Anonymous Poster

high earth to neutral voltage

01/14/2010 7:17 AM

what are the effects of high earth to neutral voltage

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: high earth to neutral voltage

01/14/2010 7:26 AM

I'll go along with PW

__________________
health warning: These posts may contain traces of nut.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: high earth to neutral voltage

01/14/2010 7:26 AM

There shouldn't be any. Neutral is a conductor carrying the return current, or the vector sum of all the phase currents in a multi-phase system, and Earth is a protective conductor that doesn't generally carry any current except briefly as is required under fault conditions in order to operate the circuit protective device.

Please define "high".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: high earth to neutral voltage

01/14/2010 8:14 AM

High neutral to earth voltage is of concern only in those electronic systems which are communicating amongst themselves. Because, to be economical, the data zero reference is taken from the ground or earth only. If there is appreciable difference in the ground to neutral voltage then there would be communication data errors.

One need not believe that high neutral to earth voltage is dangerous for all computers. It is not true. Because, in India, most of the domestic electrical installtions do not have an earthing system at all. Still, computers have been in operation in these houses for years now.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: high earth to neutral voltage

01/14/2010 9:05 AM

<...If there is appreciable difference in the ground to neutral voltage then there would be communication data errors....>

Even if the communications circuit supply were downstream of a power step-down isolating transformer and incoming supply neutral wasn't linked to the 0V rail downstream of the transformer [learing experience for PW, please]?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5
In reply to #4

Re: high earth to neutral voltage

01/16/2010 8:20 AM

If you use an isolating transformer with no neutral bond or earth bonds between the two systems, then there will not be any communication errors. But, in such a case, there would not also be a high Neutral-Earth Voltage. Most of the neutral to earth voltages are encountered in power system grounds only. They may not be experienced in communication systems.

Reply