GRP Tank Coating Suitable for Sodium Hypochlorite 12%

01/13/2010 8:52 AM

We have GRP tank for Sodium Hypochlorite (12%) which is dosed into potable water for disinfection purpose. We are faced with the problem that the fibres of the GRP tank internal surface are coming out and cloging the filters / lines and disturbs the dosing rate.

Can you suggest the resin and the internal tank coating that would be suitable for sodium hypochlorite application.

Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: GRP Tank Coat Suitable for Sodium Hypochlorite 12%

01/13/2010 11:27 AM

http://www.coleparmer.com/techinfo/ChemComp.asp

Polypropylene tanks are in widespread use.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Commentator

Join Date: Oct 2008
Location: Gaborone, Botswana
Posts: 89
Good Answers: 22
#2

Re: GRP Tank Coating Suitable for Sodium Hypochlorite 12%

01/14/2010 12:02 AM

If you have a GRP tank with exposed fibres on the internal (product side) surface you almost certainly have a major problem with structural integrity of the tank and should drain it and take it out of service immediately until it can be inspected and assessed by an expert. GRP tanks rely on a corrosion barrier of pure resin and usually a corrosion resistant veil to isolate the structural GRP from the stored chemical. Exposed and separating fibres mean that the structural layers of the tank are being degraded and could result in catastrophic rupture of the tank wall. If you want to replace the tank there are grades of resin (eg Derakanes) which are resistant but the tank must be manufactured, installed and inspected according to an appropriate standard eg BS4994.

__________________
johnbots
Register to Reply Good Answer (Score 2)
Associate

Join Date: Jul 2008
Location: Norfolk, VA
Posts: 50
Good Answers: 4
#3
In reply to #2

Re: GRP Tank Coating Suitable for Sodium Hypochlorite 12%

01/14/2010 7:40 AM

I second that - the glass provides the strength and stiffness to keep your tank standing, and although these tanks are generally (if done correctly) built with high factors of safety, you should have this assessed as quickly as possible. You may be able to repair the tank, but this is a fringe application for GRP at best. Hypochlorite, particularly if it's not well controlled (e.g. there is "free" chlorine), attacks glass, so it's in some senses ironic that people store it in GRP at all, but there are ways to do it and do it right. "Doing it right" in this application means a thicker corrosion barrier, a lower glass to resin percentage than normal, no polyester resin in the structural layers (a practice people use to make tanks cheaper sometimes), wrapping a corrosion barrier onto the end of fittings before joining them to the tank wall, etc. If you do repair, the veil material (the interior surface) should be a polymer (e.g. Nexus), not "C" glass. Achieving full cure on the repair is absolutely critical in this service, so be sure to verify - typically this will be an acetone sensitivity test coupled with a Barcol impressor. If you get a consultant involved, you should be listening for them to talk in these terms. If they don't, you might not have the right consultant.

I hope this helps.

Register to Reply
Commentator

Join Date: Oct 2008
Location: Gaborone, Botswana
Posts: 89
Good Answers: 22
#4

Re: GRP Tank Coating Suitable for Sodium Hypochlorite 12%

01/15/2010 12:04 AM

Having slept on the problem another thought came to mind - to be shedding so many fibres that filters and lines are getting blocked implies a very serious breakdown of the GRP. Have you had repairs or modifications done to the tank recently? was the tank cleaned thoroughly after repair? could scraps of glass matting or grinding dust have been left in the tank and is it this which is coming through with the hypochlorite? If not I would emphasise my earlier comments and those by jgjengr to have the tank assessed urgently.

__________________
johnbots
Register to Reply
Anonymous Poster
#6
In reply to #4

Re: GRP Tank Coating Suitable for Sodium Hypochlorite 12%

01/15/2010 11:56 PM

Yes, we had done repairs six months ago and the tank was cleaned prior to put in service. The current blockage is from the new fibres coming out of the tank wall. We have now opened the tank and found that the wall fibres are coming out. We are grinding it and thereafter will put recommended regin (DERAKANE). After two coats of resin our EPC contractor has proposed to apply 2 coats of Isophthalic based Gelcoat SIROGEL 9100. Any comments on this gelcoat material?

Thanks you all.

Register to Reply
Associate

Join Date: Jul 2008
Location: Norfolk, VA
Posts: 50
Good Answers: 4
#7
In reply to #6

Re: GRP Tank Coating Suitable for Sodium Hypochlorite 12%

01/18/2010 8:41 AM

I don't have any experience with this material or with any unreinforced (no veil material, or flake material, or ...) coatings on GRP interior surfaces other than paraffinated top coats (which are used to ensure full cure) - I hope you get good adhesion and that it doesn't crack as the tank flexes - those would be my two worries.

Register to Reply
Active Contributor

Join Date: Apr 2007
Location: Canada
Posts: 19
#5

Re: GRP Tank Coating Suitable for Sodium Hypochlorite 12%

01/15/2010 10:51 AM

The fibres coming out are most likely from your corrosion liner. Structure might not be affected yet but it's a question of time.

A double Nexus, BPO curing system and DERAKANE 411 as resin will be suitable for your application up to 80C.

Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Balki (1); jgjengr (2); johnbots (2); PWSlack (1)