Motor Protection Relay (MPR)

02/23/2010 11:19 AM

What is the difference between a Motor Protection Relay(MPR) & Soft Starter &

VVVF Drive.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Motor Protection Relay(MPR)

02/23/2010 12:02 PM

A soft starter reduces the voltage applied to the terminals of a motor at start-up so as to reduce the inrush current.

A variable frequency drive varies the frequency of the supply to the motor so that, in theory, it can start at 0rpm and accelerate from there.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Motor Protection Relay(MPR)

02/23/2010 12:24 PM

They all are pretty different thing with having common motor protection capability.

Motor protection relay: It is used for the protection of medium voltage motors and used to trip the MV motor starter when the fault condition occurs. Motor protection relays have various modules such as overcurrent, short circuit, unbalance, ground fault, number of start/hour, thermal unit etc. Common motor protection relays are Multilin 469 (GE), SEL749 (SEL), IMM 7990 (CEE).

Soft Starter: It is primarily used to limit the starting current of the motor. However, soft starter itself contains the motor protection capability and hence separate motor protection relay is not required. It is also used to control the motor start/stop. Soft starters can be used for both LV and MV voltage motors.

VVVFD (Variable Voltage Variable Frequency Drive) or VFD: It is primarily used when motor speed control is needed as well as for limiting the starting current. Like soft starters, it also contains the motor protection (hence separate motor protection relay is not required) and start/stop control capability. It is also used for both LV and MV voltage motors.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: Motor Protection Relay (MPR)

02/24/2010 4:31 AM

Motor protection relay does the function of protecting the motor from abnormal parameters like current,voltage,temperature during the operation of motor.

Starter does the function of starting the motor from o speed to designed speed .

Both devices are different does different functions.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Feb 2010
Location: India
Posts: 92
Good Answers: 2
#4

Re: Motor Protection Relay (MPR)

02/24/2010 11:04 AM

MPR- Its main function is to protect the motor from any fault and keep safe the motor. It has certain features like Thermal Overload, Instantaneous, Earth fault, negative phase sequence, Stall current etc with amny other features.

SS- Its main function is to apply low voltage to motor terminal during starting(to limit the starting current) and then gradually increases the voltage to attain the full speed or max. torque.

VVVF- Torque is proportional to flux. By applying VVVF method, flux is maintaining constant in all values of voltage. This provide constatnt torque to motor from starting to max speed.

Register to Reply
Active Contributor

Join Date: Nov 2009
Location: Mumbai
Posts: 17
Good Answers: 1
#5

Re: Motor Protection Relay (MPR)

02/25/2010 2:39 AM

Very much different !

MPR is mainly used for protection and can be a part of motor starter. A motor starter is used to start a motor and can have energy saving capabilities. A soft starter is used where the application needs to smoothly start without a jerk. Some of these starters are also believed to be energy saving devices.

A VFD (aka VVVF i.e. Variable Voltage Variable Frequency) is an energy saving device primarily used in applications requiring control of rotational speed by variation of frequency of supply. It is recommended to be used with a filter / choke (possibly inbuilt) to negate the effects of Harmonics - one of the most serious system pollutants.

Cheers,

RRV

www.econserve.in

__________________
Cheers, RRV
Register to Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#6

Re: Motor Protection Relay (MPR)

02/25/2010 12:26 PM

Also, to add to the answers already given:

MPR is a monitoring device only, can be used to disconnect the supply

Soft Starts and VFD are control devices which also may have different monitoring and protective functionality

__________________
Something new every day!
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Motor Protection Relay (MPR)

02/25/2010 1:23 PM

It should be noted that most VFDs and some high-end soft starters will provide most if not more protection features found in many Motor Protection Relays. In the case of VFDs, most inexpensive MPRs are incapable of accurately protecting the motors because they cannot correctly interpret the output current waveform coming from a VFD, so the VFD will actually do a better job or providing protection. There are exceptions to this rule as you go to higher priced MPRs and lower priced VFDs of course.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

JRaef (1); MalcolmK (1); msamad (1); PWSlack (1); ramvinod (1); rrv (1); sidhu16 (1)

Previous in Forum: ABB SF6 CB   Next in Forum: Phase Loss

Advertisement