Incomer sizing calculation for a 3phase 4 wire 415V 50Hz switchboard

04/08/2010 9:09 AM

Dear All, I am looking for a incomer circuit breaker rating calculation of a LV switchboard. The outgoing feeders with current rating are 1. 125A 2. 160A 3. 160A 4. 125A 5. 125A 6. 80A 7. 160A 8. 80A 9. 80A 10. 80A How much should be the incomer rating? All these outgoing feeders are power feeders like lighting, welding, battery charger.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Incomer sizing calculation for a 3phase 4 wire 415V 50Hz switchboard

04/08/2010 9:24 AM

The diversity of the board is what, please?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Incomer sizing calculation for a 3phase 4 wire 415V 50Hz switchboard

04/08/2010 10:54 PM

If all those items could be running at the same time, you need to add up the total FLA (full-load amps) and multiply by 1.15 (for combinations of general loads). There are some specific situations that may call for a different multlplier; for instance, if they were all motor loads, you would add up all the FLAs, plus 0.25 times the largest motor FLA. This gives the feeder ampacity; the main breaker would be ΣFLA + 1.25 (largest motor FLA), if I remember correctly. See local codes. [Caveat: it has been a while since I designed UL-508 panels, so these numbers may be a bit rusty. But they should convey the idea.]

If you can be sure that not everything will be running at once, then you can research the aforementioned diversity factors, which may allow for a smaller feeder and main breaker.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#3

Re: Incomer sizing calculation for a 3phase 4 wire 415V 50Hz switchboard

04/09/2010 1:20 AM

In addition to all the points mentioned you will need to the fault level at the bus bar.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#4

Re: Incomer sizing calculation for a 3phase 4 wire 415V 50Hz switchboard

04/09/2010 2:11 AM

Dear Guest,

As per AC fundamentals, The total current should be calculated in vector form, so you should know the power factor of each load approximately. once the total current is calculated, check what transformer capacity you need to use, considering additional margin(in KVA) for spare feeders in future. in case you have motor load which take heavy current during starting, the transformer must be able to withstand those heavy currents.

if you could provide additional details about your loads and regarding their continuity of usage, the members in this forum will be able to help you in a better way.

Reply Score 1 for Good Answer
Anonymous Poster
#5
In reply to #4

Re: Incomer sizing calculation for a 3phase 4 wire 415V 50Hz switchboard

04/10/2010 12:12 AM

Thanks for the reply. Actually this switchboard will be fed from another one switchgear. Also there is no motor feeders in this switchboard. All are lighting and welding supply feeders. Could you please confirm that 400A incomer rating will be sufficient?

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: Incomer sizing calculation for a 3phase 4 wire 415V 50Hz switchboard

04/10/2010 10:29 AM

Absolutely NOT, on the information given. Even if we assume your loads are only 0.80 times the CB ratings listed, they still add up to WAY OVER 400 A. Only if you can assure that half or so of them are idle at any given time....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard