Anonymous Poster

Differential Relay Didn't Work While CT Exploded

04/07/2010 1:15 AM

HI ALL,

POWER TRANSFORMER'S DIFFERENTIAL RELAY DIDNT WORK WHILE CURRENT TRANSFORMER EXPLODED

IS IT NORMAL ?

S=100 MVA

154 / 33,6 kV

33,6 kV SIDE 1 PHASE CURRENT TRANSFORMER EXPLODED, SECONDE PHASE'S IS LESS DAMAGED, JUST CLOUD.

AND IT CAN SEE A LOT ARC IMRESSION AT ALL MV BUS BAR.

REGARDS.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: DIFFERENTIAL RELAY DIDNT WORK WHILE CT EXPLODED

04/07/2010 2:50 AM

<...IS IT NORMAL ?...>

NO.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#2

Re: Differential Relay Didn't Work While CT Exploded

04/07/2010 1:28 PM

Really,, Is there such as probability ?

Reply
Commentator
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2009
Location: Tamil Nadu
Posts: 66
#3

Re: Differential Relay Didn't Work While CT Exploded

04/09/2010 11:17 PM

Differential relay should have tripped if it is not damaged in the process. Perhaps the o/c current relay as well if set properly.

__________________
Better not count the cent if the risk is many many dollars.
Reply
Commentator

Join Date: Jan 2010
Posts: 73
Good Answers: 1
#4

Re: Differential Relay Didn't Work While CT Exploded

04/11/2010 8:59 AM

can you please give further details?... was the current transformer, (the one that exploded) included in the differential relay? (what i mean is that it is one of the inputs to the differential relay?)

if it is not, then the relay will not trip that is for sure..

Reply
Anonymous Poster
#5
In reply to #4

Re: Differential Relay Didn't Work While CT Exploded

04/11/2010 1:35 PM

CURRENT TRANSFORMER THAT EXPLODED IS AT THE SECONDARY SIDE OF THE POWER TRANSFORMER.

IT WAS BREAKEN UP IN TWO.

DIFFERENTIAL RELAY SHOULD HAVE TRIPPED CERTAINLY ?

THANKS..

Reply
Commentator

Join Date: Jan 2010
Posts: 73
Good Answers: 1
#8
In reply to #5

Re: Differential Relay Didn't Work While CT Exploded

04/12/2010 1:01 AM

Hi..

i hope you have already understand the problem you are trying to ask..

what i mean is that..(was the current transformer you used included in your differential relay?)

as it was clarified by jans.. if this current transformer was included in your differential, then make sure to check your differential relay...

if this current transformer is not included in your differential relay, then no tripping of differential relay is expected.

Reply
Commentator
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2009
Location: Tamil Nadu
Posts: 66
#6
In reply to #4

Re: Differential Relay Didn't Work While CT Exploded

04/11/2010 1:56 PM

we normally ask for a seperate ct for differential protection wherever feasible.if not at least the differential core must be electrically the outermost core covering the metering core and perhaps the pt and la as well.on ct explosion many things are feasible.1)differential lv core opened-the differential relay would have tripped.

2) differential core shorted:then if the pilot resistance is considerable then the differential relay could trip.if the pilot resistance is much smaller than the differential relay impedance then the relay may not trip.

3)the cores are in tact but due to fault surge the differential rely may have damaged.For this reason also we prefer high speed relays since they can operate before a damaging surge builds up.

Pl. check if the differential relay is functional. When was the relay last tested.Pl. try to select a sensitive settings with proper biases.

Thorough periodic testing setting and commissioning exercises are not less important than installing the relay.

__________________
Better not count the cent if the risk is many many dollars.
Reply
Anonymous Poster
#7
In reply to #6

Re: Differential Relay Didn't Work While CT Exploded

04/11/2010 3:41 PM

thanks a lot for ur reply

Reply