Motor Class

03/12/2010 12:12 AM

Hello Everybody,

I have been going through a standard for the rotating equipments and come across the following:

65 K for windings with insulation systems of thermal class A;

80 K for windings with insulation systems of thermal class E;

90 K for windings with insulation systems of thermal class B;

115 K for windings with insulation systems of thermal class F;

140 K for windings with insulation systems of thermal class H.

What is the significance of K in this. I mean what is 'K' here. I am sure it is not 'Degree kelvin' because where I come from we use degree C. this K has some significance. Any ideas??

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Motor Class

03/12/2010 1:04 AM

This refers to the temperature rise of the insulation above ambient. The difference in temperature is the same in either degrees Kelvin or Celsius. The K does indeed mean kelvins.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Associate

Join Date: Mar 2010
Posts: 47
#2

Re: Motor Class

03/12/2010 3:01 AM

As a sample, 90 deg Kelvin = minus 183.15 deg C. So this just cannot be. Tornado, pls re-evaluate. The K must mean something else. Cannot be kilo-ohms either. Assuming that K stands indeed for kilo, this would make 90K = 90000. This is neither here nor there. Anyway, classes of insulation for electric motors are well covered, including max permissible temp rise, in K or C, makes no difference. So why not just take it from there and be done with it.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Motor Class

03/12/2010 3:44 AM

The K is exactly what I said it was. It is about temperature difference, not absolute temperature from zero. Since 1K = 1°C precisely, this works just fine.

Incidentally, the term "degrees Kelvin" (or °K) is now obsolete. It is now just "Kelvins" (or K), with neither the word nor symbol for "degrees."

Yours sincerely--Editor Crankshaft

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Associate

Join Date: Mar 2010
Posts: 47
#4
In reply to #3

Re: Motor Class

03/12/2010 7:57 AM

This little interchange with you, editor, was very illuminating and informative. Not quite what I expected, perhaps, but informative nevertheless.

Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#5
In reply to #4

Re: Motor Class

03/12/2010 2:14 PM

It is already answered – here is additional clarification:

In terms of temperature difference:

1 K = 1 °C = 1.8 °F = 1.8 °R (all indicate same amount of change of temperature)

But in terms of temperature level (scale):

273.16 K = 0 °C = 32 °F = 0 °R (all indicate same level of temperature – freezing level)

See http://en.wikipedia.org/wiki/Kelvin or http://en.wikipedia.org/wiki/Celsius

Also note in the wikipedia link 'the kelvin is not referred to as a "degree", nor is it typeset with a degree symbol; that is, it is written K and not °K'.

So, 1 K = 1 °C, 65 K = 65 °C, 80 K = 80 °C, 90 K = 90 °C and so on ….

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)