Generator Upgrades

03/21/2010 10:52 PM

Hi guys,

I have a diesel engine 10 hp at 3000 rpm but generator i have is 1800 rpm how can i best attach them??

How to upgrade a 1800 rpm generator tto be used with engine having 3000 or 3600

Do i need to make any changes to coil or anything ??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: How to upgrade a 1800 rpm generator tto be used with engine having 3000 or 3600

03/21/2010 11:13 PM

The generator is now wound for 4 poles. If you increase it to 3000 or 3600 rpm, it will produce respectively 100 or 120 Hz.

If it is possible to rewind the generator for 2 poles, you will get 50 or 60 Hz, either of which might be useful.

Or you could use a gear reducer between, which will be noisy and will add various alignment, vibration, and maintenance issues.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Mar 2010
Posts: 24
#8
In reply to #1

Re: How to upgrade a 1800 rpm generator tto be used with engine having 3000 or 3600

03/22/2010 10:43 AM

Is there any issue with rewinding for 2 poles.Won't i be able 2 get that done from some winding guy?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9
In reply to #8

Re: How to upgrade a 1800 rpm generator tto be used with engine having 3000 or 3600

03/22/2010 4:33 PM

I think this can be done, but it may depend on the specific generator. If you have access to a rewinding shop, they should be able to tell you, and give you an estimate of cost.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#24
In reply to #1

Re: How to upgrade a 1800 rpm generator tto be used with engine having 3000 or 3600

03/23/2010 4:58 AM

How does that work in theory?

__________________
Plenty of room here
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#27
In reply to #24

Re: How to upgrade a 1800 rpm generator tto be used with engine having 3000 or 3600

03/23/2010 5:45 AM

On the bit about the number of poles, the synchronous rpm of motors and generators = 120 x Hz/no. poles.

Hz...120xHz...poles...rpm

60.....7200......2.....3600

.....................4.....1800

.....................6.....1200

.....................8......900

50.....6000......2.....3000

.....................4.....1500

.....................6.....1000

.....................8......750

Because of slip in induction motors, the running rpm's are about 3% less in each case. Thus rated rpm's are something like 3500, 1750, 1165, 875; 2900, 1450, 965, 725; with variations by specific design and manufacturer.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#33
In reply to #27

Re: How to upgrade a 1800 rpm generator tto be used with engine having 3000 or 3600

03/23/2010 10:33 AM

Thank you. The rewinding, is that a rotor or stator thing. Or mechanical work too?

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#2

Re: How to upgrade a 1800 rpm generator tto be used with engine having 3000 or 3600

03/21/2010 11:15 PM

You could just slow the engine down to 1800 RPM. But you will have roughly half the usable horsepower of its 3000 RPM rating.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#25
In reply to #2

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 3600

03/23/2010 5:20 AM

I tend to agree to a degree, but I don't think the power loss will be anywhere near as much as you say as Diesels have their maximum torque (and power!) at much lower RPMs than a comparable petrol or gas engine.....it is possible that max torque is around 2000 RPM or even less....if true, this will save a lot on diesel fuel usage as .

Guessing a little as the graphic display of the torque and power curves from the engine manufacturer are needed to be 100% certain, but I would suspect that the power loss will only be 15% or maybe even less, and this may still provide enough power to use the generator fully......depending upon the max possible electrical load that the generator can take of course....that also being an indication of the maximum mechanical load it will impose on the engine.

If the generator can impose a mechanical load greater than the engine can handle, it will be relatively easy to include a circuit breaker to drop the generator offline. Also a load/power meter should be attached to see that this load level is not actually reached.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Oct 2008
Location: Deepest Darkest Rutherford Oz
Posts: 951
Good Answers: 145
#26
In reply to #25

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 3600

03/23/2010 5:43 AM

G'day Andy,

It all depends on the "source" of the motor, if its a quality motor like Hatz, then yes the rated horsepower won't fall too much at lower RPM. But if it is one of those chinese copies then it will be lucky to achieve the rated power at maximum rpm, and be a tad wobbly in speed regulation at lower speeds.

Would have been nice to have had all the information on the motor and generator from the OP. Saves guessing a reasonable answer.

__________________
There are two reasons for a man to do a thing, One that sounds good, and the real one...
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#28
In reply to #26

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 3600

03/23/2010 7:41 AM

You are so right!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
5
Guru

Join Date: Oct 2008
Location: Deepest Darkest Rutherford Oz
Posts: 951
Good Answers: 145
#3

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 3600

03/21/2010 11:41 PM

There are a couple of ways to do this, and depending on resources, readily achievable.

1/ What horse power will your motor deliver at 1800 rpm? It won't be 10hp maybe more like 8 or 6hp. If the maximum output of the generator doesn't demand more that an input of 6hp then go for a direct coupling (assuming that the motor and generator rotation are the same) and set the motor governor to 1800rpm.

2/ Step down planetary gearbox. Utilising a suitably geared planetary gearbox that is selected to turn the generator at 1800rpm while the motor runs at 3000rpm. You will lose some power from the motor but not that much. Gearboxes can be expensive though.

3/ V belt/ Micro-groove Belt drive. This is perhaps the simplest "Geared" solution. You would require double sheathed pulleys and a pair of V belts or a Micro-grooved belt and appropriate pulleys. V belt set up is cheaper. You need to achieve a ratio of approximately 1.67:1, that is the motor has to turn 1.67 times to one turn of the generator. So a pulley that's 100mm(4") in diameter at the motor turns a 167mm (6.5") pulley at the generator will give you the appropriate ratio.

4/ Chain drive, same deal as the belt drive except requires more maintenance, and is potentially noisier.

You don't mention the power demand, duty cycle or output of the generator, which kind of makes it difficult to provide thorough advise.

Diesel motors like to work, so the average power demand on the generator should be 65% of the maximum output for a good deal of the time.

I'm sure this question has been asked before, so a bit of lurking in the thread archives may provide better answers.

__________________
There are two reasons for a man to do a thing, One that sounds good, and the real one...
Register to Reply Good Answer (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 3600

03/22/2010 12:09 AM

GA, especially for the belt drive idea.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Mar 2010
Posts: 24
#7
In reply to #3

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 3600

03/22/2010 10:42 AM

well at 3000 rpm it say max output 8.8 and 3600 rpm 10 hp

Generator is built for 6kw output at 1800 rpm

Register to Reply
Associate

Join Date: Mar 2010
Location: Netherlands
Posts: 42
Good Answers: 2
#17
In reply to #3

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 36

03/23/2010 3:57 AM

@ Tobugrynbak: I agree V-belts are the best practical solution, but there is a flaw in the transmission ratio calculation: if the motor has to turn 1.67 times to one turn of the generator it is not the ratio of the DIAMETERS of the pulleys but their CIRCUMFERENCE that matters. Not so?

__________________
Don't worry, be happy.
Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#18
In reply to #17

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 36

03/23/2010 4:14 AM

NO! The ratio of diameters is identical to the ratio of circumferences; the factor π simply cancels.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#20
In reply to #17

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 36

03/23/2010 4:18 AM

diameters matter --- and a chain with 2 sprockets works also - even with less loss see my comment lower. success

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Oct 2008
Location: Deepest Darkest Rutherford Oz
Posts: 951
Good Answers: 145
#21
In reply to #17

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 36

03/23/2010 4:28 AM

Well whether you measure a pulley by diameter or circumference matters naught, the result is the same.

Pulleys are usually sold by they're diameter/number of sheaves/ profile of belt.

Now if you have a 100mm circumference pulley driving a 167mm pulley, the ratio will be the same as a 100mm diameter pulley, driving a 167mm diameter pulley. The resultant division(or multiplication) of rpm will be the same. The belt speed will be higher though.

What will bite you though is the ability of a 32mm diameter (100mm Circumference) pulley to transfer sufficient power to drive 54mm diameter (167mm Circumference) pulley for a given load. That's another consideration depending on the application. It will produce the same driving/driven speed ratio however.

My example is based on a readily available components to achieve the desired result for the OP. If you scale up the pulleys further to the same ratio you will improve the power transmission ability and reduce the belt speed, but the driving/driven speeds will still be the same.

There are a quite a few parameters to be considered. to much to go into in a short reply

Cheers

__________________
There are two reasons for a man to do a thing, One that sounds good, and the real one...
Register to Reply
Associate

Join Date: Mar 2010
Location: Netherlands
Posts: 42
Good Answers: 2
#22
In reply to #21

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 36

03/23/2010 4:36 AM

@ Tornado and Tobugrynbak: Thanks for explaining, my mistake...

__________________
Don't worry, be happy.
Register to Reply
Guru

Join Date: Oct 2008
Location: Deepest Darkest Rutherford Oz
Posts: 951
Good Answers: 145
#23
In reply to #22

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 36

03/23/2010 4:41 AM

All Good, that's what we do here.

__________________
There are two reasons for a man to do a thing, One that sounds good, and the real one...
Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#29
In reply to #21

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 36

03/23/2010 9:05 AM

I'd rather measure my pulleys by the area !!

Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#30
In reply to #29

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 36

03/23/2010 9:55 AM

That's okay too; just compare by taking square roots!

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#31
In reply to #30

Re: How to upgrade a 1800 rpm generator to be used with engine having 3000 or 36

03/23/2010 10:00 AM

LOL, I can do sq rts of ratios in my head any day

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: How to upgrade a 1800 rpm generator tto be used with engine having 3000 or 3600

03/22/2010 4:02 AM

How about introducing a gearbox?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: How to upgrade a 1800 rpm generator tto be used with engine having 3000 or 3600

03/22/2010 4:43 AM

Already been done, at least twice.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Location: Deepest Darkest Rutherford Oz
Posts: 951
Good Answers: 145
#10

Re: Generator Upgrades

03/22/2010 7:19 PM

Hmm, according to my yard stick you will need to provide a little bit over 8hp (maybe 8.5hp)to drive your generator for a 6kw power draw.

It of course depends on what your planned power draw is if your only going to draw 4 kw out of it then you can get away with slightly lower hp from the motor (not RPM though).

__________________
There are two reasons for a man to do a thing, One that sounds good, and the real one...
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11

Re: Generator Upgrades

03/22/2010 10:48 PM

I think the belt drive idea is the winner here. It is likely to be way less expensive than a rewind or a gear reduction, and quieter and less maintenance than a gear. I don't have a belt table on me, but I think a single C strand or double B will do the job. The overhung load capacity of the generator drive-end bearing will need to be checked.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
Hobbies - Car Customizing - New Member

Join Date: Dec 2008
Posts: 117
Good Answers: 11
#12

Re: Generator Upgrades

03/22/2010 11:19 PM

1) is this a single bearing, or 2 bearing generator head?

if 2 bearing, the belt drive suggestions are your best choice.

if it is single bearing, it mounts on a "generator taper" engine, and you will have to derate your output to what the engine provides at 1800 rpm

Register to Reply
Guru

Join Date: Feb 2008
Location: East Tenneesse, USA
Posts: 685
Good Answers: 46
#39
In reply to #12

Re: Generator Upgrades

03/25/2010 5:18 AM

Yosemit3, here an idea, if the generator is single bearing set it up this way. Mount the generator solid to a frame at the shaft end. Take two pillow block bearings run an appropriate size shaft through the bearings with the pulley between the bearings then on the end of the shaft have an engine coupling attached that connects to generator shaft. Just like it, if it was connect to the motor. No side loads on the single bearing. The motor would just have the other pulley as normal. Belt tension can be done several ways motor mounts slot adjustable, not the best. Generator mount with pillow blocks as a unit with bolts in slots, a little better. Best would be tension idler like used in automotive serpentine belt application.

This setup is a little more involved but not much. But it's a way around excess side load on gen with single bearing.

Charles.

__________________
Metal is the material, The forge is life, The anvil and hammer bring character and soul.
Register to Reply
Participant

Join Date: Mar 2010
Location: Belgrade, Serbia
Posts: 4
#13

Re: Generator Upgrades

03/22/2010 11:20 PM

Change nothing to the generator; just adjust rotation speed by means of belt or reduction gear drive.

Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#14

Re: Generator Upgrades

03/22/2010 11:29 PM

What is stopping from running the 3000 RPM diesel engine running at 1800 RPM. Why you are not able to throttle it down?

__________________
Subramanyam
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#15
In reply to #14

Re: Generator Upgrades

03/22/2010 11:40 PM

Not enough horsepower at 1800 rpm to drive the generator.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#19
In reply to #15

Re: Generator Upgrades

03/23/2010 4:15 AM

Depends only on the engine couple. Some diesels have that power in the lower RPM's.

__________________
Plenty of room here
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#16

Re: Generator Upgrades

03/23/2010 3:36 AM

Your diesel, if build for a generator has most probably a governor, that is the device that regulates the right dose of diesel injection to maintain a constant RPM (revolutions per minute) If you have a couple/or momentum curve of your diesel engine and you do not need the full 10 HP - run the engine to 1800 RPM - Your engine will make less noise and will run smooth. You can also drive the generator with 2 V- belts and pulleys if both shafts ( engine and generator) have 2 or more bearings. I have 3 solutions for you: 1. Run the engine @1800 RPM (change the governor - sometimes only 2 little weights) 2. Run your engine and generator with pulleys and 2 V- belts with diameters: RPM1 X d2 = RPM2 X d1 (or n1Xd2= n2Xd1) (your engine will have the smallest pulley here) 3. Buy a generator @Harbor Freight for $350 and use that, coupled directly and run your engine @3600 rpm.

__________________
Plenty of room here
Register to Reply
Anonymous Poster
#32

Re: Generator Upgrades

03/23/2010 10:24 AM

I've done this modification before. It will work on generators that have two armature bearings and an input shaft. You need to belt drive the generator from the engine with a belt drive. Figure out the pulley sizes and that's it except for fine tuning the engine governor to get 60 Hz. If the generator is not capable of a modification to belt drive listen to the other experts here.

Register to Reply
Participant

Join Date: Mar 2010
Posts: 1
#34

Re: Generator Upgrades

03/23/2010 11:17 AM

The frequency of the output is determined by the RPM. 60 Hz. generators turn at 1800 RPM. Assuming your engine has a throttle control and a mechanical governor to reasonably maintain the RPM, set it to 1800 RPM you are good.

Al

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#35

Re: Generator Upgrades

03/23/2010 11:20 PM

Direct coupling would not help since it has to do with adjusting the the engine speed that also affects the engine efficiency. Engines available for generators are for single speed that matches the speed of the alternator.

The best option available to you is the speed reducer system which can be either gear box, pulley or sprocket.

In this way the engine performance will not be affected and maximum out put will be delivered from Ur alternator.

Dickson

__________________
There is peace in silence and achievement in plans.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#37
In reply to #35

Re: Generator Upgrades

03/24/2010 1:42 PM

The power losses are considerable in such systems, going from memory that can easily exceed 10%, that would probably be about the same power loss if the engine is run slower than designed (though the designed speed has not been posted, nor has the exact engine type either!)

Just a thought!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Active Contributor

Join Date: Mar 2010
Posts: 24
#36

Re: Generator Upgrades

03/24/2010 10:55 AM

I think belt n pulley r best.Only thing i have in mind is how much would it reduce power? I mean its 10 hp engine i think if i use it full would be able to draw 6kw and if i use belt system would i be able to draw 5kw? or it be lesser than that?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#38

Re: Generator Upgrades

03/24/2010 5:09 PM

1800/3000 = 60% of rated speed. As the engine speed is reduced, the hp delivered also decreases. But the torque increases, partially compensating for this. At 60% speed, the engine can still deliver about 70-80% of its full power. We would need to see the engine performance curve to know what this particular one will do.

Another item to consider is that the load on the generator might be only 4-5 kW, even though it is rated for 6 kW. If so, the simple approach of slowing the engine down might very well work, but it won't give much reserve capacity.

A good belt drive may have about 3-5% losses. Thus the engine can still deliver about 9.5 hp. This is a good reserve to have, especially if you will be starting electric motors.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Register to Reply 39 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

adoolittle (1); Andy Germany (3); Anonymous Poster (1); Brave Sir Robin (2); Dickson (1); dvmdsc (5); fredart (2); gsearay19 (3); kvsubramanyam (1); metalSmiths (1); pradomir (1); PWSlack (1); tcmtech (1); Tobugrynbak (5); Tornado (10); Yosemit3 (1)

Previous in Forum: VVVF Drives - Vector and Scalar Modes   Next in Forum: Substation Grounding Design

Advertisement