Stuck out in the field and need to know if you can run 120vac and 24v circuits in a 4x4 gutter, stuck in field wo nec in an emergency situation
guest
Re: 120vac with 24v in a gutter
04/08/2010 12:26 PM
Told him to run all 600v control wire or seperate by 12" for capacituve coupling/inductance
guest
Good Answers: 29
04/08/2010 4:04 PM
It's OK, especially if the 24V is AC power for devices. The problem is that if your devices are measuring something and sending back 4-20 or 0-10 signals you should shield them, especially if it's a long run. What's this power of yours doing anyway?
Good Answers: 804
04/08/2010 4:25 PM
You do have to be a little careful about induced voltages if the 24V is involved in PLC inputs, but only if there is significant current flowing in the 120V circuits.
04/09/2010 2:59 AM
It would be wise to segregate them as widely as possible, though 4-20mA circuits are largely immune from nearby AC circuit coupling.