HT Cable Sizing

01/21/2010 11:37 PM

In LT cable sizing calculation we are not considering short circuit current .but in HT cable sizing it is considered why?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: ht cable sizing

01/22/2010 12:55 AM

Huh?

I have in the past done LT calculations involving transformer and cable impedance (size versus length) to determine maximum fault current.

I doubt that any cable would ever be sized to handle such large currents; instead, what you are sizing are fuses or circuit breakers and their required interrupting capacity.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#2

Re: ht cable sizing

01/22/2010 3:03 AM

Hi Friends,

In LV or MV, we are considering short circuit current. About 40 years ago, when I just joined electrical field, my supervisor told me that the first 10 meters of LV cables from MCCB are not protected against short circuit because of economical reason.

If you consider the short circuit currents, your cables would be quite large.

However, technology changed, most of MCCBs or MCBs now are current limiting, and possible to protect the connected LV cables against short circuit.

So you must make sure your LV cable is protected by your current limiting MCCB.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Commentator

Join Date: Sep 2009
Location: INDIA
Posts: 92
#4
In reply to #2

Re: ht cable sizing

01/22/2010 4:58 AM

yes i agree it is for both LT and HT cable sizing but in HT it is mandatory.Why is so in HT ?

Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#5
In reply to #4

Re: ht cable sizing

01/24/2010 7:56 PM

Dear all,

BS7671 (IEE), 430.3 states "A protective device shall be provided to break any overcurrent in the circuit conductors before such a current could cause a danger due to thermal or........, NOTE: An overcurrent may be an overload current or a fault current."

IEE is for LV installation, and circuit conductors must be protected against a short circuit current. This is mandatory in LV.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: ht cable sizing

01/22/2010 3:18 AM

It needs to be considered in both cases. Why "we" are "not" doing it is the imponderable.

British Standard 7671 again?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply