1 Pole Reclosing in 2nd Zone

04/14/2010 2:14 PM

HI,

AT HV POWER TRANSMISSION LINES, 1 POLE RECLOSING IN 1st ZONE FAULTS ....IT IS OK.

BUT IN 2nd ZONE 1 PHASE GROUND FAULTS ?

WHAT DO YOU THINK ? IS IT FEASIBLE SOMETHING ? AND IS AIDED RECIEVE NECESSARILY ?

THANKS

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: 1 POLE RECLOSING IN 2nd ZONE

04/14/2010 3:25 PM

It sounds like you have a phase to ground fault (unless this is a sensing problem and the fault isn't actually real). If reclosing into the fault did not remove it then it is 'permanent' and you will need to send a line crew in to find and repair the fault (which could be a tree on the line or a downed line on the ground). Follow standard company procedures, etc.

If you want any better advice you are going to need to provide much more information presented in a clear and detailed way, for example what does Zone mean (phase, location, upstream/downstream line segment designation), etc.

AND IS AIDED RECIEVE NECESSARILY ?

No I would say line fault location and repair is necessary.

__________________
jack of all trades
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: 1 POLE RECLOSING IN 2nd ZONE

04/15/2010 2:56 AM

Please turn off Caps Lock, for pity's sake....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Commentator

Join Date: Jul 2009
Location: chennai, India
Posts: 55
Good Answers: 1
#3

Re: 1 POLE RECLOSING IN 2nd ZONE

04/15/2010 12:56 PM

Single pole single shot auto re-closing is generally adopted for a section of transmission line between two stations.Generally 80% of length of line is covered under First Zone.the balance 20% is covered under IInd Zone.

[Suppose a single phase to ground fault occurs in the end 20% of line. Then one end will Trip in Ist Zone and other end shall trip after second zone delay.

[However provisions such as Carrier aided under reaching tripping schemes are available to make the other end also trip in zone 1 time. This enables the successful auto re-closing feasible without minding for synchronising before re-closing .

For any other fault Single pole auto reclosing cannot be attempted .

__________________
There is nothing either good or bad, only thinking make it so -
Reply
Anonymous Poster
#4

Re: 1 Pole Reclosing in 2nd Zone

04/15/2010 1:23 PM

you can put into use high speed single pole single shot even if there are no channel recieving and sending.

am i right ?

Reply
Commentator

Join Date: Jul 2009
Location: chennai, India
Posts: 55
Good Answers: 1
#5
In reply to #4

Re: 1 Pole Reclosing in 2nd Zone

04/16/2010 1:06 AM

Can be Possible, but the dead time has to be increased by 400-500ms ( i.e second zone time) to ensure that both end had cleared the fault.

It is not advisable to operate the system in an unbalanced condition ( Keeping 1 pole in open condition) and not generally practiced.

__________________
There is nothing either good or bad, only thinking make it so -
Reply
Reply to Forum Thread 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); jack of all trades (1); Panneer Selvam (2); PWSlack (1)

Previous in Forum: Power Cable Comparison   Next in Forum: Vacuum Tube

Advertisement