the power factor for the whole system is going very low upto 0.3 ,the load is all induction motor running through DOL starter,what should we do to increase the power factor
Re: power factror is very less(0.3)
03/06/2010 7:22 AM
put capacitor bank
03/09/2010 12:40 AM
what factor sould i consider for calculating the value of capacitor bank
03/09/2010 1:54 AM
Limits within which the power factor - in fact the KVAr is varying (after all you compensate the KVAr) then you should put a APFC in line
Just the way you do not go for a high lagging pf, you shouldn't land up in a high leading pf either.
Looks to be the only choice is APFC (or may be convert them into DC Motors or some other type where the load does not spoil the powerfactor so much.
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member
03/06/2010 9:03 AM
Connect capacitor bank to your main incomer bus. Use two Capacitor banks if you have two bus sections.
03/07/2010 1:43 AM
what should be the rating of capacitor bank ,what factor need to be taken care before installing the capacitor bank.
03/06/2010 9:24 AM
Induction motors running through DOL Starters - driving what?
The pf of 0.3 means (if measured correctly) these are on almost no load.
If it is so then why are they running at all?
Why don't you put proper sized motor ?
Putting capacitor etc is all OK but why the motors are so excessively over-rated?
03/07/2010 1:41 AM
these motors are install for converyer which have to be always in running condition
02/14/2023 6:26 AM
Then expect the power factor to be low when it is doing very little work.
An unloaded, energised cable has a power factor of zero.
Good Answers: 18
03/07/2010 11:00 AM
Put in a Somar Integra motor regulator for each motor.
One of its functions is to provide soft-start. It also has very many other control and protection functions.
As concerns power factor, it greatly corrects power factor for motors. Since your power factor is so low, this mean sthat your motors are operating at very low load or that the motors are too big for what you're doing with them. Despite that, Somar Integra motor regulators will continually raise the power factor for each motor up to 90%+.
Here is Somar's website. Just ask Somar who distributes and provides services for Integra regulator in your area.
http://www.somar.co.uk/energy-saving-technology/Integra-motor-control.php
Good luck! DZ
Do unto others. Then run.
03/07/2010 11:52 AM
Don't start the motor...
03/08/2010 3:04 AM
It sounds as though the motors are oversized for the job.
Review the provision of motors and their matching to the connected mechanical loads.
Switch off unused motors.
03/08/2010 11:10 PM
YOU NEED TO CORRECT IT BY CONNECTING POWER CAPACITORS ACROSS THE LOAD .IN DOING SO YOU HAVE TO DECIDE YOU ARE GOING TO CORRECT POWER FACTOR OF INDIVIDUAL LOAD OR TOTAL SYSTEM CORRECTION.
ANY WAY HOW MUCH IS YOUR LOAD IN TERMS OF KW?PLEASE SPECIFY.