How Tapping in H.V side is used to vary the L.V voltage
Re: Doubt on Tappings
02/05/2010 2:20 AM
Increasing the number of effective turns on the HV side will decrease the voltage on the LV side, and vice versa.
02/05/2010 4:35 AM
Sir,
Thank you for your reply, I can understand the concept. But I have studied in a
book that , " in a step down transformer to get a output voltage up to 10% above
nominal voltage with nominal voltage applied to high voltage winding , and allow for 5%
regulation in transformer require that tapping should be on H.V side at about -13%. Thus
the voltage in L.V side will be boosted by 15%."
I cannot understand this, Can you please explain this ?
02/05/2010 7:11 AM
100%/(100%-13%) = 115%
02/06/2010 12:12 AM
Sir,
Thank you for your reply, my doubt is if -13% tapping is provided means the voltage on H.V side is reduced by 13%, then how the voltage on L.V side will be boosted. Can you please explain this.
02/08/2010 6:34 AM
The voltage applied to the primary side remains the same. The number of primary turns goes down by 13%. Therefore the secondary voltage goes up by 15%.