VFD vs. Soft Starter (Pump Application)

03/30/2010 7:01 PM

What are the differences between VFDs and soft starters??

(Cost, functionality, different pump applications such as positive displacement, centrifugal, etc., pros and cons)

http://www.integratedcontroltech.com/downloads/StockAutomation.pdf (Sorry! Link no longer available.)

Based on the features specified for each (VFD and soft starter) in the weg catalog, the one thing that stands out is the speed control. VFD have a more accurate speed control, whereas soft starter do not function necessarily to control the speed of motors.

Thanks!

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: VFD vs. Soft Starter (Pump Application)

03/30/2010 9:10 PM

Well really, that's it in a nutshell. A soft starter cannot change the speed, so if you need to, it will not work. You cannot really compare them in that realm.

VFDs are 5-10 times more expensive than soft starters once you get above about 25A, so you really cannot justify using a VFD in place of a soft starter unless you have some very specific issues:

  1. A VFD can allow starting of an AC motor at 100% FLC or less, a soft starter cannot. So if you have a severely limited power source, sometimes a VFD is your only choice. A soft starter cannot start a loaded motor with less than 200% current, usually 300-450% depending on the type of load.
  2. A VFD can allow a 3 phase motor to be run from a 1 phase source (with proper selection), a soft starter cannot.
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
3
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: VFD vs. Soft Starter (Pump Application)

03/30/2010 10:38 PM

Good explanation by JRaef - not only in this thread but in many previous threads as well. One recent thread about VFD and Soft starter I can remember is http://cr4.globalspec.com/thread/50941

In addition, I just would like to add little more:

The intention for using soft starter is primarily to decrease the starting current, not to save energy, not to control speed.

While the intention of using VFD is to decrease starting current, control speed and save energy. However, saving energy by VFD is sometimes misused and misunderstood, VFD can save energy only when it is used for controlling the flow with varying the speed of centrifugal pumps (for liquid) or fans (for air) and the flow varies in wide range and remains at lower end most of the time.

How VFD saves energy?

VFD saves energy based on the affinity law which indicates

Flow ∞ RPM

Head ∞ RPM2

Power ∞ RPM3

Let me explain with this example: In a system, a centrifugal pump delivers 1000 CFM at 1800 RPM and 500 CFM at 900 RMP. The flow of the system varies from 1000 CFM to 500 CFM and most of times the flow remains at 600 CFM.

In this case, if you use a DOL starter, the motor runs at 1800 RPM all the times and the theoretical power consumption of the motor is proportional to the cube of 1800 (as per the affinity law). If a VFD is used here, the theoretical power consumption is mostly proportional to the cube of 600. So, VFD saves power in this case.

Let's consider the same example but most of times the flow remains at 900 CFM (instead of 600 CFM).

In this case, the theoretical power consumption by the VFD is mostly proportional to the cube of 900 and the power saving is not significant as compared to the previous case.

(Note: I mentioned 'theoretical power consumption' because the calculation is not exactly this in practical – there are other things to consider as well)

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 3)
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#3

Re: VFD vs. Soft Starter (Pump Application)

08/07/2016 4:35 AM

Dear Friend,

VFD will vary the Frequency of output speed of motor. and Soft Stater will LIMIT the starting current of the Elec.Motor. Also pl. note the Motor for VFD application is different from conventional motor

For example, if 1500 RPM Synchronous Speed motor, will run at 1440 RPM if the supply frequency is 50 Hz., where the slip is 4%. If VFD is used you can vary the speed from 200 RPM to 1200 RPM and the soft starter has no roe here.

If Soft Starter is used it will reduce the starting current - for example If DOL starter is used, starting current may be 6 times of full load current. Star-Delta starter may take 4.5 times full load current, Slip-Ring rotor starter may take 3 times full load current and soft-starter may take 2.4 to 2.8 times full load current.

This is only an example. Each type of starter has its own merits and de-merits and also linked to the cost.

DHAYANANDHAN.S

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: VFD vs. Soft Starter (Pump Application)

06/25/2024 7:40 AM

It's difficult to make comparisons. It's a bit like asking the difference between an apple and an orange: they do different jobs, they don't taste the same and they are both fruit.

<...VFD vs. Soft Starter...>

They do different jobs, they don't taste the same, and they both start motors.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856