We are getting high neutral to earth voltage at the output of UPS, but corrosponding input having low voltage what action to be taken for that?
Re: Neutral to Earthing Voltage
03/18/2010 8:03 AM
None at all, as it is irrelevant.
03/18/2010 8:11 AM
what is irrelevant ? please read carfully
03/18/2010 8:12 AM
The voltage between neutral and earth is irrelevant. Earth is a protective conductor.
It is the voltage between neutral and live that is of interest!
03/18/2010 8:19 AM
Our Power supply getting burned without getting fuse blow up at that time earth and neutral vaotage mattars right or wrong ?
03/18/2010 8:24 AM
Getting the earth & neutral conductors the right way round matters a great deal. If they are incorrect, then all sorts of damage and personal risk may ensue. If in doubt, consult a qualified electrician locally.
http://cr4.globalspec.com/comment/541126/Re-Neutral-to-Earthing-Voltage
03/18/2010 12:21 PM
Is the secondary of the isolation transformer (neutral point) kept floating?
Is it by chance connected to incoming neutral? Through NGR?
03/19/2010 2:10 AM
Please check the condition of your earth pits connected to your mains,are they alive or dead meaning showing very high resistance.if it shows high resistance than neutral to earth voltage becomes high.
03/19/2010 7:29 AM
It is my understanding that the resistance to earth needs to be < 25 Ohms for the protective circuitry to work correctly (at least in residential wiring). You might check that reading.
I have had personal experience in which 3 additional ground rods were required to get the reading down to < 25 Ohms.