Current for a 3ph compressor?

03/30/2010 5:14 PM

I would like to know the formula for working out the current for a 3ph compressor rated at 45kw?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#1

Re: Current for a 3ph compressor?

03/30/2010 7:07 PM

Personally, I wouldn't worry too much about the formular for the compressor as it does not use electricity.

The motor on the other hand will not need a formular either, it has a special device on it will all the information you need on it. It's call a specification Plate.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Current for a 3ph compressor?

03/30/2010 9:19 PM

Formula for current in a 3 phase motor:

I = P/(E x Eff. x PF x 1.732)

I = Current

P = Power, 45kW in your case

E = Voltage, you didn't say

Eff. = Motor nameplate Efficiency, assume 80% (.80) if you don't know

PF = Power Factor at Full Load, assume 70% (.70) if you don't know

1.732 = Sq. Rt of 3, because it is a 3 phase motor (I'm assuming, because 45kW is typically too big to run on single phase).

So assuming you have not yet received your compressor and are attempting to determine in advance what size service you will need for it (which moves us beyond the earlier sarcasm), assuming you have a 400V motor and service;

I = 45kW / (400 x .8 x .7 x 1.732)

I = 45000 / 387.97

I = 116A FLC

What your compressor actually draws will likely be less than this, but you must base your design criteria for service equipment on this in advance to be safe.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)