AC to DC, its load on the AC input line is not linear. That means that its input current waveform is not in a direct relationship to the input voltage waveform. Until the input voltage of the sine wave exceeds the DC bus voltage, negligible current is drawn. Then it turns off again when the input voltage on the sine wave drops below the DC bus voltage. Therefore, the current waveform appears more like a series of square wave pulses, with the spacing between them increasing and the pulse widths decreasing when the VFD load is lowered. If there is no filtering on the supply side of the VFD (such as with line reactors), this pulsed waveform imposes on the supply a large amount of harmonic noise, with the total harmonic distortion easily exceeding 500%. The monitoring electronics on the ELR are not programmed or designed to see this as noise; they see it as a faulted load.

I am not at all surprised that the ELR is thinking there is some sort of fault on the load. There is---a design application fault. The applied load is not what the ELR was designed to feed. Early failure of the ELR is very likely; The VFD will probably survive.

Get rid of the ELR---every function it provides can be provided directly by the VFD. If your application must have a line side contactor, provide a magnetic one not an electronic one.

Your question to this discussion board is a good one to ask. I (and the rest, I am sure), greatly appreciate your fast responses to our requests for more information. Thanks--John M.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: VFD Faults

01/07/2010 1:42 PM

I agree. REMOVE that ELR immediately! Using a solid state contactor like that in front of a VFD is setting up a race to see which one fails fastest, the consequences of which can be a loss of the VFD input rectifier. There is NO NEED for that device in the circuit anyway. The VFD will provide superior motor protection and is fully capable of reversing the motor on it's own. In fact, if you reverse the input phasing to the VFD it will have no effect on the motor direction anyway, the VFD is simply rectifying the incoming power. Relative phase rotation of the supply is completely irrelevant.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#12
In reply to #11

Re: VFD Faults

01/07/2010 6:30 PM

We should give ourselves GA's!

Register to Reply Off Topic (Score 5)
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#13
In reply to #12

Re: VFD Faults

01/07/2010 9:33 PM

These posts sound like there on the shop floor

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15

Re: VFD Faults

04/28/2023 4:18 AM

One of the possibilities is a loose or open link inside the motor terminal box (got the T-shirt - it's now on a well-known internet auction site) . If one of the links goes open circuit than the phase currents will go out of balance, and under those circumstances it would be quite in order for the <...VFD...> to say "Sorry - I'm not playing".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Register to Reply 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

amerlathqani (1); Anonymous Poster (1); GW (3); jmueller (1); JRaef (3); phoenix911 (2); PWSlack (1); Taki R (3)

Previous in Forum: ONAN/ONAF/OFAF and short circuit currents   Next in Forum: Conversion for Stamford 300kW 480V to 120 / 208v
You might be interested in: Conveyor Controls and Monitors, Conveyor Rollers

Advertisement