Short Circuit Current

01/28/2010 7:04 AM

Why all marine Specifications calls for 3 Times short circuit current from the alternators?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Short Circuit Current

01/28/2010 7:05 AM

All three phases shorted at once?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#2
In reply to #1

Re: Short Circuit Current

01/28/2010 7:12 AM

Yes, All 3 Phases shorted together.

The specs says' the generator should be capable to deliver the 3 times short circuit current for 3 seconds'

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Short Circuit Current

01/28/2010 7:16 AM

That's why, then. If it couldn't then something is undersized.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re:The specs says' the generator should be capable to deli Short Circuit Current

01/28/2010 11:47 AM

quote "The specs says' the generator should be capable to deliver the 3 times short circuit current for 3 seconds"

3 time what short circuit? What value are you using?

Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#5
In reply to #4

Re:The specs says' the generator should be capable to deli Short Circuit Current

01/29/2010 2:30 AM

the generator rated current is 100 amp, Specs says that it should deliver 3 x 100 amp when all the three phases are short circuited.

Register to Reply
Commentator

Join Date: Dec 2009
Location: Jakarta 12130 Indonesia
Posts: 76
Good Answers: 1
#7
In reply to #5

Re:The specs says' the generator should be capable to deli Short Circuit Current

01/31/2010 6:28 AM

Dear Visham Lele,

Refer to ANSI C50.13-1977 the generator should able to deliver current as below:

Sec 10 30 60 120

I armature (%) 226 154 130 116

If your spec state 3 times full load amperes when all three phases short-circuited.

It may be difficulties for generator manufcaturer to decide subtrasient reactance to generate shart-circuit current 3 times full load amps. Please check again your spec.

As pen ANSI above, The generator should able to be loaded for 226% FLA for 10 seconds. It make sense that 3 times FLA for 3 seconds.

Regards,

__________________
RSM Elect Specialist
Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#8
In reply to #7

Re:The specs says' the generator should be capable to deli Short Circuit Current

01/31/2010 8:12 AM

I have now the recent update from Marine Agnecies.

As per the specs the Generator should be able to deliver the 3 times the Full load current when all 3 phases of the Generator to descriminate the fault.

The Explanation is -

When the Short circuit Fault occures in any equipment connected to the generator, the generator will see the phases short circuited & the terminal voltage of the generator's shorted phases would be ZERO. at this moment the Automatic Voltage regulator will see no voltage at the terminals. If the AVR's power is being fed through the Terminals of the alternator , the AVR will fail to work. Resulting tripping of the Circuit breaker at the generator end.

Now if your Generator has the above capability ( to supply the power to the short circuit) the Short Circuit fault in the equipment will be fed untill the Equipments protective relays tripps. In this case the Fault Descrimination will be easy.

I feel this is what I understood talking to different Marine Agencies.

Please correct me if I am wrong....

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6

Re: Short Circuit Current

01/29/2010 11:42 PM

There is incorrect language being used in the specs, or in someone's repetition or interpretation of them.

It would make sense for a generator to be able to deliver briefly 3 x rated current, such as for starting motors, but it is impossible for it to deliver more than the short-circuit current, because that is all even a short circuit will draw.

The generator will "brown out" before that happens, anyway. Ain't fun to watch....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

PWSlack (2); rasam.syamsudin (1); Tornado (1); vishram lele (3); wareagle (1)