Harmonics

01/23/2010 1:23 PM

Thanks for looking

I have a customer,with a problem involving a welder and his office pc's.When he uses his tig welder,his pc's have fits,he has small ups/surge protection on each pc.His building service is a closed delta 240 system.He has made attempts in the past at a solution but as not been successful,a electrical contractor,talked him into running a 225 amp sub panel that only feed his welder did nothing to solve problem,which is a 250 amp dc/ac/tig machine,brand new miller,he has had it checked by manufacturer and they say all is fine.

Looking for a relatively in expensive solution ,I am thinking that a filter feeding the pc's.

Has anyone found/used a product that would help?There is all kinds of harmonic filters on the market for ac/dc drives but all run in the 1000's any suggestions would be helpful.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#1

Re: Harmonics

01/23/2010 2:56 PM

Does he have the required earth ground on the welder like whats shown in the owners manual?

If so is the earth ground actually connected to the earth where it supposed to be and in the correct way?

To me it is either radiating some level of electrical line noise back through the power lines or its more likely that the welder is dumping its normal electrical noise onto the buildings earth ground system (where its supposed to) which may not be actually connected to the earth itself or is poorly connected at best.

That tends to give the effect of having the whole buildings earth grounding system working like a direct connection to and from everything for all electrical noises in general.

UPS units clean up the line power but not the ground lines themselves. Any higher level ground line noise goes right past them.

I worked as a welder and plasma cutter repair tech (still do some) and I have seen that when ever machines cause interference with other devices or have glitches them selves its almost always because the earth grounding leads or the lines that take that lead to the actual earth are removed, broken or have never been connected.

I saw many machines that had 4 wire power cords wired with three prong welder plugs with the ground line not connected to anything. Simply connecting the ground cures loads of odd problems with electrical noise issues.

Register to Reply Good Answer (Score 3)
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#3
In reply to #1

Re: Harmonics

01/23/2010 3:16 PM

I am in full agreement with tcmtech.

From my experience too many get by on and take for granted electrical feeds that will work somewhat independent of proper grounding as long as the neutral will carry the backfeed, but always there are problems if there is not a good solid ground, especially when major amp draws are involved.

__________________
You don't get wise because you got old, you get old because you were wise.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#8
In reply to #1

Re: Harmonics

01/23/2010 4:34 PM

Good point tcmtech. You also get a GA from me.

Keep in mind that all ground currents should be undesired or fault currents.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Harmonics

01/23/2010 3:13 PM

There is no simple magic wand that can be waved to solve an interference problem like this. I would start by identifying the interference path by running the welder with all of your computers running on the batteries of their UPS. If this still causes interference then no amount of power filtering will help. You might find that your internal wireless communication network cannot cope with the RFI produced by this TIG welder. But clearly the least expensive method will be to identify how the interference propagates (broadcast, communication cables, power cables) before buying hardware. Once you find this out, you will have to decide on a course of action. Making the PC's tolerant to TIG welder noise maybe the lowest cost per application but will have to be reevaluated with every new piece of office equipment. Preventing the TIG welder from polluting the air waves or power grid will require more expensive equipment, but need be done only once.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Jul 2008
Posts: 1688
Good Answers: 145
#4

Re: Harmonics

01/23/2010 3:36 PM

I don't know what "PCs have fits" means, but most UPS systems are "off line" and won't go "on line" unless they detect a loss of 60/50 Hz for a certain number of ms. Then, they go "off line" again very fast if the AC is restored. This will work well for "normal" loss of power, but might not do anything for you with very dirty power. As a last resort, a "true on line" UPS that is actively producing the AC output 24/7 would give you clean power.

Note that this is the "last resort". Checking grounds AND NEUTRALS first is a much better way to go. If poor grounding of the welder allows the welder to screw up neutral then you might be equipped with the right idea but still barking up the wrong tree.

It might be helpful if you add a few details about what "PCs have fits" means (reset, data/program corruption, power down, run with bad video, etc.)

__________________
Few things limit our potential as much as knowing answers and setting aside questions.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5

Re: Harmonics

01/23/2010 3:46 PM

A couples of questions...

1) How is 120 volts Ac provided for the PCs? You said it was closed delta, as such, there is no 120 volt available. Is there step down transformers?

2) Is this a corner grounded delta system,? If not, that is more then likely your problem.

I did my apprenticeship in a very large printing plant fed from a 240 volt closed delta 3 phase system that was not grounded. When we installed new laser graphic scanners (this was in the 70s - the scanners were HUGE), we had all sorts of problems with ground loops.

We solved the problem by installing a grounding resistor between "ground" and one of the phases. This gave us a "corner grounded delta system" and the resister limited available fault current to a manageable level.

We then tied all of the "grounds" together, including the neutrals of our step down transformers for lighting and hotel loads and the problems went away.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Associate

Join Date: Mar 2008
Location: north east
Posts: 29
#6
In reply to #5

Re: Harmonics

01/23/2010 4:06 PM

Thanks for all the input,It is a corner grounded system,no xformers,Welder install was done buy an electrical contractor,but also same guy that told owner,installing a sub panel just for welder would cure problem.As the Pc having fits,the small ups go to battery and monitors show distortion,don't know if data is lost,will look at grounding system closer,at this point making and assumption that licenced contractor knows what he was doing as far a grounding,but we all know about that. Have s[spoken to some other people and they suggest,changing service to a 120/208 system.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7
In reply to #6

Re: Harmonics

01/23/2010 4:26 PM

I would not argue with the statement that changing to a 120Y/208 system would not help the situation. Having said that... I would question if such a change is needed at this point, as not enough data has been presented yet.

You still have not told me how the 120 volts is derived for the PCs. There has to be transformers if it is infact a 240 volt delta system as there is no way to get 120 volts other then to center tap one of the three phases. Which does not go with a "corner grounded" system.

More investigation work is called for...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#9

Re: Harmonics

01/23/2010 5:54 PM

All of Millers welders have considerable line noise filtering built in. But all of that filtering is very dependant on the primary earth ground circuits being adequate. In some applications adequate literally means an solid earth grounded point within so may feet of the machine with a large enough size of wire from the machine to the ground rods and the correct size and number of ground rods for the local soil conditions.

Without the correct ground circuit those machines basically become high powered RF hash/noise transmitters!

As far as what the contractor says, To be honest I have met more electrical contractors that have never opened an electrical code book or electrical physics book since the day they got their licence than those who have by a very wide margin!

Having a contractors license is very similar to most people having a drivers licence. They passed the test 20 years ago and have kept the renewals current but that doesn't mean they have read the rules and regulations books since the day they got it! If anything most couldn't come close to even passing the test again if they where given it on the spot!

Register to Reply Score 1 for Good Answer
Anonymous Poster
#10

Re: Harmonics

01/23/2010 8:39 PM

to tcmtech

SLAP!!!!

from an electrician with a license that closes the books long enough to eat, sleep, and work

Register to Reply Score 2 for Off Topic
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#11
In reply to #10

Re: Harmonics

01/23/2010 9:26 PM

Hehehe! Some one is offended by my comments and had to post as a guest!

A good licenced electrician would have never thought twice about my comments being that they would have considered it was their competition I was referring to and not them!

As I referred to MOST. If your offended that likely puts you on the wrong side of the MOST list.

Since your so sensitive here is a joke for you.

How many licenced electricians does it take to change a light bulb?

9 plus one inspector, $17002.98, and four months time do it.

It takes a month for the first electrician to show up and give you an estimate. Then it takes 8 more electricians two months to put in a new service from the utility pole, through the whole house up to the light socket for the cost of $17000.

Then one month more before the inspector comes by and signs off on their work.

He then hands you a new bulb and tells you that you have to do it yourself because of a liability clause in the work contract that stipulates that a light bulb is not the contractors responsibility due to hazardous material handling regulations ($2.98 CFL bulb of course) but is the end user/home owners responsibility.

(Oh, and you still have to wiggle the light switch 'just right' before it will come on just like it always did before anyway.)

If you have ever had any electrical work done by a licenced contractor you know full well what I am referring too!

Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#15
In reply to #11

Re: Harmonics

01/24/2010 1:29 AM

I appreciate tcmtech patience in posting. I too was a licenced electrician now working as a senior manager. I have faced inspectors who gave licences to people who bribed them but not to those who really deserved; that was too bad. I think tcmtech did not offend any one; what he said is some realities.

__________________
Subramanyam
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#19
In reply to #15

Re: Harmonics

01/24/2010 2:03 PM

Thanks. And thanks to everybody else as well it is appreciated!

In my working career I have met many very good knowledgeable and honest contractors in many fields that if needed I would recommend to anyone.

Unfortunately I have met more unskilled, unqualified, and dangerously corrupt and crooked ones in the same time line plus a few bad inspectors included as well. I have seen licenced contractors steal customer property, and other contractors property, bribe incompetent inspectors to pass horribly wrong and dangerous work, and far worse. I have even been asked and expected by a former employer to play along because it was good for everyones business. And no I didn't play along. All the while the customer was getting shafted from front and back by everyone.

To me this thread likely points out the OP has a questionable contractor (likely incompetent and or greedy too) on his hands.

In my line of work experience the service system is the last thing that gets upgraded when odd electrical problems occur with office equipment, not the first. I would have started with taking a basic look at the welders grounding system and the buildings grounding systems first.

After that I would have likely put in an isolation transformer or line filtering system for the office supply lines. A 1 - 2 KVA isolation transformer, or a number of smaller individual ones for each computer, is far cheaper than a 20 - 30 KVA transformer for a welder system. Plus small ones could be set up as a simple plug in and go devices as well. No service line work would have been needed.

If the problem went away the noise is in the lines and can be cured at the welder with a some off the shelf commercial line filters installed in the welder AND in the service panel systems. If it didn't the noise is in the grounding system which any competent electrician should always suspect first and never last!

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#17
In reply to #11

Re: Harmonics

01/24/2010 5:00 AM

LOL!

I like your style.....

The "low life" will probably not come back.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#16
In reply to #10

Re: Harmonics

01/24/2010 4:58 AM

Who is also not man enough to post with his CR4 name.....!!!!

Your comment was simply rude, probably inaccurate as well, so it brought nothing to the problem fix......eg. Totally useless!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#28
In reply to #16

Re: Harmonics

01/25/2010 10:14 AM

My thoughts exactly. Like really now, who could ever link Brave Sir Robin to my real identity? So funny.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#12

Re: Harmonics

01/23/2010 9:43 PM

Dear dg1258,

This is off topic, but long as I've been around on CR4 the avatar picture you have up is one long I have associated with Bob C.

When I first joined up I picked mine out of the choices, partly as an irony, and partly due to feedback I got about what I was in the course of a leadership workshop.

At one point I put up a picture of myself in place of the avatar picture I have used now for years, and I tried another odd picture from my files, but well, it was too late, I didn't like looking at myself here.

Then I became afraid that someone else might take the image I had so long used, and I took it back, and have kept it since.

Don't know what I would do actually if someone new, or old decided to use the avatar pic I've used on this forum for the past few years.

Guess I'd go take a picture of a bomb going off, or a fire, or try and get one of an asteroid or big meteor burning up of my own to use.

__________________
You don't get wise because you got old, you get old because you were wise.
Register to Reply Off Topic (Score 5)
Anonymous Poster
#13

Re: Harmonics

01/23/2010 10:20 PM

wouldn't the noise come from the large currents in the welding cable like a spark gap transmitter?

Register to Reply
Anonymous Poster
#14

Re: Harmonics

01/24/2010 12:59 AM

Is the welder 3 phase or single phase?

Single phase supplied from a closed delta will unbalance the delta. If the system is a grounded B-phase more problems will orrur. Grounded B-phase is no longer allow per NEC.

Check the wire sizes to small of wire will create problems to.

Register to Reply
Anonymous Poster
#18

Re: Harmonics

01/24/2010 10:48 AM

From: Tim Hawley Master Mech.

All of you gave great feed back to dg1258

I would recommend as well, a ground rod drill through the cement floor, drove down minimum of 4 foot into earth and connected to ground bar in service panel.

Also look for floating grounds on AC connections on cold water pipes etc...

If this doesn't solve the problem, use an isolation transformer to feed the AC to the welder.

Problem solved.

Best Regards,

Tim

Register to Reply
Power-User
Hobbies - Target Shooting - New Member Hobbies - Model Rocketry - New Member Safety - ESD - New Member

Join Date: Jan 2008
Location: here
Posts: 109
Good Answers: 5
#20

Re: Harmonics

01/24/2010 5:35 PM

I DUN kNo but I thunk they chould change the smoke in the wires feeding the computors. That what we do when we need extra money.

Really, I think the first answer is probably the best. Start with the grounding of any system and you can usually solve a lot of problems. Remember, by code you are only allowed one reference to ground, and it has been more than a month since I opened a book (do comics count) but I think the reference is 25 ohms to ground. But dont quote me on that. Just like reading the post.

CA licensed union electrician, who teaches and gets an average of 4 to 10 CE a year.

Have are great day and stay healthy

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#21
In reply to #20

Re: Harmonics

01/24/2010 7:42 PM

by code you are only allowed one reference to ground,

Actually the NEC code book has Article 250 which is related directly to grounding issues. Just in my pocket reference book it has 148 sub articles taking up 33 pages and representing nearly 10% of the article texts in the pocket reference book. Plus many of the sub articles under the primary article 250 have multiple sub breakdowns within themselves.

Multi point earth grounding is highly encouraged and in most instances required in regards to many types of power systems and sub feed systems. No single earth ground point should be used unless absolutely no other means is possible. Rather multiple points (earthing grid) are recommended and now often required for any distributed electrical service or services.

Industrial and commercial multiphase has requirements for multiple earth grounding points. Also independent earth grounding methods specific to specialized electrical devices are also encouraged.

The actual reference to 25 ohms (Article 250.56) is in regards to any single earth grounding point and is the maximum resistance that any one earth ground point can have.

CA licensed union electrician, who teaches and gets an average of 4 to 10 CE a year.

No offence but I hope that doesn't mean you are putting 4 to 10 more unqualified and improperly educated and licenced and certified electricians into the work force every year.

Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#23
In reply to #21

Re: Harmonics

01/25/2010 3:27 AM

I didn't feel you were being quite fair, nor accurate in what you wrote.

I am placing here what I understand for earthing, correct me if I am wrong please.

Correct earthing, each unit (motor, PC or welder for example) is connected to the earth busbar once.

But if an earth path developes as in the red wire shown in this diagram, some nasty things can happen as in here:-

There are other possibilities that can cause loops, I have just picked a simple version....

Tell us what you think please.

PS I liked also the idea of rolling the cable completely out, especially if on a metal drum. My wife nearly burnt our house down many years ago when she used a rolled up cable for the wash dryer!!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#24
In reply to #23

Re: Harmonics

01/25/2010 9:32 AM

If your getting a voltage differential on the earth grounding circuit between your two devices you have something wrong in one or more of the devices.

Multiple earth grounds are just that. There are more than one point of physical contact between the devices grounding wire that goes to your buss bar and the actual physical earth/ Tera firma/ the big thing we live on.

Basically the short answer would be that every device in your drawing can have a earth grounding rod next to it that ties it directly to the physical earth itself in addition to the ground line going to the buss bar you have shown. This is fairly common procedure in correctly designed electrical systems as I have seen it.

I cant be more specific to any or all instances or applications without actually printing the whole NEC code books article 250 section which is pages and pages long.

Its situations like this that are why stuff gets screwed up in real life implementation of designs. Someone takes an incomplete, inacurate, or condensed version of just part of the rules as given by someone else instead of consulting the rule book like they should have and then builds their system on incomplete misunderstandings of information.

If you need to know the details get a copy of the 2008 NEC code book and read it. Or wait until the next one gets printed in 2011. It gets updated every 3 years.

Sorry but thats the only real and correct answer I can give.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#25
In reply to #24

Re: Harmonics

01/25/2010 9:41 AM

Bravo. Precisely the point of this and many other comments here at CR4, follow your local code. Not the code of another location, nor somebody's vague recollection of what a code states. Buy the code book itself for your area, maybe even take a class on how to translate the code into English (very helpful class IMHO).

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#26
In reply to #21

Re: Harmonics

01/25/2010 10:06 AM

You said...

"No offence but I hope that doesn't mean you are putting 4 to 10 more unqualified and improperly educated and licenced and certified electricians into the work force every year.".

IMHO... that was not called for and was rather arrogant. But... that is just my opinion.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Aug 2011
Posts: 76
#36
In reply to #21

Re: Harmonics

08/24/2011 2:18 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Off Topic (Score 5)
Power-User
Hobbies - CNC - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Apr 2007
Posts: 163
Good Answers: 6
#22

Re: Harmonics

01/25/2010 2:23 AM

I have had this occur before and accidentally solved the problem by laying the stinger cable out as straight as possible on the floor. The cable had been rolled up on the hook on the cart. Maybe it acts as a big antenna when coiled up?????

Beware the misplaced decimal point.......

Register to Reply
Participant

Join Date: Jan 2010
Posts: 2
#27

Re: Harmonics

01/25/2010 10:11 AM

dq1258,

I'm afraid there will not be a cheap solution to this. I can't see how you will avoid installing an harmonic filter.

The welding equipment will continue distorting the supply voltage to the building and creating harmonics. This will be 'seen' by everything else in the building and possibly by some of their 'electrical' neighbours. The contractor should be ashamed of himself. A separate sub-panel was never going to be the solution.

Rob

Register to Reply
Anonymous Poster
#29

Re: Harmonics

01/25/2010 11:23 PM

Driving Ground rods next to each device can work, but this solution can create problems. High ground resistance can create ground loops between the devices.

The ground rod should only be used at the power supply source for the building.

Register to Reply
Active Contributor

Join Date: Jan 2010
Posts: 10
#30

Re: Harmonics

01/28/2010 11:10 PM

Hi - I am Highly experimented on this kind of problem 38 years experience - I am consultant for power quality system - with adequate test ,i may help

Forward your test to me .

I will help or quote depend on the time i need for examinate problem! Joshua Gabriel SAADA

B.R. Alternative Power Systems
http://www.aps-microgen.com
http://www.calnetixps.com/
www.CalnetixPS.com
Joshua@aps-microgen.com
saadaj@netvision.net.il
Alternativepowersystems@gmail.com
Tel: 972(0) 88652424
972(0) 774100494
Cell: 972(0) 546566191
Tel/fax on demand: 972(0) 88652424
Electrical Test Engineer: License Nr: 085195
Senior Electrical license Nr: 007922

Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#31
In reply to #30

Re: Harmonics

01/29/2010 8:54 AM

I'd hate to be your Spam filter.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#32
In reply to #31

Re: Harmonics

01/29/2010 9:56 AM

Its not so bad with a good quality hot mustard!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#33
In reply to #32

Re: Harmonics

01/29/2010 10:15 AM

With bloody Vikings singing in the background.

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Mar 2006
Location: Vallejo, CA USA
Posts: 132
Good Answers: 10
#34

Re: Harmonics

01/30/2010 1:46 PM

Tig welding is a given around nuclear power plants. Whenever any Tig welding was underway, the nuclear instruments would go crazy. Not good. However, the Navy never found a solution and, as far as I know, the instruments still have problems.

Essentially a Tig is a spark transmitter and the spark is not at all constant and it tends to be of a fairly high frequency IIRC.

Given the relatively poor shielding of a standard office PC, I am not surprised they react. There are shielded PC enclosures designed for use on factory floors. Hard to imaging those working well in an office environment, however.

Maybe the office, if it isn't too large, can be placed in a Faraday shield. Probably not practical.

Maybe a faraday shield around the work area?

__________________
It was burning when I put it down!
Register to Reply
Power-User
Hobbies - CNC - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Apr 2007
Posts: 163
Good Answers: 6
#35

Re: Harmonics

02/24/2010 1:55 PM

Just wondering if you solved your problem with the TIG vs computer trouble? What fixed it?

beware the misplaced decimal point.......

Register to Reply
Register to Reply 36 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!